ivegotaseri wrote: » title i need to go from 16,16,10s to 16,16,16s, what is actually involved in the process, eg would the electrician have to check all sockets, lights etc or is it as simple as open the meter and the board, remove old tails install new tails and test. in the time of covid id put it off for another few months if it req the electrician to go from room to room.
JL spark wrote: » Why are you only going with 16s ? Your as well off to pull in 25s when your at it , any new builds we are at 25s are standard
ivegotaseri wrote: » title i need to go from 16,16,10s to 16,16,16s,
2011 wrote: » So you only need a larger earth? That is unlikley to make difference to the earth fault loop impedance (which would be the main reason for doing this). How long are the tails approximately? I would be looking into this a bit more if I were you!
2011 wrote: » If for whatever reason you need to upgrade the tails I would recommend that you go for increased size on all as has already been suggested by JL spark. I would also select 25 mm sq for all three. This would be good from a future proofing perspective as these would have a greater current carrying capacity (so better for an EV). Also the additional cost would be minimal. Replacing the earth only makes no sense whatsoever. I would be looking for another electrician if it was me. For the record I gave up working as an electrician a very long time ago.
JL spark wrote: » You made the right decision giving up
JL spark wrote: » You made the right decision giving up , Trade is on its knees, Just regarding the tails , I would also say get a second opinion, a lot of lads out there doing guess work
ivegotaseri wrote: » thanks for the advise, ill give the rec a call and clarify exactly the reasons for the upgrade and ring around next week after the bank holiday to get a 2nd opinion
2011 wrote: » I would be interested to know what the REC says. The explanation may show that there is more to it than what has been outlined above.
ivegotaseri wrote: » the earth appears to be caught on something in the wall or that the earth is about 2 to 3 foot shorter than the 16s
is rubbing against the block where the entry into the attic is
has no slack,
while there is no visible damage he would prefer to be cautious.
apologies this is an old thread but i have to get tails upgraded for a ev charger install. Ive had two electricians call - one said needed new tails, new earth to gas boilier, hot water cylinder.. and that be it.. the second said same but also said because the meter is being opened the house needs to be recertified.. if it makes an difference i just had a smart meter upgrade a few months ago.. he said the certification process is a pain and he will basically need to remove any metal light switches that arent earthed (id be ok with this) but also remove the kitchen metal light fitting and the two light fixtures downstairs in the living room and dining room.. both are chandeliers.. nothing fancy but are a mixture of metal and wood.. this will be kinda of annoying - never mind the cost - just picking out new lighting etc.. do they have to be removed? is the certification process required? house is circa 1980
the gas boiler was upgraded a few years ago and they brought earth to cylinder and gas boiler but they arent strong enough?
You'd have the ESBN side which is the supply to cabinets and their equipment in cabinet , that's their side of an upgrade
Consumer side is the main protective device in the cabinet, tails, main board ratings and earthing
The tails itself is only a part of the chain and you know what they say about the links on a chain
Yes. A Cert 1 is required.the whole house has to be tested and pass in order for the certificate to be issued.sometimes issues are discovered during testing and need to be rectified or a notice of potential hazard issued. Your installation is 40 years old and it’s possible a full Rewire may be recommended as it may not pass the insulation resistance testing along with other discoveries.