2011 wrote: » It should not reset if there is a fault present. If I were testing this I would disconnect the cables from the load side of the unit (because I am a qualified electrician). If it can be reset when this is done it would suggest a fault downstream of the RCD is preventing the unit from resetting. If it was still not possible to reset I would conclude that the RCD is faulty. By the way Garo are not known for producing quality components.
meercat wrote: » 2 quick checks 1 make sure the rcd isn't fitted upside down
meercat wrote: » 2 quick checks 2 turn off main switch fuse and all mcbs and see does it reset now(turn on all mcbs one by one)this may not identify neutral-earth faults.
Gautama wrote: » Some good news: The middle position is not labelled at all, whereas the On and Off positions are labelled (I and O respectively). This is the reason I'm confused by the behaviour of the RCD. I'd made the (incorrect) assumption that the trip position would be the same as the Off position (as is the case with every MCB I've ever dealt with), and that this middle position was a fault. I pushed the switch down to the Off position (for the umpteenth time) but I pressed it with much more force this time. Sure enough, it clicked into that position and remained there. Then flicked it up into the On position and everything is hunky-dory again.I'd have felt like some tool had I called an electrician.
Tuco88 wrote: » Can anyone clear this up for me? I can never get to the bottom of it I'm not really a domestic Electrician, You are to upgrade an old fuse board lets say it's DZ fuses so on. Main supply is 16mm² cable from 80amp ESB HRC fuse next to the board. You install a new consumer unit do you have an 63Amp MCB or Switch Fuse as your main over-current protection? I know the method is 63amp MCB in an IP enclosure to an Isolator in the consumer unit for a new install this is not the case tho. I am aware it states that 533.3.5 states it must be an MCB(which I am stating) personally id rather the Switch fuse. I only ask this because there is a number of us have different views on it and id like to set the record straight. The job will be RECI inspected we are due one so we don't want to give them an inch.
Risteard81 wrote: » If the tails are more than 3m long then you must have an MCB in IP rated enclosure in the Pirelli Box as the main overcurrent protective device. As you say a switch fuse is better to ensure discrimination/selectivity but unfortunately that's what you have to do.
Tuco88 wrote: » There less than a meter, looks like it's an MCB so.
Risteard81 wrote: » Why? I said it's only required if they are >3m (not less than!). Although RECI Inspectors generally like to see it done anyway, but there is no requirement if <3m.
Tuco88 wrote: » I might have put you off a bit my mistake. Basically as per ETCI 533.3.5 page 108 must my main overcurrent device now be an mcb fitted in the panel.. So the good old switch fuse is gone?
Risteard81 wrote: » As I said, only if the tails exceed 3 metres. Otherwise a switch fuse can be used in the distribution board.
Tuco88 wrote: » Ok cheers Risteard81, it looks like anther rule I can't understand that makes no sence to me... says mcb but not an mcb...
Risteard81 wrote: » It doesn't state MCB except for if the tails exceed 3 metres though.
Risteard81 wrote: » The bit you are quoting only relates to where the main overcurrent protective device is to be located within the meter cabinet.