Counter lighting

  • 22-03-2011 11:53am
    #1
    Registered Users, Registered Users 2 Posts: 8,720 ✭✭✭


    Hi, I have 3 counter lights under my presses but they stopped working a while ago. I suspected the transformer so replaced it with an identical rated one but no joy.

    The wiring seems intact to each light and bulbs have been replaced. I have a diagram to illustrate the setup (excuse my poor mspaint skills). Could it be the light fittings themselves that have been damaged by condensation?

    152512.JPG


Comments

  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    How did you confirm there is power at them. A phase tester for example will only show you there is a live feed at the items, it wont show if the neutral is ok at them.

    Also, it only probably needs one bad connection in the junction box for all the lights to not work, but a multimeter might show there is power there (12v)


  • Registered Users, Registered Users 2 Posts: 8,720 ✭✭✭Hal1


    All I had was a phase tester :o. The wiring is intact, no breaks etc. The room lights and extractor are all ok. I should have said that a feed from the extractor is powering the counter lights.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Hal1 wrote: »
    All I had was a phase tester :o. The wiring is intact, no breaks etc. The room lights and extractor are all ok. I should have said that a feed from the extractor is powering the counter lights.

    A phase tester wont show power at the junction box either if its 12 volts.

    Anyway, switch on the lights, and put the phase tester into the neutral supply connection of the transformer, and see if the phase tester lights. If it does, you have an open neutral. Wiring can look intact, thats why we have testers to indicate if circuits are open, to save physically having to pull them apart.