Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Cable Sizing

  • 28-04-2010 12:48pm
    #1
    Registered Users, Registered Users 2 Posts: 1,559 ✭✭✭


    Can someone please go through whats required when installing a cable.

    I know first you need to find the designed current i.e. the current of the load and then select your breaker and your cable is sized from the breaker with whatever correction factors (grouping, temp, etc.) is there any other considerations?

    Also there's mention about loop impedance in other threads what is this about and should this be done on every cable? Are there any other checks required?


Comments

  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    the 'loop-impedance' needs to match the 'protective device' for the cable

    to ensure 'automatic disconnection' within the required time

    (basically a short- circuit)

    'overcurrent protection' will still work even if the loop impedance is wrong


  • Registered Users, Registered Users 2 Posts: 630 ✭✭✭mazthespark


    Can someone please go through whats required when installing a cable.

    I know first you need to find the designed current i.e. the current of the load and then select your breaker and your cable is sized from the breaker with whatever correction factors (grouping, temp, etc.) is there any other considerations?

    Also there's mention about loop impedance in other threads what is this about and should this be done on every cable? Are there any other checks required?

    ya you have mentioned most of the main ones there voltage drop is another one to consider.

    etci regs are very handy for it and the sequence to do it which of course isnt in them! should have a sample question somewhere from my fas days if you need it

    also if you are anywhere near the max values of a cable go up to the next size will allow for expansion etc.


  • Closed Accounts Posts: 4,431 ✭✭✭M cebee


    433.1 in the rules shows a simple formula

    Ib<In<Iz

    thats 'Design Current' less than/equal to rating of 'Protective Device '

    less than/equal to 'CCC' of cable(including correction factors)

    The 'Fault Loop Impedance' will have to be appropriate for protective device and type of circuit(distribution or final)

    and 'VD' is 4%max within installation- at FLA or design current

    you already have the most of it anyhow


Advertisement