powerade wrote: » Hi John. I had tested this before and the results were as follows: 1. If the manual dial is set @ a temperature less than the digital thermostat, the manual dial will control the boiler, e.g. digital thermostat set at 32 degrees, manual dial set at 18 degrees, boiler will knock off at 18 degrees 2. If the manual dial is set higher than the digital thermostat, the digital thermostat will control the valve/boiler. I will test it again later jyst to be absolutely sure but I am reasonably confident that these controls are working as expected.
powerade wrote: » I turned off the heating, reset the ABV to 0 5 and turned the heating back on. The temperature soared to 72 degrees, and then went into a rapid anti cycle. It took quite some time to get back up to 65 degrees whereas it got there pretty quickly when the ABV was set at 0. The actuator light for Zone 1 is still off. The pipe from the bypass valve to the return pipe is equally as hot as the flow pipe. The pressure is ever so slightly higher than I have previously noticed it to be (around 1.6). The radiators are very hot in both zones, except the kitchen radiator. The boiler has not cycled, apart from when I changed the ABV setting but the temperature has still only increased by 1 degree in an hour in Zone 2 compared with 2 degrees in Zone 1. That is slow for Zone 1 but it go off to a very slow start when the ABV was set at 0.
powerade wrote: » The actuator light is off if I have the ABV fully open or closed. In relation to the dual thermostat functionality, I will check again when the heating has cooled down a bit. I am also going to test both zones for one hour again with the ABV fully closed to see if that speeds up Zone 2. I have attached a photo of the pipes & wiring of the thermistats.
John.G wrote: » The plot thickens, a ABV is normally a two port valve and would be connected BETWEEN the flow and return, the valve shown is a 3 port and is inserted in the flow pipe, it looks like some form of pressure mixing valve, IMO the flow line should be un restricted so I just don't know how this works, normally a valve inserted like this would be a mixing valve and would be thermostatic. As you look at your photo above showing flow and return horizontally (I know they are vertical but I cant post your picture showing that ) and pretending the "ABV" is a inverted T so the direction of flow is from left to right and the leg of the T attaches to the short pipe joining the return pipe.....can you say where that arrow is stamped, it on the left or the right (or on the leg) and which direction it is pointing in and we might be able to figure something out. Also its name, I know you gave it in a previous post.