Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

household bonding

  • 21-01-2011 12:42pm
    #1
    Registered Users, Registered Users 2 Posts: 721 ✭✭✭


    is all household bonding to be 10sq these days?

    what is the rule regarding bonding a radiator in a bathroom with plastic pipes to sink?

    any help appreciated thanks


Comments

  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    if it's not screwed to foil backed slab and doesn't have copper extending through the floor-it may not be extraneous

    amd doesn't need to form part of the bathroom local bond

    1 metre of tap water in 15mm rad pipe apparently has a resistance of 100Kohm

    http://www.plasticpipesgroup.com/pdfs/earthbonding.pdf


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    The high resistance/impedence of water is definitely right. Many assume its a good conductor because we hear of it making electrical shocks far more dangerous which it does, its extremely poor at conducting in reality though. What it does do though is makes the skin have a much better contact when live conductors are touched.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    http://www.tlc-direct.co.uk/Book/5.4.3.htm

    that's a UK link but they quote a figure of 23/50 Kohm-measured from the rad etc. back to MET

    below-it's considered extraneous

    above -it's ignored


Advertisement