Small amount of Air in Rad??

  • 26-02-2010 9:47pm
    #1
    Registered Users, Registered Users 2 Posts: 983 ✭✭✭


    A small amount of air is getting in to the same section of a double radiator time after time. What would cause this? Its an open system with a water tank in the attic. Is there a simple solution. I have no signs of a leak.


Comments

  • Registered Users, Registered Users 2 Posts: 887 ✭✭✭suitseir


    I have that problem as well. A double radiator with the problem on the top of the inside one. The plumber just bled it during the last service and it worked fine. Saying that, the system is now due another service and that same radiator is acting up again...just at the top...the rest is fine! Don't think leaks would be a problem in that case! Could be wrong! But I definitely have no leaks....


  • Closed Accounts Posts: 6 aj25


    Inquire about fitting an AAV (automatic air vent), usually fitted at the highest point of your system and will let any air out.