problem with baxi boiler

  • 07-01-2010 11:47pm
    #1
    Registered Users, Registered Users 2 Posts: 345 ✭✭


    have problem with baxi boiler only 5 years old and has been serviced regularly.
    first off i got a flashing error on 60 led so repressurised it was low under 0.5 cold now at 1.7 cold after represurizing.
    worked for a while but problem has reoccured any suggestions .thanks


Comments

  • Registered Users, Registered Users 2 Posts: 647 ✭✭✭corcaigh1


    Hmmm..Checkout the giggling pin and the laughing shaft.


  • Registered Users, Registered Users 2 Posts: 345 ✭✭curraghyid


    an expert


  • Posts: 0 [Deleted User]


    Sludge can get in to the low pressure safety device blocking it, so that when you refill it can't sense the pressure or the switch is just defective, the first i would think, but you would need a RGII http://www.rgii.ie/ anyway to identify, Gary.


  • Registered Users, Registered Users 2 Posts: 345 ✭✭curraghyid


    hanks gary71. problem turned out to be the microswitch actuator stuck in on differential valve must have hapened when pressure dropped off.:D