Immersion timer (again)

  • 21-06-2007 1:45pm
    #1
    Registered Users, Registered Users 2 Posts: 2,102 ✭✭✭


    Hi all, just looking for some advice.
    We have a standard "on / off" and "bath / sink" switch for the immersion.
    DW is always leaving it switched on for days and I was hoping to have this fitted to switch off the supply after a set time.

    We don't want a programmed timer that you use to heat the water at specific times, just something simple.
    Anyone any experience with this unit? any suggestions welcome.

    Thanks.


Comments

  • Registered Users, Registered Users 2 Posts: 10,952 ✭✭✭✭Stoner


    Neil,

    I had a look at that switch. It says it can carry 3KW. However most domestic immersions have a 1.5 KW sink and a 2KW bath element, and the batch/sink switches decides which one is "on".
    This unit can only be used for one of these elements as it seems to be single pole.

    So to use it you'd have to drop out one of the elements. I would not recommend messing with the switching so that you would try to keep the bath/sink switch working. If it was me I'd pick the element you use the most and cable it through this.


  • Closed Accounts Posts: 1,338 ✭✭✭hobie


    I suspect the device is mounted before the normal bath/sink switch ....
    i.e. it simply controls the power to the existing switch ..... the bath/sink switch remains in use to select 1.5/3.0 KW elements ....

    Horstmann have a web site with contact info here .....

    http://www.horstmann.co.uk/

    It's a nice idea ..... :)


  • Registered Users, Registered Users 2 Posts: 10,952 ✭✭✭✭Stoner


    hehe , nice one Hobie, I never thought of that, that's the simple way of doing it, just break the feed to the immersion switch, but keep the immersion switch


  • Registered Users, Registered Users 2 Posts: 11,220 ✭✭✭✭Lex Luthor


    was going to say same as hobie and install prior to your current Bath/Sink On/Off switch.

    Nice idea alright


  • Closed Accounts Posts: 5,332 ✭✭✭311


    It's hard to locate insulated switches like these ,I definetly wouldn't order one from ebay.


  • Advertisement
  • Closed Accounts Posts: 1,338 ✭✭✭hobie


    _Brian_ wrote:
    It's hard to locate insulated switches like these ,I definetly wouldn't order one from ebay.

    This link has contact info ...... maybe ask them for Irish Distribution info ...:confused:

    http://www.horstmann.co.uk/aboutus.asp


  • Registered Users, Registered Users 2 Posts: 2,102 ✭✭✭Neil_Sedaka


    Thanks for the replies folks.
    Yeah, I was thinking it could go "before" the existing switch and simply act as a "power on / power off" kinda thing.

    Have an electrician mate that will most likely install it for me, don't like messing with high load stuff like this. Always conscious of the fire risk due to overloading etc.


  • Closed Accounts Posts: 1,338 ✭✭✭hobie


    _Brian_ wrote:
    Hobie ,it's the ampage that burns out switches.
    I was in O'riellys last month and they hadn't got any .

    I'm lost .... are you saying Radionics are selling duff equipment? ....


  • Advertisement
  • Closed Accounts Posts: 5,332 ✭✭✭311


    hobie wrote:
    I'm lost .... are you saying Radionics are selling duff equipment? ....

    Hobie ,that switch is listed under central heating controls /ventilation.

    The reason I am been anal about amperage in these switches is because ,a high percentage of house fires start at the hotpress.
    I really wouldn't consider buying stuff like this ,without actually consulting someone in a shop or suppliers ,thats all.

    Thats not me trolling or being vindictive ,I'd be concerned about stuff like this to be honest.


  • Closed Accounts Posts: 1,338 ✭✭✭hobie


    _Brian_ wrote:
    Hobie ,that switch is listed under central heating controls /ventilation.

    The reason I am been anal about amperage in these switches is because ,a high percentage of house fires start at the hotpress.
    I really wouldn't consider buying stuff like this ,without actually consulting someone in a shop or suppliers ,thats all.

    Thats not me trolling or being vindictive ,I'd be concerned about stuff like this to be honest.

    O-key-doke .... looks like NS will have it installed by a competent electrician so let's hope all his "Immersion being left" on problems are a thing of the past .... :)


  • Closed Accounts Posts: 5,332 ✭✭✭311


    It's not a lot of help ,but turning down the thermostat on the immersion might help stop energy waste.
    At least if it's left on then ,it wont keep eating too much electricity.


  • Registered Users, Registered Users 2 Posts: 2,454 ✭✭✭cast_iron


    I put in one like this just a couple of weeks ago. And as mentioned above, I found the easiest thing was to just out it before the emersion switch. That way, the odd time hot water is needed rather quickly and there's none left, just flick the timer to "on" and change the "sink/bath" to "sink".


  • Registered Users, Registered Users 2 Posts: 11,220 ✭✭✭✭Lex Luthor


    I bought a 7day/24hr electronic timer from RS a few years back....they have them with the sufficient amperage...just neeed to look harder


  • Registered Users, Registered Users 2 Posts: 2,876 ✭✭✭Borzoi


    Lex Luthor wrote:
    I bought a 7day/24hr electronic timer from RS a few years back....they have them with the sufficient amperage...just neeed to look harder

    Yeah, Grasslin, Danfoss, all make proper 7 day electronic timers for controlling immersions. Get thm at either an electrical wholesaler on even Woodies/B&Q


  • Closed Accounts Posts: 1,338 ✭✭✭hobie


    The problem is NS doesn't want a Timer ....
    We don't want a programmed timer that you use to heat the water at specific times, just something simple.
    Anyone any experience with this unit? any suggestions welcome.

    So with that his 'Boost' switch idea seems the way to go .... :rolleyes:

    but ........

    there is an alternative and it's something an electrician can put in very simply .....

    I have a coloured light bulb in our hallway (just outside the hotpress) that lights up whenever the immersion is on ..... it's a 25watt if I rem correctly so uses little power and can be seen for miles!!!! :) ...... it's bright yellow (you could have a red one if you wish;) ) .....

    ..... and the cost? ..... about 5 yo yo's plus the leccie's time to connect it .... :)


  • Registered Users, Registered Users 2 Posts: 22,818 ✭✭✭✭The Hill Billy


    neil_sedaka:

    Why not move the switch to a more obvious area? I don't know if you ever noticed but Grandpa Billy dropped the switch in his house from the hot press down into the kitchen so that it could be seen when the immersion was on when it shouldn't have been. (On the left as you walk into the kitchen from the hall.) Easily done in his house, but may be a tad more difficult in your's.

    What if you moved it to the wall on the landing? It would only be slightly more obtrusive than a light switch.

    See you later.


  • Registered Users, Registered Users 2 Posts: 2,218 ✭✭✭MBSnr


    Horstmann E15 or E30 from www.heatmerchants.ie

    Selected Product:338993

    Description HORSTMANN ELECTRISAVER E15 ELECT TIMER
    Price (Excluding VAT and quantity discounts) €32.10

    The trouble I have is they are supposed to be protected by a Double Pole switch which isolates the timer from the mains. (If you're replacing a combined on/off bath/sink switch then that is double pole - means that both the live and neutral to the immersion element are isolated). Even though the timer itself is DP. Not having a manual DP switch between the immersion and the supply probably is breaking some regulation someplace....

    I was also told that as the E15 timer is rated max 13A I should install a DP FCU (fused unit) before the timer instead of just a DP switch even though the unit is on a 20 Amp MCB in the consumer unit.

    My simple job just got a bit harder... as really you should have FCU (13A) -> timer -> immersion switch (to get bath/sink option). I plan to use FCU -> timer and not wire the sink in.

    I'm sure that doesn't really help things.

    Regards


  • Registered Users, Registered Users 2 Posts: 10,952 ✭✭✭✭Stoner


    The old Horstmann E7 or maybe Horstmann QE7 , they don't look pretty but they never give trouble.
    these units don't need a double pole switch, they have one built in, so you don't have to worry about that end of things.

    However the listed timer is only rated at 3KW once again 13 Amps.

    Also I have never seen or heard of a DP FCU, in my experience it has been a single pole FCU and a double pole switch.

    I'll look one up now, but a dual surface box, C/W first , 13Amp FCU, then DP switch, then your timer, followed by an immersion switch sounds a bit mad, IMO

    Now I am fairly sure that this could be a simple operation, I might even redeem myself here.

    The internal wiring of a HorstmanE7 is carried out buy about 4 or 5 plugs.

    It has a boost function giving heat for 1 hour and less,
    I think it is possible to arrange the plugs so that only the boost timer suppliers power to the immersion
    It will still allow you to choose between sink or bath
    and it does not need a double pole switch.

    I'll get one in as a sample and bell it out for you if you want, cos it has me thinking.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 419 ✭✭eoghan.geraghty


    This is the common controller used in new apts here with a boost/timer function but like all others I've seen there is no bath/sink option. This is because immersions put into apartments have but one element.
    Incidentally the common household immersion has 2 elements, sink 2kw and bath 3kw. Either one or other is on, never both.
    You could break the sink feed after the existing switch through this controller, leave the immersion switched permanently to sink ON. Now your controller can be used as a simple boost switch.
    But honestly the simplest option is to use the one recommended by cast_iron and you have a day to remember to unset it.


    http://www.screwfix.com/app/sfd/cat/pro.jsp?id=44419#


  • Registered Users, Registered Users 2 Posts: 2,218 ✭✭✭MBSnr


    Stoner - You're right it is overkill to a certain degree but I'm just complying with the way I've been advised. I'm putting in a DP FCU with neon before the E15. Then from the timer just wiring the bath and not the sink. Never used the sink element anyhow. If you need a sink of hot water just boil the kettle.....

    The DP FCU satisfies the requirement to be able to isolate the supply to the timer and immersion, which I'm told is a regulation(?) and also provides protection to the 13A E15 as my MCB (dedicated circuit) in the CU is 20A and not 16A for some reason.


  • Registered Users, Registered Users 2 Posts: 2,102 ✭✭✭Neil_Sedaka


    Ok, I'm a tad confused now :o

    Would I be ok fitting the Electrisaver E15 before the "bath / sink" switch, or do I need a double pole switch too?

    I was planning on leaving the "bath / sink" switch in place, should I maybe remove this alltogether and only use the 3kw feed?

    Would I be far better off removing the immersion tank, pipes etc. and converting the hotpress into a rather small, multi screen cinema?


  • Closed Accounts Posts: 1,338 ✭✭✭hobie


    Leave everything as is ...... :)

    ask Horstmann if you can simply have your electrician wire the E15 just before your existing 'on/off/sink/bath switch'

    here is the link (half way down the page) .....

    http://www.horstmann.co.uk/faqs.asp

    They seem to be a good reputable company ....
    Horstmann ... we’re in control

    As one of the UK’s leading designers and manufacturers of controls for domestic heating systems and advanced metering equipment, Horstmann Controls offers a comprehensive range of state-of-the-art solutions.


  • Registered Users, Registered Users 2 Posts: 2,102 ✭✭✭Neil_Sedaka


    Email sent to Horstmann, will update here with their reply.
    Thanks everyone.


  • Registered Users, Registered Users 2 Posts: 2,218 ✭✭✭MBSnr


    Sorry for the long post...

    Neil_Sedaka - You should be able to wire the timer before the switch to get timed sink/bath element as hobie as says. That was what I was going to do until I asked on the UK diynot.com forum..... A little learning is a bad thing!

    So this is what I found out.

    The E15 timer is rated at 13A and the supply will probably be fused at 16A or greater. The reason for me including the FCU (13A fused DP switch) before my timer is twofold.

    1. If the immersion element goes faulty it will draw up to the rated MCB in the consumer unit before tripping. If the MCB is 20A (as mine is) then it's possible a faulty immersion element would also blow the timer before the MCB acts. Adding a 13A in the circuit is perhaps "belt and braces" but it should protect the timer from those extra 7 Amps if the immersion element goes.

    2. I didn't want the sink element wired (never use it) as I have a oil boiler which does both water/central heating for 6 months of the year (longer if this summer is anything to go by..!). In the times when I need a bit of extra hot water I always use the bath setting anyhow so it suits me to remove the bath/sink switch.

    Of course you may need to use both sink/bath.... ;-)

    Horstmann are slightly vague in their replies on this timer. I both rang and emailed them. According to them the timer is not DP so you need a means of isolating both poles to the immersion element for repair etc. Your existing on/off/sink/bath switch does that if the timer is added before it, so no problems there.

    However their manual says "Means of disconnection from the supply having at least 3mm contact separation in both poles must be incorporated in the fixed wiring".

    I queried this because I wasn't sure if they meant "from the immersion to supply" or "from timer to supply" saying I was adding a DP switch before the timer and their reply was;

    "The E15 doesn't isolate both Live & Neutral so by fitting a DP switch
    ahead of it will fine. Ideally, it needs to have 3mm isolation. (if it's
    a proper mains switch it probably has it already be design). We mean in
    our leaflet that the 3mm isolation is back at the consumer unit main
    ON/OFF switch. In other words - full isolation (3mm clearance) can
    always be achieved by switching off the main switch if work is to be
    carried out on the immersion heater."

    I take from that to mean that as long as there's a DP switch in the wiring (before or after the timer) then things are ok.

    Horstmann suggest a 16A MCB to feed the circuit (there are no 13A MCBs). You might want to talk to a qualified electrician/Horstmann about the 13A timer rating if your supply MCB/fuse is greater than 16A (as mine was). I'm not qualified to say whether this is ok without additional fuse protection.

    I wired mine up last night with a DP fused switch -> timer running only the bath element.

    Like I said a little learning sometimes means more work.....!


  • Closed Accounts Posts: 1,338 ✭✭✭hobie


    Did I already say this ...... ;)
    there is an alternative and it's something an electrician can put in very simply .....

    I have a coloured light bulb in our hallway (just outside the hotpress) that lights up whenever the immersion is on ..... it's a 25watt if I rem correctly so uses little power and can be seen for miles!!!! ...... it's bright yellow (you could have a red one if you wish ) .....

    ..... and the cost? ..... about 5 yo yo's plus the leccie's time to connect it ....


  • Registered Users, Registered Users 2 Posts: 2,218 ✭✭✭MBSnr


    It'll have to strobe flash and a have a large klaxon installed for my missus to notice..... ;)


  • Closed Accounts Posts: 1,338 ✭✭✭hobie


    MBSnr wrote:
    It'll have to strobe flash and a have a large klaxon installed for my missus to notice..... ;)

    I like that one !!!!! ...... :p


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 10,952 ✭✭✭✭Stoner


    hobie wrote:
    Leave everything as is ...... :)

    ask Horstmann if you can simply have your electrician wire the E15 just before your existing 'on/off/sink/bath switch'

    OK I had a look at a Horstman E7.

    It requires a 16 Amp MCB.

    Its instructions deal with single and twin immersion heaters. For twin elements (sink Bath) you still need the immersion switch to choose between sink or bath. The instructions say that this is to be connected on the fuse side of the immersion switch.

    anyway as discussed the boost and the timer part of the E7 can be disconnected inside the box, I have included pics of this. The boost and the timer can be joined so that either or will power the element (or in your case the live into the immersion switch)

    So if you dont connect the timer element only the boost will work and it has the 2 hour setting that you were looking for NS.

    So with a 16 AMp MCB this unit can have one immersion element hooked up to the enomoy 7 and only the boost will work.

    Or as long at the immersion switch has a built in 20 Amp DP as most have you can cable from the E7 to the immersion and the immersion switch will give you the sink bath option


  • Registered Users, Registered Users 2 Posts: 10,952 ✭✭✭✭Stoner


    instructions for above attached


  • Registered Users, Registered Users 2 Posts: 2,102 ✭✭✭Neil_Sedaka


    Here's the reply from Horstmann:


    Many thanks for your enquiry.

    Whilst the Electrisaver E15 requires live and neutral in/out, it only
    switches the "Live" so it is feasible to connect to just to the Live
    bath feed. This will mean however, that you would not be able to keep
    your immersion heater on for any longer than an hour at a time.

    We make a unit called the Economy 7 Quartz which is designed to operate
    on a typical "Sink/Bath" installation allowing timed control of the bath
    and boost (2 hour) of the sink.
    This may be a more suitable unit for you.

    I hope this helps.

    If you require any further information, please do not hesitate to
    contact me.



    Regards,
    Jason


  • Registered Users, Registered Users 2 Posts: 10,952 ✭✭✭✭Stoner


    Here's the reply from Horstmann:

    We make a unit called the Economy 7 Quartz which is designed to operate
    on a typical "Sink/Bath" installation allowing timed control of the bath
    and boost (2 hour) of the sink.
    This may be a more suitable unit for you.

    This is the unit I have been telling you about, it has plugs and connections so you can do what ever you want with it, the timer and the boost (0 - 120min) are independent of each other.
    The only reason you need an immersion switch is because in your OP you only wanted a 2 hour boost to work, the E7 needs the immersion switch to give you the option of boosting either the sink or the bath.

    But that's fine just ignore me!!!!!!!!!!! :)


  • Registered Users, Registered Users 2 Posts: 2,102 ✭✭✭Neil_Sedaka


    Sorry Stoner, wasn't ignoring you :o Was just a bit bamboozled with all the options.

    But yeah, you're right, the E7 looks like it will do the job.
    Found a new problem last night though, the ex owners of the house had the attic converted and it seems that the 4 double sockets in the attic are fed from the immersion feed!! That'll have to be changed before I do anything else.

    Thanks for all the time you spent on this, I really do appreciate it, cheers.
    Thanks to everyone else too.


  • Registered Users, Registered Users 2 Posts: 10,952 ✭✭✭✭Stoner


    no probs NS, best of luck with the other electrics, I'd say there is a chance there is a couple of security lights hanging off it too


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,102 ✭✭✭Neil_Sedaka


    You could be right there, must check that too.
    Thanks again ;)


  • Registered Users, Registered Users 2 Posts: 1,829 ✭✭✭KerranJast


    Hi all. A related question so I thought I should post here. I wired in an immersion timer between the mains and the immersion switch (the on-off sink-bath panel). The immersion is still working fine but the timer isn't moving. It's one of simple 24 hr mechanical ones. I've treble check my wiring job and it's correct according to the instructions but I still can't figure out why the timer won't move. The timer is rated for 13A (3120W) and is similar to this model except that it has Live&Neutral In (from mains), Live&Neutral out (to immersion switch) and a common Earth pin, instead of being plugged into a wall socket. Is the damn thing faulty or have I screwed up the installation?

    My setup Mains
    >Timer
    >Immersion Switch---->Immersion.


  • Registered Users, Registered Users 2 Posts: 2,876 ✭✭✭Borzoi


    KerranJast wrote:
    . The timer is rated for 13A (3120W) and is similar to this model except that it has Live&Neutral In (from mains), Live&Neutral out (to immersion switch) and a common Earth pin, instead of being plugged into a wall socket. Is the damn thing faulty or have I screwed up the installation?

    My setup Mains
    >Timer
    >Immersion Switch---->Immersion.

    Not sure the current problem but I foresee two others:
    1) That timer rating is very low to switch an immersion, most elements are arount the 3.5kW mark, you're timer is at 3.12kW

    2) With the proposed wiring set up you wont be able to use the sink function when the timer is off. Really you'd need to take the feed from the Imersion Switch Bath Outlet, and run that through the timer, but that's still not a great setup. TBH an all in one timer and switch unit would be much better


  • Registered Users, Registered Users 2 Posts: 1,829 ✭✭✭KerranJast


    Thanks for the reply. I've not been able to find a timer with anything greater than 3kW rating. I thought 3.12kW would be high enough. Any suggestions where I could get a better one? I'm not too bothered about the sink function being disabled when the timer is off. We don't really use that much hot water anyway except for showers will be provided at designated times during the day.

    Edit: I found a 16A timer here . I presume that's a higher wattage but is it safe to use off what should be a 13A line?


  • Registered Users, Registered Users 2 Posts: 10,952 ✭✭✭✭Stoner


    Lads sounds like the E7 could still do what you both want.

    OP if you look closely at the time dial on the E7 you will notice a little blue and red tab. You can control the off peak times. Although they come set to work between 4.5 and 7 hours they are not limited to this. The recommend adjusting them before installation, but you can change these tabs (cams) position so that the off peak time is less then 4.5 hours if you want ( in theory). If you are interested I'll scan in the instructions for this adjustment.

    also the stat on the immersion will keep turning the element on and off so you dont really get the unit on full blast for 7 hours anyway.

    a 16 Amp MCD is recommented for protection of E7s.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 10,952 ✭✭✭✭Stoner


    might be of some use


  • Registered Users, Registered Users 2 Posts: 1,168 ✭✭✭TM


    Anybody know what the going rate in Dublin is for the Horstmann E7 (the one with off-peak timer, off/timed switch and 2 hour boost option - I think there's a variant with just 1 hour boost)? The only quote that I've got so far is c. €100 incl. VAT from Phibsboro Electrical Wholesalers. Any suggestions on where else to try that might be competitive? There are also a couple on eBay from UK sellers with low initial bids and a few days left on the auctions but I tend to prefer "buy it now" sales on eBay to be honest.


  • Registered Users, Registered Users 2 Posts: 10,952 ✭✭✭✭Stoner


    cost sounds about right TM, however if Phibsboro is near you, you can call up to me in Glasnevin and you can have one i got in as a sample for free.


  • Registered Users, Registered Users 2 Posts: 1,168 ✭✭✭TM


    Hi Stoner - that's extremely kind of you! :) I will PM you separately about it. A mate of mine in the industry also confirmed that c. €100 incl. VAT was about the norm.


  • Registered Users, Registered Users 2 Posts: 1,168 ✭✭✭TM


    Picked the unit up from Stoner's place. Thanks again! :)