John.G wrote: » My Hager 40A/30MA RCBO seems to have short circuit protection as well as o/load & earth tripping, can you explain this please and does a MCB have the same? (apart from earth leakage tripping).
John.G wrote: » I would try and narrow it down, see where you can disconnect any neutrals local to the boiler, ie, neutral from the circ pump, neutral from the boiler stat(s), neutral from the fan/burner or/and any others you can think of and then reconnect the main neutral, reset your rcd/breakers and then start reconnecting the above neutrals, checking after each. It might be no harm either to have a small electrical load from anywhere on while doing this which will give a fault current to earth and trip the RCD which otherwise it may not. See page 7 of attachment for some of a typical burner neutrals. Edit: got mixed up there, between a oil/gas boiler!!. so attachment of no help really.
Bruthal wrote: » Where did you disconnet it?
lintdrummer wrote: » You sir are a lifesaver! Disconnected the neutral feed and all now works. So what does this tell me about my problem?
John.G wrote: » Yes.
John.G wrote: » Have you tried replacing the RCD even if it seems unlikely? Can you break the neutral from the boiler, you may have a neutral to earth fault. Also, if you have a multi meter, with the RCD tripped, test the resistance on a number of plug sockets between neutral and earth. Edit: I see you have replaced the RCD.
Wearb wrote: » It is intermittent, so don't rule it out. Was there any test carried out on the circ. pump? btw not sure if you can use a megger on them.
lintdrummer wrote: » Thanks for the suggestion. Would this make sense even though bypassing the high limit stat solved the problem for so long?
Wearb wrote: » I've seen this on an oil boiler. It was caused by a faulty circulating pump. Worth looking into.