iffandonlyif wrote: » When turned on, my power shower immediately trips the circuit breaker but remains running. That’s been going on a few weeks. Recently, my kettle tripped the breaker after being on for a minute or so. That’s something that’s never happened before or since. I don’t overload sockets and I’ve no unusual electrical appliances, etc. I’d appreciate anyone’s expertise.
iffandonlyif wrote: » Thanks again everyone. I’ll take the advice on not showering. I had one this morning, so that should do me till whenever an electrician can come! You’re right, Punisher, that most lights are unaffected. Just the main and mirror lights in the bathroom. And, yes, the test button on the top right works. As you probably knew, it trips the shower. I’ll mention a separate RCGO.
DublinDilbert wrote: » Based on the description and picture of the board, it looks like the shower is on it's own RCBO, but is tripping the RCD for the sockets when running, but the shower continues to run. Possible Earth-Neutral fault on the socket circuit or an appliance What you could do is try to plug out / switch off all appliances and see if you can identify if it doesn't happen when a specific appliance is turned on. The ones i would turn off first are Washing machine, Dryer, Immersion etc... If you can't narrow it down to a specific appliance this is a job for a REC.
DublinDilbert wrote: » Based on the description and picture of the board, it looks like the shower is on it's own RCBO, but is tripping the RCD for the sockets when running, but the shower continues to run. Possible Earth-Neutral fault on the socket circuit or an appliance.
iffandonlyif wrote: » and put some temporary arrangement in place.
iffandonlyif wrote: » Electrician out today diagnosed the problem as being the 'ancient' power shower
and put some temporary arrangement in place.
I'm dubious, but I know so little.
My father dealt with him and has a track record of giving misleading information or failing to properly oversee work being done.
Henry... wrote: » Obviously the rcd and rcbo should operate independently if I'm reading that right
iffandonlyif wrote: » I don't know for sure but I've been told the solution means the switch will no longer trip.
That can surely only mean something dodgy, right?
I appreciate all your warnings, but having passed them on to my father, there's nothing else I can really do beyond avoiding using it myself.
punisher5112 wrote: » Shocking stuff to be honest.... It's such a risk. I didn't look back but isn't it 63amp that's tripping. I'd want that properly investigated.
tDw6u1bj wrote: » On the same neutral busbar so you still have that leakage path? High loads tripping the RCD seems like pretty classic N-E fault behaviour, no?
Henry... wrote: » Not quite following everything on the thread RCDs and Rcbos should operate independently of each other If they don't it means the distribution board is configured wrongly
punisher5112 wrote: » Shocking stuff to be honest...
tDw6u1bj wrote: » I'm no expert or anything, but is there a reason it wouldn't be possible for current from the RCBO to find a route to earth via a neighbouring RCD that has a neutral-earth fault somewhere on it?
Henry... wrote: » Hmm I dunno if I'm getting this right You'd have a few parallel paths for fault current -Main protective conductor -Earthing conductor -Fault paths Would there be enough current through the fault path to cause an additional imbalance tripping the rcd
2011 wrote: » Not quite. A fault current could be phase to neutral, or phase to earth. A fault current to earth could be via the circuit CPC and / or other. "Other" could be any combination of pipework, water, a metal bath, concrete, wet things.... A domestic RCD should trip when there is a difference in between the current in the phase and neutral flowing though it >30mA.
Henry... wrote: » Would there be enough current through the fault path to cause an additional imbalance tripping the rcd
Henry... wrote: » You're mostly confirming what I said
Not sure what your point is
The L-N isn't relevant here
tDw6u1bj wrote: » You're saying that neutral to earth leakage doesn't happen?