deezell wrote: » Have you wall thermostats in addition to the Grasslin? How many? Did the installer remove the Grasslin?. It was the timer unit, I'd assumed you had no wall stats. If you have more than one stat, it sounds like you have zoned heating, with Zone valves. If it works properly with these stats turned down, then there's some other source of switched power being sent to fire the boiler, just leave them down and see does the system work as it should.
raytaxi wrote: » Yeah its the only way I have is the ember stat at the moment, how would i go about mechanical stat to cylinder. Would i need to get a wire to drayton face plate ?
baldshin wrote: » 2 wall thermostats. Just turned both down and nest seems to function as expected. Will hold off on the celebrations and see if the heat randomly kicks in or stays on of its own accord!
raytaxi wrote: » I have 3 zone valves does that equal s-plan. Think i may have to go down sonoff for control as cylinder is fully insulated and just have pods for sensors. Think junction box is in garage and hot press upstairs and don't think i could get wire from one to other.
deezell wrote: » I'm intrigued. The grasslin was just a single CH and HW controller? Yet you had two stats, so two zones. Are these pumped zones, or using zone valves? Perhaps the installer made other wiring changes, combined them into one. I'm surprised he even went ahead with a single zone replacement for what is obviously a single timer two CH zone installation, but with some odd wiring arrangements. If it works, then happy days, I'd no idea it was a two zone system, but it might explain some of the odd results.
baldshin wrote: » To be quite honest, I'm unsure if they're pumped or valved zones. Scheduled heating came on this morning, but didn't circulate the heat around the house, having left the old wired dials turned all the way down. So it seems they have overriding control over the nest. I'm assuming if they can be traced back to the boiler and removed, this may be a solution? Definitely something I'd need an electrician for, the wiring itself is like a nest!
foxatron wrote: » Folks, I currently have a climote installed with 3 zones upstairs downstairs and hot water on gas boiler. I was looking to get a system where I could control individual rooms. Has anyone changed from a climote to a system like this. I saw tado wired stater sets on sale but not sure if they'd suit. Any advice appreciated.
eddiem74 wrote: » I have the following set-up and was wondering what Tado gear I should go after. Boiler: Vokera Mynute 28eZones: 3 : upstairs, downstairs, & waterTimer/Clock: next to boiler a timer that lets me schedule 3 times per zone, plus manual boost.Thermostats: Nothing on any wallRadiators: 5 downstairs, 7 upstairs with vertical thermostatic values (>15years old)
deezell wrote: » Total Nerd stuff, excellent. We should have a rating for posters. I'd award that 3 Anoraks.
deezell wrote: » Tado is still limited to one wireless receiver, so to control the two CH zones, one would have to be wired back to the zone valve for it's floor. If the zone valves are somewhere downstairs, check and see how easy it would be to run a light twin wire mains cable from a living room or hallway wall to the valves. It might be easier from upstairs, from the landing wall, via the hot press across the attic and down. An alternative is to fit the entire upstairs with TRVs, locating the wired stat as a relay for the upstairs motorised valve next to the valve, and having as many zones as their are rads upstairs, say 6 leaving a bathroom or towel rail rad open. Downstairs would use the wireless stat and the extension kit (receiver) would control the downstairs CH and HW valves. All assuming your system is zoned with a 3 independent zone timer (make and model?). Your system is ideal for the guy installation of the Drayton Wiser Kit 3, 3 zone controller. 2 wireless stats and HW control to a single receiver which just drops in in place of your current timer.
deezell wrote: » Has the Geasslin timer been removed? It would make sense that the old stats need to turned up to provide continuity to the circulation pump (pumps?) whose power is provided by the nest., but this doesn't explain how it was still circulating after the scheduled nest heating event ended. It's possible those stats supply zone valves, and they may well have a relay connection directly back to the boiler to fire it, independent of your original grasslin timer. In this case though the heating should cease when the timed interval ends, regardless of it comes from the nest or the Grasslin. If the Grasslin is still connected , just set it to off, or unhook it and cover the pins with tape for the moment. If it has already been removed, then it sounds like you have some kind of loop in your wiring, whereby a timed event is throwing a relay in a valve which is going to the boiler but also back to the timed output, effectively holding the relay open. If your grasslin was operating in gravity mode, this should not create a loop. IF there are zone valves wired to fire the boiler in addition to the direct connection from the HW relay on the Nest, then a loop will occur. But then you don't need the gravity wiring mod on the Nest. I suggest you just remove the link between pins 3 and 4 on the Nest on my diagram, which will revert it to standard two zone timer, and turn the old stats up full. Try and discover if your zones are supplied by Zone valves which have their own relays to fire the boiler. Its even possible you have a zone valve for HW, as you have 2 heating zones. You do seem to have an odd setup, but it will need to be traced to understand the logic behind the wiring. Is it possible you also have a wiring box with relays inside? If your CH zones are pumped by individual pumps rather than the flow directed by Zone valves, it's possible, necessary even, that you have such a box, often know as a Lex box, to provide relay firing of the boiler for any wall stat or HW timed event. It's a pity you didn't mention the two wall stats back in October, this would have raised some alarms, as you have a compromise system with split from the single timer to two stat zones.
eddiem74 wrote: » If going with Drayton instead of Tado, I believe this is what I need, correct?https://www.amazon.co.uk/Drayton-Heating-Radiator-Thermostat-Amazon/dp/B075GNJ7ZN They don't seem to do deals on the radiator thermostats that I can see, only sell individual?
deezell wrote: » If you want to have a crack at the installer mode, page 14 below, work though the options and turn HW mode on, your app should recognise this and enable the HW timer. Alternatively, drop support a line and ask for HW on, two wired stats. You did pop the mode jumper into position 2, with the dot on the bottom?https://drive.google.com/file/d/1KRGbtTNoust23GEX3lXtgx6akSbArrJx/view?usp=drivesdk
south wrote: » I think I may have gone wrong somewhere, the heating is working as it should but I noticed the other day that while the downstairs heating comes on as scheduled it also lights up the hot water valve and heats the water. It also doesn't show up in the app that the water is turned on. It's great having hot water most of the time but it's probably costing me more than it should.
deezell wrote: » Apologies first for that link I included with that last post. It seems to be the wrong installation manual. This is the link I intended, https://drive.google.com/file/d/1NokMAEyjxNyh5k5Kb7owcKdoN4260RJm/view?usp=drivesdk On page 14 it shows the path to enable HW control on the ext kit from installer mode. On page 15 there is a further setting to chose 'Fully pumped' or 'Gravity' by selecting Ext kit relay mode R01 or R02. This shoud be R01. In gravity mode, the ext kit assumes the the CH terminal only operates the circulation pump, with the HW terminal going live to fire the boiler for either a CH or a HW timed event. In 'Fully pumped' mode each terminal only goes live for its respective timed event, CH or HW, and these lives then turn on the appropriate zone valves, whose built in relays calls the boiler. You say your HW valve is also opening for a CH event. For a HW timed event without CH, I presume only the HW vavle opens. If both downstairs valve and HW valve open, then it indicates the output wires are crossed. If HW valve only opens this would indicate that the ext kit is in Gravity mode, with HW terminal going live for either a downstairs CH event or a HW event. You can request support to put the ext kit in "Fully Pumped', R01 relay mode, and then your HW valve should open only for HW timed events. You can change it yourself by entering installer mode on the downstairs stat. 3 sec press to bring up the two link symbol, release, 3 second press to bring up the installer symbol, release, 3 second press to start this mode. You can step through the different settings without changing them, reading off each setting as you go, TS > HC01 > HW✅ > Ek✅ > R01 ( if this is R02, use arrow keys to change to R01). Another press to SAVE, then a short time to upload and back to the standard display.
south wrote: » Thanks Deezell, this looks to have sorted the problem out.
legend99 wrote: » Reporting 44 now! I was also thinking I'll need to take 2 approaches. One report with the Sonoff calling for heat. And one when not calling for heat to just see what the water mixing and settling does in terms of what temp it stabilise at. Hopefully someone does can report back what timing schedules/temp schedules they are using on it. Don't want to make a balls of it and make it worse! P.S. And I very much appreciate your willingness to award 3 anoraks - what a day to be alive!!
deezell wrote: » ... 4. I can think of three options. a. If you get the ext kit, but continue to use the Danfoss for HW timing, you can use the ext kit HW live signal to operate a mains relay for your electric rad, which I assume has its own built in stat. b. If you want independent control, just add an additional tafo stat to the garden room, use it's output to switch a mains relay to turn on the electric rad. c. Alternatively, you could link a tado zone via smart software such as IFTTT to operate a smart mains switch/socket, so when say " Kitchen Zone" is on, IFTTT will detect and operate Garden room mains relay.