Marlow wrote: » That was a hard read. You really need to format your posts. The dedicated interface is the web configuration of the router. AVM have always pride themselves, that this is a system, that stays within your home. For security reason more than others. And yes, you have various ways to control the heat of the TRVs: schedules, using the TRV itself, the myFritz app, the Fritz!DECT 440 when it finally is launched and their own DECT phones through the Smart home menu. Also you are wrong on the Fritz!DECT 400. That one has no temperature sensor. It is not quite that simple. Because also in Germany boiler heating is not uncommon either. And when you have your traditional TRVs, they can't signal a heat call either. They don't have to. The heat call comes from your zone thermostat. So having the thermostats from one company and the remainder of the system from another is not really a problem. /M
deezell wrote: » There is no formal controller, although the Fritz 400 is a stand alone switch with a built in temperature sensor, looks for all the world like a wall stat, and it can be used to control Fritz TRVs and smart sockets. There is no dedicated interface in the Fritz system to call boilers, though this could be achieved using the fritz 210 smart socket, you would need a continental plug convertor to plug it in, and a continental plug lead to take the switched power to the boiler terminals.
deezell wrote: » Because in Germany, community heating is common, whereby circulation of the heating water is controlled on an estate basis, an apartment block say. All you need is to open and close the rads valves.
xl500 wrote: » For the Fritz Smart Valves do you have a central controller like to set schedules etc
Marlow wrote: » Not sure, if it has been mentioned, but I've moved my entire home to the AVM Fritz!DECT 301 TRVs. They can be screwed straight onto the standard Honeywell valves, but a lot of adapters are available. One type Danfoss adapter comes by default. They are DECT operated (no cloud, no subscription), but you need an AVM Fritz!Box router to control them centrally. Lots of flexibility in the system. And because DECT is 1.8 GHz, it won't interfere with WiFi. There are also DECT switched sockets with the same amount of programming possible and build-in temperature sensor, but they are all the continental Schuko type. Not available in 3-pin UK plug. Now, that sorted out my radiators. But my immersion and the 4 zones in the house still are on what I would call a make-shift DIY system. For that I've looked at Velbus .. some real interesting options there: https://www.velbus.eu/ Here's is a basic demo video: https://www.youtube.com/watch?v=VCdLmLPhHFU Their TRVs would have been no use to me anyhow, as they are wired, but I can certainly build a very usable system for control of the boiler, 4 zones and the immersion. And it's all fully accessible using OpenHAB. So is the whole smart home implementation of the AVM Fritz!Box routers. /M
championc wrote: » I've bought online what I (and seller) believe to be a v3 (since it includes the options that are subscription based on the v3+). The box is grey rather than the largely white with orange. So I'll know when I register it ?
deezell wrote: » V3 and V3+ bridge are the same, but on installation, V3 will use the old app, and offer an upgrade to v3+.http://support.tado.com/en/articles/3387241-what-s-the-difference-between-the-v3-app-that-comes-with-v3-products-and-the-v3-app-that-comes-with-v1-v2-v3-products
championc wrote: » Does anyone know as to what are the physical differences between the Tado v3 and v3+ internet bridge ? Is there an identifying model number or some minute physical characteristic, since they appear to look identical.
olestoepoke wrote: » Any Idea what the ballpark cost would be to have the plumbing done for the stove, given that its ready to go in the living room? Just the plumbing no work needed around the fireplace as ill be doing that myself. thanks guys
chuck eastwood wrote: » But that's thing thing with stoves. From time to time people have to leave them fully stoked and all you can do is close off the air supply. Either way it's pretty unlikely to be unlucky enough to have a power cut when your stove is at full whack and you have just left the house. Also I've seen ups used in computers I've never seen or heard of one large enough being used on a domestic system to back up a stove pump
deezell wrote: » That of course is what happens. There are obviously thermostat operated pumps and links to zones as well in the system. None of these will operate though during a power cut, so it behaves the householder to damp down the stove in this instance. Some of the larger stoves have outputs in double digits of Kilowatts, and if not damped would be beyond the heat sinking capacity of a cylinder coil or an open rad. There are a number of options, such as passive thermostat valves to vent the system water to a drain, or open to a gravity zone upstairs. Also, an inexpensive ups (uninterruptible power supply) could be wired to supply the stove pump, and at least one zone valve. Belt and braces solutions, you'd hope a large stove fully stoked would not be left running in a vacated home.
chuck eastwood wrote: » Speaking from experience, I have an open rad and gravity fed coil about 4 foot fro the stove. It's not enough to dissipate the heat with a decent fire going. It's really only a safety thing if you have power failures. This system needs to be set up so a zone is brought in when the stat hits a certain temp.
deezell wrote: » A good plumber will figure it. He's looking to see where those capped pipes are linked, and if your current system is sealed or vented. If vented, direct connection possible via a blender or 'neutraliser' tank or manifold. There needs to be a thermal heatsink for the stove, (open radiator or gravity coil on the cylinder). A heat exchanger is required if the current system is sealed.
olestoepoke wrote: » Thanks again. I had my whole house plumbed by a great guy who was very experienced. His preference was Systemlink and thats what he intended to use. The house was completely re-plumber, new Worcester boiler, new larger cylinder everything new pipes included. There are two pipes in my hot press that say stove return and stove flow. These two pipes run under the landing floor and stop about 5 ft into my living room and are capped. Unfortunately, a couple of years passed and the plumber emigrated to Canada. So I need someone to finish the job, would a good plumber with no experience in theses systems be able to do it? Thanks again for your time and help its very much appreciated
deezell wrote: » The systemlink does have the passive (non electrical) safety remote valve to physically dump overheated water from the stove system in the even of power failure while a large stove is lit. Have you checked if you haveca spare coil on your cylinder? Without this you will need a heat sink, such as open bathroom or landing radiator connected to the stove system to dissipate heat. Am I correct in saying your gas boiler is a closed system? You also say your system was left 'ready for a stove. Is there already a blender/manifold? A heat exchanger. 'Stove Ready' to me would be capped flow and return pipes, straight the boiler, and no more than a stove circulation pump required. Highly unlikely that much redundant kit was installed In terms of choice, I went with the NRG Zone 4 manifold, well made and tidy to install. My oil boiler was vented, didn't need a heat exchanger, but as you need a manifold and possibly an exchanger, you could haggle a price for both from NRG Awareness, or just get a heating company to give you an overall quote. Contact NRG, get the names of known installers of their kit in your area.
olestoepoke wrote: » Thanks again, One last question would you have a preference between the stystemlink and NRG given that they are both in and around the same price? Thanks
deezell wrote: » Sorry, can't help there, but have these facts to hand if you get someone out to take a look, or email them some of the schematics, see if they know what they're on about. I can understand tradesmen being wary of something like the Heatgenie, presented as it is as a magical 'Black box' solution, when internally it's just a few pumps, pipes, stat and a heat exchanger,(and also a passive thermal operated safety drain sensor and valve).It's all well within the theoretical knowledge of an apprentice. Same goes for the NRG link exchanger, a modest plate exchanger, 2 pumps, a pipe stat , wired to turn on both pumps when the stove water exceeds set point. Nothing there that a plumber couldn't understand. A good one could even put it together himself, but given their hourly rates, it might well be true that they'd need €800 to cover parts and labour.(this is actually part of he sales pitch for the device). Here's the full file on the device,https://www.nrgawareness.com/wp-content/uploads/2017/11/NRG-Link-Dual-Pressure-Interlinking-System-Installation-and-Manual-1.pdf If a plumber or CH installer can't figure out how to go about the job after reading this, I give up.
olestoepoke wrote: » Wow, great info thanks very much for the effort. If you can recommend anyone in and around Dublin thats experienced enough to install these I'd appreciate a PM. Thanks again, great info
deezell wrote: » It depends on how the boiler and cylinder installation was carried out, and what pipework was installed to facilitate later connection of a stove. Is the gas boiler heated water system sealed, or vented? (attic head tank). If vented, this will simplify blending of the two heat sources. Does the cylinder have a spare unused coil? This would provide a direct heat sink for an active stove. It's all about having a mechanism to dissipate stove heat in the event of power failure, to reduce the risk of boiling the heating circuit water. There are some great schematics on NRG Awareness website, which detail the different methods used to blend heat sources. They manufacture a manifold which combines the heated water from both boilers, for distribution to the radiators and HW cylinder. There are many permutations of these systems, but the concept is easily understood.https://www.nrgawareness.com/ They're based in Cork, The systemlink heatgenie is a heat exchanger, which is required when the heated water of the gas/oil boiler is not vented, but is closed and pressurised. As the stove must be vented, the heated water from the stove can not be allowed to directly mix with the gas boiler system water. This is similar to the idea that the boiler heated water that enters your HW cylinder is isolated from the actual hot water you get from the cylinder out of the tap. In order to then blend the heated water from the boiler to the heated water from the stove heat exchanger (or direct from the stove if the gas boiler is vented), a manifold or neutraliser box is needed. These are the models available from NRG Awareness. https://www.nrgawareness.com/product-category/nrg-zone-manifolds/ Systemlink have similar models, and some tube like models known as Spirozone.https://www.plumbingproducts.ie/system-link/3741-systemlink-spirozone-5.html The NRG Awareness version if the heat genie is this,https://www.nrgawareness.com/product-category/system-interlinking/ Similarly expensive to the heat genie, it consists of a heat exchanger, pipe stat, and a couple of circulation pumps, with some pre made pipework. Not a lot of for nearly €800 it has to be said, a good plumber would pull it together from a couple of hundred euros of parts. This the basic principle of the heat exchanger. Heres a link to a number of schematics for sealed boiler vented stove, as it probably more closely describes your system, assuming your gas boiler is sealed. If not, no heat exchanger required. This information should assist plumbers in assessing your system for upgrade.https://www.nrgawareness.com/product/nrg-link/
olestoepoke wrote: » Hya and thanks for the reply. A gas boiler and a hot water cylinder that were newly installed around 6 years ago knowing that a boiler stove would be installed one day. So all the pipework is there capped ready to go. Need an experienced installer.
deezell wrote: » Are you running this along with a gas or oil boiler? Have you a HW cylinder or is your HW direct from the oil/ gas boiler?
olestoepoke wrote: » Hey guys looking for advice on a back boiler stove installation. Ive been told that a system link heat genie needs to be installed with it. Ive contacted a few plumbers and none of them seemed confident about installing it. Or are there other options apart from the system link? Any reccomendations on companies or plumbers that a experienced in installing stoves with back boiler via system link? Thanks and PM me of course as per the rules.