John.G wrote: » Depending on load there is always some voltage drop in the neutral due to its resistance, for example if I have a kettle and a toaster on then I get ~ 2V between neutral and earth but I would be quite alarmed if i got 10v.
Bruthal wrote: » What is voltage L to É and L tó N?
alan4cult wrote: » Check N to E at each socket on that kitchen circuit would be something else you could check. Also, if possible, turn off every other MCB on this RCD and test same, then turn of RCD and test same.
TJSparks wrote: » L-N 228v and L-E 218v. I was getting 10V between N & E at the wiring centre when heating was switched off and 18v when I called for heat. I'm thinking you might be right about the floating earth I'll go back and do a loop test on the circuit as I hadn't the testers with me on the job. Thanks for the input I'll give an update.
TJSparks wrote: » Thanks, I'll take readings from each outlet on the circuit. What's your thinking behind switching off MCBs and RCD?
alan4cult wrote: » . I think testing at a few sockets will definitely allow you to see if it's present across the circuit.
TJSparks wrote: » Was back at the job with my MFT and attempted an FL test on the kitchen circuit, with no joy. The kitchen had a refurb obviously by cowboys 6-7 years ago and the "sparks" must have left a JB badly connected in a wall or floor which is anyone's guess if its accessible. Might have to borrow an earth from another circuit. Also found another missing earth on another circuit where the home owner drilled through a cable hanging pictures and reset the MCB after the flash minus the earth.
meercat wrote: » You must Issue a notice Of potential hazard. Your primary concern is the safety and integrity of the installation and circuits. It’s not your concern what type of flooring is fitted. Run a new circuit back to the db protected by rcd(up through attic with trunking down bedroom wall). Don’t be doing temporary/unregulated work to suit the customer. Set your standards high and stick to them.