I noticed (twice) that my DC breaker has tripped when on a high charging load at 100A. The breaker gets very warm and trips. The model I have is the "DIHOOL DZ47B-125 125A", so in theory, it should be able to handle the 100A load. As a test, I've set my battery to charge at 50A to see if the issue repeats.
I have 35mmsq cable coming from the battery to the breaker and 25mmsq from the breaker to the Sofar 6000HYDEP inverter. Given the thickness of the cable, I don't have any Ferrules on the battery cable going into the breaker. I assume this is fine, the connection is very solid.
Has anyone seen this issue?