    I have a fault occuring every once and a while.were my alarm is not set but goes off. It sounds strange but seems to go off on Sunny days between 10 and 11. My panel says 17 call engineer


«1

Comments

  • Registered Users Posts: 6,827 ✭✭✭fred funk }{


    Are you sure it says 17?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    I'd say it's 77.
    What displays after you disarm the system after an activation?


  • Registered Users Posts: 11,657 ✭✭✭✭altor


    robs1 wrote: »
    I have a fault occuring every once and a while.were my alarm is not set but goes off. It sounds strange but seems to go off on Sunny days between 10 and 11. My panel says 17 call engineer

    17 indicates a faulty sensor on a loop.
    If it is going off like you say it may be an environment issue.
    Any PIRs facing a window or getting a glare at this time?


  • Registered Users Posts: 91 ✭✭robs1


    When it goes off it comes up on the panel zone 3 and then flashes up sensor contact panic. the only pir i have is in the hall and is well shaded. somone said to me it could be the end of line resistor going and with the sun shining on it causing this problem. i have never heard of thus before. yes its 17 showing


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    Sounds like a very bad connection on zone 3 possibly the EOL resistor is not tight.
    Sensor refers to shock sensors and not the PiR.


  • Advertisement
  • Registered Users Posts: 11,657 ✭✭✭✭altor


    robs1 wrote: »
    When it goes off it comes up on the panel zone 3 and then flashes up sensor contact panic. the only pir i have is in the hall and is well shaded. somone said to me it could be the end of line resistor going and with the sun shining on it causing this problem. i have never heard of thus before. yes its 17 showing

    If it is showing 17 and not saying anything to do with the end of line resistor then it may be a faulty device or two on this zone.
    The only way to check this is with a multimeter.


  • Registered Users Posts: 91 ✭✭robs1


    How should i check with a multimeter. do i disconnect each device


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    Disconnect the zone from the panel & remove any end of line resistors,
    Set you meter to continuity and connect the pair to the 2 meter leads.
    on a lenght of cable long enough to reach all your windows on zone 3.
    Make a note of the reading in ohms. One by one tap evey sensor & open and close every contact. After a tap or an open close the resistence should return to the around the same value. If it does not disconnect that device , close of the pair wired into it & move on. Replace any that you had to close off.


  • Registered Users Posts: 11,657 ✭✭✭✭altor


    robs1 wrote: »
    How should i check with a multimeter. do i disconnect each device

    You could if you wanted to do it that way. Just remove the resistor to close off the end of the zone and do the same in the control panel. Another option if you can get someone to give you a hand is to just get them to stay at the control panel with the meter with resistor taken out of the end of line. Set the meter to 200 ohms. The reading should be 0. Now go around taping each sensor, any sensor that does not return the meter to this value after you tapping or opening the contact, take out of the loop and move on. Replace any you find faulty. If the value is already higher than 0 then see which sensor you tap or open the contact on that returns this to 0. Take it out of the loop and check all the sensors again.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    If you are metering out the entire zone from the panel the reading will be higher than zero. An average 3-4 windows could read around 5 ohms or more depending on the length of the cable. If its excessively high to start with close off each sensor one by one to see which brings it back down.
    Then test the other sensors by tapping each one a few times & check if the value returns to the same level. Ignore percentages of one ohm in the difference. eg 5.1ohms to 5.3ohms or 5.4ohms wouldn't warrant changing the device.


  • Advertisement
  • Registered Users Posts: 11,657 ✭✭✭✭altor


    Are you checking this on continuity or ohms :confused:


  • Registered Users Posts: 91 ✭✭robs1


    That's great lads ill give that a crack tomorrow


  • Registered Users Posts: 11,657 ✭✭✭✭altor


    robs1 wrote: »
    That's great lads ill give that a crack tomorrow

    Your welcome, any problem let us know.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    altor wrote: »
    Are you checking this on continuity or ohms :confused:
    Ohms of course
    altor wrote: »
    Set the meter to 200 ohms..


  • Registered Users Posts: 11,657 ✭✭✭✭altor


    Must of being lucky over years: Always get 0 unless there is a faulty device and that would be with 8 or less devices, sometimes even more.


  • Registered Users Posts: 6,827 ✭✭✭fred funk }{


    altor wrote: »
    Must of being lucky over years: Always get 0 unless there is a faulty device and that would be with 8 or less devices, sometimes even more.

    You should almost never have zero. There's always some resistence.


  • Registered Users Posts: 11,657 ✭✭✭✭altor


    You say almost?
    If there is a fault then yes there would be a higher resistance.


  • Registered Users Posts: 6,827 ✭✭✭fred funk }{


    Yes, almost. Depending on the gauge of the cable, the bigger the gauge the less resistance. With a pair of seven strand alarm cable there's relatively high resistance over a small distance.


  • Registered Users Posts: 11,657 ✭✭✭✭altor


    Yes, almost. Depending on the gauge of the cable, the bigger the gauge the less resistance. With a pair of seven strand alarm cable there's relatively high resistance over a small distance.

    Never came across this but will keep it in mind.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    Even a perfect run with one perfect sensor an average cable run in a normal house will show a couple of ohms. Connecting directly to a perfect sensor you may get closer to zero.


  • Advertisement
  • Registered Users Posts: 6,827 ✭✭✭fred funk }{


    altor wrote: »
    Never came across this but will keep it in mind.

    How do you test for a faulty sensor on a zone? Just curious, we might be talking about two different things.


  • Registered Users Posts: 11,657 ✭✭✭✭altor


    How do you test for a faulty sensor on a zone? Just curious, we might be talking about two different things.

    I set my meter on 200 ohms to test the devices.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    By connecting the meter to the entire zone at the panel?


  • Registered Users Posts: 11,657 ✭✭✭✭altor


    KoolKid wrote: »
    By connecting the meter to the entire zone at the panel?

    Disconnected from the panel, yes.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    Just to be sure I'm getting this right. You take out the EOL(S) and then connect the cables at the panel to your meter & get a reading for the whole zone?
    If your doing that the reading would never be zero.


  • Registered Users Posts: 11,657 ✭✭✭✭altor


    KoolKid wrote: »
    Just to be sure I'm getting this right. You take out the EOL(S) and then connect the cables at the panel to your meter & get a reading for the whole zone?
    If your doing that the reading would never be zero.

    Really???
    Are you trying to say I lie?
    Here we go again....


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    Any engineer will tell you any length of cable with any number of devices will have some resistance on the cable. An average upstairs of a house with 5 or 6 windows on a loop would be 4 or 5 ohms for example.
    Zero ohms would be a direct short on a meter or so of cable.


  • Registered Users Posts: 11,657 ✭✭✭✭altor


    I am an engineer. I am telling you what I am getting on 200 ohms.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid




  • Advertisement
  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    By the way alarm cable would probably be around gauge 22.