Assuming a power factor of 0.8:
With 80 Amp fuses there's a theoretical Maximum kW Load = (√3 x 415V x 80 x 0.8) / 1000 = 45.2 kW
With 80 Amp fuses there's a theoretical Maximum kW Load = (√3 x 415V x 100 x 0.8) / 1000 = 60.3 kW
If i want to run a 48kW electric boiler, do i need to ensure ESB install 100amp fuses?
Also, is there any limit / restriction on cheap night rate elec i can use (with a Time Of Use meter)....e.g. Energia Night Boost: 02.00 - 06.00 cost per kwh = 12.64 cents....
Could i in theory pull down 60.3kwh @ 12.64 cents for 4 hours every night?