2011 wrote: » It works a bit like this: design current (A) < protective device rating (A) < current carrying capacity of the cable. There are other factors that may require a larger cable to be used such as lenght of run, high ambient temperature etc.
What is happening in the circuit?
It still doesn't answer how he has determined which size MCB he should use.
Or have I completely missed the point!!!!!!!!!!!!
NoseyMike2010 wrote: » Or have I completely missed the point!!!!!!!!!!!! :o:o:o
Stoner wrote: » in short, the circuit will require a certain amount of electrical current to supply its load, or power requirement (Power = voltage x current) You then select the cable size that can carry that current over that distance from the fuse/MCB board. (using tables in the latest wiring regulations) You then select and MCB to protect that cable, i.e if the cable can carry 11Amps max you could select a 10Amp MCB to make sure that the cable does not burn out due to over current. So if you want to find the cable size, and then the MCB size you need to know what you want to supply on the circuit and find out how much power it will use. there are other consideration, regulations etc but this is the basic first step approach.
Randyleprechaun wrote: » MCB's are put in circuits to protect the cabling and the cabling only, Therefore, the only thing you need to consider when trying to size a breaker is the cable size!!!! Discrimination of course should be taken into account but it is cable size that is of most importance. Obviously, the size of the cable will be in line with loads, volt drops etc etc.
M cebee wrote: » you consider the load when sizing the breaker you consider the breaker when sizing the cable
you consider the load when sizing the breaker you consider the breaker when sizing the cable
NoseyMike2010 wrote: » What are fuses needed for? And how do you determine what value fuse you need to protect a system? I will scan some of my work later and hopefully it will show me grasping the idea of whats happening in the system! Thanks to all for helping and replying :)
What are fuses needed for? And how do you determine what value fuse you need to protect a system?
Basically, a mechanical or process engineer will design something and produce a P&ID which will not only show the mechanical elements of the project but also all the instrumentation required to operate it.
To be honest, I don't think that circuit diagram makes any sense. Not on it's own anyhow. I'm open to correction but I don't believe an AI card can read fibre optic light pulses.