Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

gerkros cosyman oil burner problem

  • 29-09-2007 11:10am
    #1
    Registered Users, Registered Users 2 Posts: 47


    I recently installed a Gekros Cosyman oil heating system. It is in a self contained metal box. My problem is that the system keeps tripping out. Not from the burner itself but the box containing the thermostat. It has a covered trip which has to be opened and reset every day at least once. I have been left with no documentation by the plumber who did the job and he is getting back to me with it. Yeah right. Any one know what causes this to trip. Is it a wiring problem or what ?. Any help would be great.


Comments

  • Registered Users, Registered Users 2 Posts: 12,555 ✭✭✭✭AckwelFoley


    http://www.gerkros.ie/cosy%20man.htm

    Follow the link and click the link at the bottom left of the page. You can download the Manual there.


  • Registered Users, Registered Users 2 Posts: 47 Bravadin


    Thanks but I have already seen that. The Cosyman Dual Stat is the piece of equipment which is misbehaving but there is no information about the sort of problems which might be causing this.


  • Registered Users, Registered Users 2 Posts: 1,271 ✭✭✭.243


    it mightnt be the stat,it could be happining because its up too high(ie,95 degrees turn it down to 65degrees) or the ciculating pump is gone so the water is only heating in the boiler itself or there mightnt be no or very little water in the system,


  • Registered Users, Registered Users 2 Posts: 47 Bravadin


    Well It's not the temp as I have turned the temp down and it still happens. Will check the water supply in the system tomorrow. The pump is ok as the system works for a while ,varying duration, and the rads get hot. thanks again


  • Registered Users, Registered Users 2 Posts: 1,775 ✭✭✭JamesM


    Make sure that the sensor probes are inserted fully in their pockets. Also make sure that there is no air in the top of the boiler.
    The safety stat is working, but the main stat is not shutting off.
    Jim.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 47 Bravadin


    thanks for all your advice. I emailed the Gerkros company as well for advice and they are sending a man out to look at it for me. thanks to them and ye guys


    Edit

    just to finish off. The engineer got here today and replaced a faulty thermostat. Very prompt service from a very helpful company. Thanks again


Advertisement