BarneyMc wrote: » What's 'normally' allowed for 1st floor insulation ..
hexosan wrote: » Mine is 25mm insulation and 50mm hemihydrate screed
BryanF wrote: » What's wrong with heating up the first floor slab. Its thermally broken from the external so the only consideration is the reaction time when the heating is put on. But surely in a new build the heating is set to keep the internal temp constant?
barryoc1 wrote: » The slab is generally lined underneath with battens and then plasterboard, creating as such a suspended ceiling with a void. The heat from the floor above will only heat this void and you wont get the benefit in the rooms at ground floor level. The heat in the slab will find it very hard to make its way back up through the insulation and through the screed to be of benefit to the rooms at first floor level. If you want to use the concrete slabs as a thermal mass for the rooms at first floor level then dont use any insulation and pour the screed directly on the concrete slabs.
galwaytt wrote: » It's not thermally broken where the slabs are on the walls. 50 mm might work in a timber house and timber deck, but in a concrete one you need more. Otherwise you're heating the structure first, rooms later. I would be looking at maximising the insulation not minimising it.
BarneyMc wrote: » Spoke with my plumber and he said 50mm insulation would be fine to bury the piping. Aeroboard seems to be a lot cheaper than the rest so will likely go with that.
BryanF wrote: » 50mm Aeroboard as opposed to 30mm kingspan ?
ferryman35 wrote: » We are using 50mm in our build with a 100mm perimeter strip, and a 50mm screed.
ferryman35 wrote: » Our MHRV system uses an interesting concept - most of the ductwork for the upper floor can be attached to the underside of the concrete slabs, and just drill through the hollowcore where required.
ferryman35 wrote: » Don't want to breach any rules, but square section pipe lagging in various depths is available for incorporating pipework in the floor insulation