salnado wrote: » Hi, I am looking for some Tado advise, apologies if it is already covered above. I have a Vitodens 100W WB1W boiler, an upstairs circuit and a downstairs circuit both with wired thermostats, and a hot water circuit with a strap-on cylinder stat. These are all wired, via a wiring centre to an EPH T37-HW controller as in the attached drawing. The thermostats are poor and the downstairs one is badly located so I purchased the Tado wireless smart thermostat starter kit and an extra smart wired thermostat on Black Friday. They arrived last week, but on starting the install Tado's app says they don't support the EPH T37 HW. Initial response from Tado's support is "Unfortunately, we are not compatible with a three channel programmer, so you can not replace that device with our Extension Kit" and advised me to return the wireless stat and put in two wired stats and use the existing controller set to constant for the heating circuits. This is not ideal due to the location of the wiring for the downstairs stat. From what I had read here, I thought that I could install the wireless thermostat for the downstairs circuit and the wired one for upstairs and was prepared to pull apart and rewire from the wiring centre if necessary. Can anyone tell me if Tado's response is my only option or if I can wire it up the way I want it. Thanks in advance
deezell wrote: » Sounds like it set up as full S plan, though Im curious about HW heating when only a ch zone is active. If all three zones have valves, will be independent, if HW has no valve or it's valve is latched/stuck open, HW will heat for any event. You've a bit of testing to do, it should operate exactly like the Horstman, but with the addition of the TRV zones.
deezell wrote: » The CH1 and CH2 outputs are paired to the wall stats, but also to the TRVs. Any TRVs you pair to an output will open the corresponding valve, so don't pair a TRV on an upstairs rad with the downstairs CH1 output. Unless you have a full TRV setup in a zone, other rads in the zone will only heat when a TRV calls the zone. Pairing the wall stat and locating it in a general area, hall/living downstairs, landing upstairs, will allow general control and accurate temperature for the zone, while TRVs in the zone will fine tune their rooms, or turn them off when not needed, e.g., spare bedrooms, or living room in the afternoon. Reading ahead to your next post you say you have zone independence, but in this post you say HW always heats when any CH zone is on. This sounds like a gravity system, or the Horstman was switched to gravity mode. I checked, there is a switch or jumper at the back of the unit. See if it was set to gravity or pumped.
eddiem74 wrote: » I wired per your suggestion above and ran the App set-up. Upon completion Hot Water was all that was visible in the App. I then proceeded to swap out all the radiator values with the Drayton ones. 3 radiators had those little pinheads that would not move even after WD40 so still installed the new values for the moment. At this point I had done nothing else and had not installed the 2 room stats I had gotten, was unsure with the radiator values if they were needed or not? Per the default app schedule at 4PM it was to set rooms to 20degrees and i could see from the stats some rooms were at 17degrees. So I just waited and at 4PM the boiler kicked in and I can see on the App any rooms that are below 20degrees have a fire symbol. I set hot water to off as typically when I run the heating / radiators in the winter the hot water heats as a result so I do not need to have hot water on, per the old wiring/timer. I assume still the same or?
deezell wrote: » Looking at this closer, there are two brown wires from the HW ON terminal 5 on the Horstman. If your system is a three zone valve S plan system, there would be no requirement for anything other than a single live to each zone valve, the zone valves' relays in combination firing the boiler and powering the circulation pump. There is a possibility that your system is wired without valve relays implemented, there's been a rash of these in recent posts. In such a system a single timer or a HW zone operating in gravity mode fires the boiler for all zone events. I'll take a look and see if your Horstman has a gravity mode switch and get back to you.
deezell wrote: » The supply Live to L appears to be looped to 2, 4, and 6, and from 6 out the back of the baseplate. Perhaps the installer thought these were COM terminals for the 3 relays, rather than as on the diagram where COM is internally wired in the unit from L, and 2,4 and 6 are NC terminals for each relay. It may be the case that a different unit was on the same baseplate previously, and had this requirement. Physical baseplates are semi standardised, but individual manufacturers use of the pins is not. What is clear is that there is no switching involved, as all 3 terminals are held live. So all you need to do is make sure that the brown wire from 6 that goes out the back of the plate is connected to Live on the Drayton plate, all the others have no function. So your wiring instructions are; Change the basplates, terminals 1, 3 and 5 of the Horstmann to terminals 1, 3 and 2 of the Drayton, and external wire to 6 on the Horstman to L on the Drayton. Live and Neutrals on the Horstman to the L and N on the Drayton, discard any loops.
eddiem74 wrote: » So removed the existing programmer and this is what is there in terms of wiring. It looks like there are wires looping between the off positions if I am reading everything correctly. Does this look normal before I proceed further?
deezell wrote: » Yep. Straight swap. Change the basplates, terminals 1, 3 and 5 of the Horstmann to terminals 1, 3 and 2 of the Drayton
deezell wrote: » At least its just wiring, actual plumbing is done.
John mac wrote: » future proof , gona swap out the ball valve i have with a motorised valve in the summer , (although i have been saying that for 16 years ) ..
John mac wrote: » Smashing thanks .
eddiem74 wrote: » Interesting post above, same question for me. Will the drayton valve fit?
John mac wrote: » my system is a simple one , power in and power out to fire the boiler . i have the two channel version , so what i need to know is what terminal do i use to send power to the boiler ? _______________________________ think i may have it / like this ? or do i wire it as the single channel
eddiem74 wrote: » Interesting post above, same question for me. Will the drayton valve fit? Also when removing the old valve is there any servicing that should be done? I vaguely recall my plumber saying to check the pin the valve sits on, perhaps some WD40 and some pushing in/out with a plyers? I might be dreaming though...:o
deezell wrote: » Check out the previous discussion with RayTaxi, his situation is identical, 3 zone valves, but a single old timer firing the boiler, the zone valves controlled by stats but the valves themselves not connected to fire the boiler when called, in a proper S plan setup. If you keep the valves, and seperate the operation of the HW valve from the CH valves, you can have independent HW only in the summer. HW valve can be operated by a cylinder stat, in combination with the currently unused HW timer terminal of the ext kit. The CH terminal of the kit can be used to open both the CH valves, but to achieve independent firing of the boiler, the valve relays will have to be wired in S plan to fire it, no direct connection from the ext kit. This way when no TRVs are calling for heat, all rads will be closed, and a call for HW will only open the HW valve.
deezell wrote: » You can latch the valves open to convert everywhere to a single zone. It this case the old stats can be left full on or removed. What's currently firing the boiler, the ext kit? I'd use its CH on as live to fire the boiler on behalf of the TRVs, but also use its HW contacts to open and close the HW valve. You'd then need to wire the HW valve relay (currently unused) to fire the boiler to get HW only operation when all the rads (bar two) are closed. If you don't want these two to heat during a HW only timed event, connect the CH on from the ext kit to both CH valves, then no radiators will heat during a HW only call, and only the active TRV rads plus the open two rads will heat during any CH event. If you continue to use the two CH valves, turn old stats up full or short their wires to maintain a connection of CH ON live from the ext kit, which formerly was supplied by the output of the old single timer.
raytaxi wrote: » My existing system is the last one and zone one is hot water, just need to run cable to Stat on cylinder then between 6 on each board. So that when water is at heat it opens and goes off ? The stat you have pictured can the probe go into a cylinder pocket as mines fully insulated and has 3 pockets for stats.