6 x 400 Watt MH on one circuit

Options
  • 14-01-2010 6:19pm
    #1
    Registered Users Posts: 315 ✭✭


    what size cable would you recommend to power 6 x 400W metal halides on one circuit or maybe 3 and 3, also what size breaker to use? please. It comes to 10.43 Amps


Comments

  • Registered Users Posts: 419 ✭✭eoghan.geraghty


    Split it between 2 if not 3 circuits, are they 400 or 500W?


  • Registered Users Posts: 1,135 ✭✭✭maxamillius


    2 circuits 10A mcbs


  • Closed Accounts Posts: 1,712 ✭✭✭davelerave


    2 C10 mcbs for 3+3 alright.
    what are they for


  • Registered Users Posts: 1,135 ✭✭✭maxamillius


    indoor in a warehouse or outdoor,will be deciding factor on your cable type,nymj or swa!


  • Registered Users Posts: 315 ✭✭johnnyfruitcake


    There for use outdoors lighting an arena, prob have to use SWA so,
    maybe 2.5 sq. 3 are close to the board and the other 3 will be 20 - 30 metres away


  • Advertisement
  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 10,952 Mod ✭✭✭✭Stoner


    i agree, sq cable for 1200Watts using two circuits. Would you consider NYMJ


  • Registered Users Posts: 315 ✭✭johnnyfruitcake


    Would 2.5 sq NYMJ be safe to use, it would save me a good bit of money all right, I might run it through ducting instead of using SWA and loop the lights through seperate junction boxes


  • Closed Accounts Posts: 1,712 ✭✭✭davelerave


    if it's underground- rule out nym ,even with duct