Reisers wrote: » I think my point was well made If a contractor provides a plug for the connection of a standby generator he should switch the live poles. Its an invitation to connect anything that starts up to the grid otherwise.
live poles
Steve wrote: » There is only one live pole - in a 1~ domestic installation. The neutral or PE is not a "live pole"
Reisers wrote: » A lot of posters struggling with definitions here
Switching earths not allowed as per rules
Reisers wrote: » Draining a generator isn't an electrical term I mean there's a load on the generator
karolaug wrote: » If the generator had floating neutral then any fault current would go through the meter even if the house is powered by generator which shouldn't be the case.
karolaug wrote: » In shared neutral scenario if generator has also neutral bounded to earth there will be two bounding points, which is wrong.
If the generator had floating neutral then any fault current would go through the meter even if the house is powered by generator which shouldn't be the case.
In my case I use small Honda generator that has floating neutral so in order to ensure that installation still has functioning PE I have N and PE bridged in generator plug.
That way fault current goes through PE and to N in the generator.
2011 wrote: » But the generator PE is connected to the MET which is connected to the the ESB cut out which is connected to the ESB neutral. So even though you switch the ESB neutral off at your changeover switch you have essentially connected the generator neutral to the ESB neutral. What is the point in switching off the ESB neutral if you are going to short out the very same switch?
Bruthal wrote: » This disconnecting the ESB N thing came up before. I think I remember the ETCI council member or similar giving reasons to you why it should be disconnected. I remember being a bit sceptical of reasons given, although I cant find the thread. Imo a lot of things mentioned or put forward in electrical circles, are based more on convention and traditional teachings,rather than real life tests, or experiences.
2011 wrote: » But do you accept that in the example just given the neutrals would be electrically connected to each other regardless of the status of the switch?
2011 wrote: » Agreed, two neutralizing points would be wrong. I am saying there should be just one, at the ESB cut out. This remains in circuit if the neutral remains unswitched. Then you have just connected the neutral of the generator to the ESB neutral, so what is the point in switching the neutral? Also this deviates from standard practice.
karolaug wrote: » Switching neutral makes sure that there is only one neutralizing point even if the generator is neutralized internally.
Leaving the neutral connected and making sure that generator has floating neutral will use the path through meter to neutralize the generator. As technically it will work I don't believe it's the best practice.
If the ESB removes everything before the meter my setup will still work as ground rod is still in place and if you leave the neutral shared and rely on neutralization point provided by ESB you will lose that.
Depending on the house you can have neutralization point outside the house and it is technically part of the circuit while generator is used.
In that case you would have to disconnect the generator whenever there is any work done like meter replacement.
The whole point of changeover switch should be to provide safe electricity supply from generator without using part of the circuit that is not owned by customer.
If ESB wants to change the meter in my house they can do it after they remove PE to N connection which is not mandatory for my generator to work and be safe. In your house as you are using the meter as part of the circuit you have to wait in the dark until they finish.
Tuco88 wrote: » A silly question but Is the Neutral and Earth not at a common point in every generator?
For it to be a PE does it not have to join to the neutral at some point?
So connecting a genny to the house you would have connected 2 "neutralising" points regardless...
If the ESB neutralising link failed at some point or it was a TT system (new fuseboad never neutralised correctly 60/70s job) a fault in the generator could result in a live Neutral wire on the ESB side ?
Tuco88 wrote: » Points taken, for clarity... say you have a generator on a car trailer connected to the house. (No earth rod installed on the generator) and the neutral is not switched via the isolator.
Neutralizing is done at the ESB meter only as always. A broken neutral occurs at the plug/socket for the generator.
Is the neutral bar now live with the MET and so the ESB supply neutral wire coming in?
With the Neutral and Earth not ever being common on the genny side how can a short circuit happen??
If we had broken the ESB neutral via the C/O switch would we have not have protected people working on the lines from a shock anyway?
Reisers. wrote: » You're going to need an RCD for Automatic disconnection with a small generator feeding into a domestic installation
and it won't operate with the single pole changeover,its looking into a N-E short
Small Genset needs spiking and N-E connection>RCD> 2 pole changeover
The above and people applying voltages to N-E with dual voltage centre tapped generators would be the problems.
Only proper genset is a fixed standby generator and 1 N-E installation link in standby operation.
Reisers.. wrote: » 2011 , i'm providing an alternative viewpoint on changeover of portable generators i have provided all the relevant information to clarify to fully support and clarify the point i made on RCDs and ADS from the rules maybe study it before retorting