kingden2006 wrote: » sorry the power factor is normally a lagging power factor never leading and the phase are 120 degrees out of phase..
kingden2006 wrote: » doing phase 6 in sligo IT arse biscuits..
kingden2006 wrote: » would i not need the length of 2 sides for that?
kingden2006 wrote: » no can"t seem to get my head around it 2011,you"d think i would remember stuff like this especially since i"ve only done phase 4 this year,and got all credits..um
kingden2006 wrote: » no i would not have covered this type of question yet
yes i understand the phasor diagram in 56
kingden2006 wrote: » thanks 2011 and a happy new year to you.
kingden2006 wrote: » 4.21 amps in the neutral,is this right?
HC1 20 SIN 0=0 VC2 30 COS 150=25.98 HC2 30 SIN 150=15 VC3 40 COS 270=0 HC3 40 SIN 270=-40.
2011 wrote: » With this type of question most of the marks will be awarded for the method used and drawing the above diagram. A mathematical error would result in only a small reduction in marks. I would not get too hung up on simple maths.
kingden2006 wrote: » anyone tell me where im going wrong on this one? I1=40 AMPS AT UNITY. I2=30 AMPS LAG VOLTAGE BY 30 DEGREES I3=30 AMPS LEAD VOLTAGE BY 30 DEGREES.. VERTICAL AND HORIZONTAL COMPONENTS. I GOT... VC1=40 HC1=0 VC2=-25.98 HC2=15 VC3=0 HC3=-30
arse..biscuits wrote: » The marking system is 1 or 0