25A RCBO

  • 10-10-2009 4:02pm
    #1
    Registered Users, Registered Users 2 Posts: 899 ✭✭✭


    Folks,

    How many sockets may be safely attached to a 25A RCBO radial config ?

    Also, can you confirm that 2.5 sq cable is suitable ?

    P.


Comments

  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    2.5 is not suitable according to the new regulations (ET101 4th edition) it must be 4mm sq.

    A maximum for 10 twin sockets may be connected to a radial socket circuit.


  • Registered Users, Registered Users 2 Posts: 899 ✭✭✭bauderline


    Thanks I appreciate that ! 4sq and a second rcbo then...

    P.