Stove Fan wrote: » Hi:) Is the flue it's joining too a stainless steel twin wall insulated chimney? 11 inch external and internal 9 inch? Any chance of a photo? Stove Fan:)
Stove Fan wrote: » Hi:) This stove is a bit more shallow. It has a 24kw boiler too:)http://www.stratfordboilerstoves.co.uk/models/freestanding-stoves/stratford-tf90b-boiler-stove.html You have quite a few rads:cool:. What are your rad sizes, singles or doubles and we will make sure the stove is the right size for your house:) What is the room dimensions and insulation levels where the stove is being installed? We don't want to roast you alive:eek: Stove Fan:)
tipptom wrote: » Thanks for reply,its measuring 11" internal,its a square fireplace about 4 ft tall and then there is a metal tube going from the top of that out through the roof.The outer metal tube must be 2 ft wide that goes through upstairs and out through the roof beleive it or not.The chimney then goes out through a lower slant in the roof in what looks like a twin wall insulated pipe for another 2 metres approx.Unfortunatly he lives in the midlands so i have no pics.He refuses to tell me how much this was as an extra on the house but it was a disaster that smokes now and again.They brought over an expert from Germany who started on about his timber being to wet.Dont know what that had to do with his chimney on an open fire but he was hoping the stove would work for it.
avfc1874 wrote: » we have 9 double rads 3 x47"x4". and six 4"wide average of 35" long.then we have 5 singles average 35"LONG.THE ROOM THAT THE STOVE WILL BE IN IS 12FT WLDE AND 18FT LONG. not too sure about the insulation levels its a dormer house built 6 yrs ago. thanks
damian139 wrote: » Firstly, thanks stovefan for advice to date! To install cara inset stove I've cut the fireplace sides to increase the opening and removed the fireback. The floor of the opening is now lower than the hearth- what should I use to being it level-fire cement? Also, would the insertion of fireboard adjacent to the other faces of the stove be advisable? Thanks in advance!
Stove Fan wrote: » Hi:) From a rough calculaton of your 8 rads I calculated 13kw for a boiler stove or 45,000btu and 3.5-4kw output to the room. I prefer steel but both have their merits. It's normal to heat the water by the stove or a seperate immersion heater. You may be able to seperate the rad and water heating from the stove depending on the stoves controls but there really wouldn't be much point as the stove has to be lit anyway. If you just want hot water light a very small fire. Stove Fan:)
Stove Fan wrote: » I have done a rough calculation of your radiator outputs. You are looking for a 24kw boiler stove to run your hot water and all of your rads. On your room size you need around 4.5kw to adequately heat it. I think the stratford TF90 is your best bet:) Stove Fan:)
newbie4 wrote: » Hi Stove Fan Just wondering what you think of think of this system A henley "the Blasket 21kw" stove Piped into a buffer tank 300l Of that I will be heating 5 large rads 4 small rads a couple of towel heatres and some underfloor heating hoping that it will take the work away for condenser boiler Just wonderin what u think will it work? E850 for stoove by the way
avfc1874 wrote: » hi stove fan the wife has decided she'd prefer the glenmore instead of the stratford TF90 they both have simillar out put to water,but the glenmore has nearly double the out put to room 8.5kw and the stratfordTF90 has 4.5KW. i'm worried that the glenmore would overheat the sitting room which is 18ft by 12 ft. i don't want to have to leave the door open because it's to hot. thanks for any advice
Stove Fan wrote: » I think you are going to be too hot:( especially if your room the stove is in is well insulated and is not open to the stairs or you can't open double doors to another room(s) We have a room thats very well insulated thats 6.2m by 5.7 with a ceiling height of 2.8m. 4kw adequately heats this room in the coldest weather. It's a new cavity walled extension. I don't think opening one door would be enough to cool the room. Stove Fan:)
Rob_talisman wrote: » Unfortunatley neither of those two stoves are reviewed on that site... Good news is the hunter glass is flat, no curves and replacement is <£20. Hmmm decisions desicions.
potter on wrote: » hi Stove Fan, Did a calculation using the website you provided, looks like we'll need between 11-12KW output in total. the stanley cara only provides 8KW, a bit short. I guess we should get one that is adequate rather than one which is short in terms of output. Thanks for your help
Reyman wrote: » I have a bungalow and I'm hoping to put in a stove with 6/7kw output. I'd like to get one with a boiler included to heat the water in the cylinder, which is only 4/5 feet away. The heat split would be 3kw to room / 3kw to the cylinder/water A couple of questions: 1. It's a bungalow so the cylinder is at the same level as the stove and I don't think a 'gravity' flow heating of the water will work? Does anyone know a way of overcoming this (without raising the cylinder, which would be pretty difficult)? 2. What 'head' do those gravity water heating systems need to work properly? 3. I seem to remember in the old days that gravity water heating back boilers were always made of copper because of problems if dissimilar metals were used with constantly changing water. eg copper pipes/cylinder and steel boiler. Is this not a problem anymore?
Reyman wrote: » Thanks Stovefan - that's a useful lot of information, though I can't see myself putting the cylinder in the attic. It was freezing up there last winter because it's very well insulated to keep the house warm. I take your comment on using indirect heating of the cylinder by gravity - it would be pretty inefficient versus circulating the water directly through the boiler. Do you happen to know what height of a head is needed for gravity circulation to work? Have you ever heard of anyone putting a pump in the circuit to get over the problem? Are gravity circuits usually thermostatically controlled?
Reyman wrote: » Thanks Stovefan. I'll have to shift the cylinder, which has about half dozen pipes going into it! By the way you said I should go for the stainless steel boiler - presumably this avoids any issues with corrosion? Is there any difference between the built in boilers and the clip on ones offered by some manufacturers?