StephenS147 wrote: » Our house was last renovated fully in the mid 80s' which is when it was fully rewired last.
A different lighting circuit serves upstairs but has no CPC throughout. I'm planning on installing metal LED downlights in the room. The switch I bought is double insulated so doesn't require an earth but the light fixtures do.
Is it possible to take the CPC from the different circuit that's under the bedroom floor and use a wago maintenance free box and take a 4mm single CPC to the light fitting or does it need to be part of the same circuit to the consumer unit?
2011 wrote: » It is probably high time you got an electrician to check it over!
2011 wrote: » Many LED down lighters don't have an earth terminal on them. Are you sure yours does? You could use double insulted downlighters.
2011 wrote: » Assuming the CPC you have found is indeed connected this may "work" but it is against the regulations and best practice.