Heat Pumps - post here.
Hi All,
I have some questions some of you may have answers for.
I have a Ochsner heat pump for my geothermal heating system and on the information plate at the back of it, it says that it should use 3.6 KWh based on 20Amps at 230V with a power factor 0f 0.78. There is also another figure for the maximum current of 23 Amps.
My issue is that I have measured using a clamp meter a current of up to 28Amps (at 226V), I have also run some tests where I have switched off all circuit breakers in my house except for the ones used by the geothermal system. Taking account of shunt pump and controls the heatpump uses (measured over a few nights) approximately 4.8KWh. The supplier claims that this is due to a lot of heat loss in my house and that therefore the pump has to work harder. I think that this may be a fob off as the information plate clearly states that it should draw a max current of 23 Amps but to use 4.6KWh it must be drawing an average of over 26Amps. Has anyone else seen this? Is it normal? Will it affect the life of my heatpump etc. etc.