I have a C35 condensing boiler operating 1 manifolds around 18 kw, 1 manifold around 11kw, 11 radiators, 4 towel rails & trench heating. My issues are as follows
1: Boiler overheats
2: Boiler struggles to get to set point and if finally reaches set point, flow will increase by 10C
3: Boiler cycles on and off every 2 mins
4: Boiler blows water out the condensate pipe, dries out the trap and melts the condensate pipe.
5: On the flue analyser the settings are as follows: Danfoss nozzle .65 80S, 12 Bar, Air 5, CO2 12% flue gases 134C, excess air 43%.
Can anyone help me as to what is causing all these issues please. UFH manifolds run 80% of the time there is no buffer tank of LLH on the system.