championc wrote: » The Irish standard allows for 230v +/- 10%, so it indeed should shut down at 207v. See section 2.2 of the Irish Regulations here - https://www.esbnetworks.ie/docs/default-source/publications/conditions-governing-connection-and-operation-of-micro-generation-policy.pdf?sfvrsn=ad5c33f0_8 If the inverter continued to work, you could be shut down by ESB Networks.
graememk wrote: » Yeah that's nearly brown out territory isn't it? The lowest I've seen mine go in the last month (from when I started recording it) is 228V ish, but that was when I was pulling nearly 10kW. The voltage around here runs a bit on the high side, currently sitting at 244V.
garo wrote: » There may be some polarity issues with the way your solar is wired in? Have you seen a drop in bills since your solar install? Low voltage coinciding with good sunshine hints at something being wired with the wrong polarity. You should check the voltage at the board after the inverter has shut down to see if it is still low or your inverter was causing it.
Sir Liamalot wrote: » Could be the neighbour's jacuzzi too! Voltage is set at the local transformer. It will sag as the community increases load and rise as load is reduced. Hence evenings are often the lowest and afterhours the higherest. If it's outside ±10% 230v then you can get the ESB to tweak the traffo. They'll often want to measure it first. Then claim it isn't. Then do nothing. My SMA inverter is way more tolerant of small upsets than my previous special snowflake MasterVolt..that yolk was woeful...
Sir Liamalot wrote: » If it's outside ±10% 230v then you can get the ESB to tweak the traffo. They'll often want to measure it first. Then claim it isn't. Then do nothing.
daughy wrote: » Unfortunately it's a housing estate...
Sir Liamalot wrote: » If it's you then it's them too. Out of range is outtov range. Now you could load it up with 15kW at peak times during the test period to influence a favourable result if you were so inclined.
KCross wrote: » The ±10% is not a hard limit. They are allowed breach that 5% of the time. Mine went close to 200V several times during their measurement but it didnt breach the guidelines set by the CRU to warrant a grid upgrade and that was that!
DrPhilG wrote: » If you go into the Eddi icon on the myenergi app and check the total power used, does it still give you a high figure? In the consumption history? The myenergi app does sometimes throw up odd numbers but 5 minutes later they're settled. Like in my screenshot you can see a few little wobbles around 10am, but the total consumed is still 0kWh. If your consumption history shows that you DID actually consume a large amount then I'd contact myenergi support. Their phone support is very good in fairness.
championc wrote: » Do you have two separate CT Clamps reading your Grid , with both of them on the same cable from the meter to your main board ? You SHOULD have two CT Clamps on that cable. However, your readings appear to say different.
gomamochi1 wrote: » No it's showing high energy use in the morning even though I have set the hybrid inverter not to discharge until after 2PM when we are home. The eddi is reading like there is solar gain excess that is not being used and being diverted to hot water tank approx 5 low per day .....dooh any suggestions
graememk wrote: » There is for sure something wrong with the ct or the communication. Is the ct the wrong way round? Something must be seeing "excess" so it tries to absorb it. Would the cut off be because your hot water tank got hot?
garo wrote: » With a DC coupled battery and hybrid inverter it is impossible for the Eddi to tell whether the power is coming from solar panels or the battery. Once it starts drawing power it will keep going and the hybrid will keep drawing the battery. Have you set an export margin on the Eddi?
gomamochi1 wrote: » No not sure how to do that
garo wrote: » I think if the Eddi is doing the draining you do it on the Eddi.https://myenergi.com/wp-content/uploads/2019/04/eddi_manual_v2.3_english.pdf Set it to 100W or something. It will make sure Eddi isn't draining anything until you have at least 100W excess. You can reach it via the Advanced Menu. Passcode 0000 The idea is that the Eddi will leave 100W exporting at all times there is an excess. if it starts draining the battery, there will be a 100W excess which will cause the hybrid inverter to export 100W less - as it senses an export so reduces battery output. The eddi will then consume 100W less and so on until there is a genuine excess and no battery drainage.
gomamochi1 wrote: » Is that in the advanced menununder supply grid=device limit? Is says its off at the minute.
gomamochi1 wrote: » yes 2 ct clamps on the main fuseboard after the meter one from the Zappi which is master and one for the Solis hybrid inverter. I note from that video that my battery is DC coupled (I think). Thanks in advance
gomamochi1 wrote: » One of the ct clamps was opened so will wait till the morning to see if its draining again and also adjuster the zappi as mentioned above. Watchful waiting.
garo wrote: » Yes that's the one. The default is Off or 0W. If fixing the CT clamp doesn't work set it to 100W.
graememk wrote: » There still is something not right. In October you would rarely get 2kw excess at 9am or do you? Correct me if I'm wrong but the eddi only needs to see the amount exported. When running on battery does the house run on a slight import (as not to export anything stored in the battery)
garo wrote: » That's not the only way as I explained above. Setting an export margin is probably more effective. But different strokes for different folks.