deezell wrote: » You're correct, the Drayton uses a variation of the 2 zone backplate pins to accommodate 3 zones, CH1, HW and CH2 on pins 1,2 and 3. As your controller was only 2 zone the backplate was ok, though the wiring was not. You were hoping CH1 and 2 were tied together at the plate. Still, not rocket science, and if you were confident to rearrange backplate wires, you could feed the two valve control wires directly in to 1 and 3, scrapping the wire that goes to the old stats and the returns from it.
loyatemu wrote: » any thoughts on why there are 2 live and 2 neutral tied together running into the backplate? There is a separate wiring junction box in the same cupboard as the valves so I'd imagine the Drayton can be wired up in there, but it would be easier to have it go where the existing controller is (I bought it anyway, couldn't resist the £50 off).
deezell wrote: » Have you a cylinder stat? Is it easy to run a wire from the valve cupboard to it?
AstraMonti wrote: » In Tado, is there a way to temporarily turn all the rad valves off together in all rooms instead of going one by one? I have 12 so it's a bit annoying.
AstraMonti wrote: » Yes I had a look at IFTTT but it expects a trigger. I don't want this to be automatic, yet, just a button to turn off all rads when I want. Grouping them all together unfortunately defeats the purpose of having each room separate temp (I think).
deezell wrote: » The trigger can be manual, as i said, it can be a widget or button on your phone home screen, or it can be a voice command via google. I have a few, for boosting zones for the duration of the timer set in tado, (20 mins). I've another which just cancels any manual action on any zone and returns it to tado automatic control. The boost is handy as the geolocation doesn't kick in until you're close to home, and if away for a few days, you might want to turn it on while on the way. Using "OK Google" you can do it hands free while driving, say 30-40 mins from home, just enough time to get the house right if it's been in Away mode for a number of days.
AstraMonti wrote: » Ok thanks, I am fairly newbie in IFTTT apart from a couple of small applets. How do you create the manual trigger?
AstraMonti wrote: » Additional question, can I use sonoff TH10 with the thermostat for the hot water cylinder and through IFTTT (or something else) to trigger the Tado to turn off the boiler when the temp is above x Celcius?
deezell wrote: » If you put a Sonoff on the cylinder, this can be wired to directly call the boiler on demand, you just need to wire a switched live from the Sonoff relay in parallel with the SL coming from the CH valve relay (assuming your tado is not instructing the boiler via OpenTherm digital interface). This is all that happens in a valve zoned system, each valve outputs a SL to the boiler, they are all combined. If you CH is not plumbed via a valve, and the boiler is called directly from a SL from the Tado stat, then any call to the boiler will result in the boiler and circulation pump sending water to the rads, not a problem if they are all fitted with (closed) TRVs. Is your HW heated as a consequence of CH, or can it heat on its own? does it currently have a cylinder stat?
AstraMonti wrote: » Thanks very much again. I don't have a valve to turn the HW separately, it heats up with the rads, and that's why I put the tado trvs on all rads so I can just heat the water. There is a cylinder stat at the moment but i think that's internal for the immersion as far as I know and I can't see anything to setup temperature. If I wire it directly to the boiler, wouldn't Tado turn it on again if it's "within" schedule?
deezell wrote: » It's likely that's an immersion stat, check do the cables from it go to the power terminal cover of the immersion. Without a valve, HW will always heat when any TRV calls the boiler. You also need to call the boiler without any TRVs coming on. You'll need to connect a switched live from a sonoff to the same SL coming from the Tado. Either will then call the boiler. If you adjust the boiler temperature close to the setting of the cylinder stat, then the cylinder is unlikly to exceed it's set temperature when a TRV call is in progress, as the circulated heated water will likemy be less than the boiler setting while it's passing through radiators. 65-68 is good for the boiler, with 55-60 For the cylinder stat, depending on how hot you like your hot taps. It's a compromise, you don't want to scald anyone using a hand basin, but you might like fairly hot water for dishes etc. The settings above will ensure that there is at least 10 degrees difference between boiler and cylinder so heat transfer takes place.
deezell wrote: » So basically you have a 2 zone CH system with standard controls, HW control is not required. Nothing unusual about this, systems with combi boilers and on demand HW require no intervention from the CH stats and timer controller, smart or otherwise. At most, some systems may have HW priority built in, which will delay CH until HW demand is met. From the viewpoint of the stats, it calls for heat, then monitors room temperature, calling off the boiler when set temperature is reached or in the case of smart stats, approached. Drayton may mistakenly assume you want it's kit to control HW, which you wouldn't, or perhaps it might not match well with the response profile of Heat pump souced hot flow, though this sounds unlikely. The Drayton controller just substitutes for conventional controllers using a standard baseplate with wiring variations for 1 zone CH, two zone CH + HW, and three zone, 2 CH + HW. I think the confusion arises because standard 2 zone controllers come in two flavours, CH + HW and two CH. You would have the latter, though there is little difference between them technically except perhaps the CH + HW type might have a gravity mode switch, but in normal mode it can be used for two CH. Drayton rightly will advise that their CH plus HW controller can't be used for 2 CH zones, as it only supports one wireless stat. There's nothing to stop you using their kit 3 though, 2 CH plus HW, you simply ignore the HW facility, by leaving it timed permanently off on the app, and by not connecting anything to its HW SL terminal 2 on the the backplate. I can see no reason why this won't work
AstraMonti wrote: » Thank you again. On a more practical example, let's say 6 with 7 I have the boiler to kick off. I have all the trvs off and let's say sonoff reads 50 at 6:30 and turns the boiler off. Wouldn't tado turn it back on since it still has 30 minutes left on its schedule?
Fwarder wrote: » Hi all, I have one small question regarding Nests and Google home. Can you control the HW through Google home? I know that you can say "Set the temp downstairs to 20C" etc. but I get "I'm sorry, I don't understand" when I ask for HW Maybe I should ask for "boost on" or something
deezell wrote: » Typical schedule living zone 24.00 to 07.30, 16° 07.30 to 09.00, 21° (breakfast) 09.00 to 16.00. 18° ( less if empty house( 16.00 to 21.00 21° (kids home, dinner, tv. etc) 21.00 to 23.00 20°
deezell wrote: » This kind of evolved over time.
deezell wrote: » I don't worry too much about it, it seems to ensure comfort around the clock, house is not empty midweek but the drop after morning is there as you don't need "sitting down" temperatures if you're active in or outside, so 19-20 does fine. If everyone is gone, the away schedule takes over. You could probably set just 2 temperatures for 24 hours, sleep and awake, and let away drop it when you're at work. I've a TRV for the kitchen, which is a cooler corner room, it drops down about 6.30 pm to 18°, then lower after supper, stays like that till before rising. Master bed TRV is suspended at the mo due to the noise at night, I'll put it elsewhere when I change rad valves to TRV type. I dont change schedule in summer, in warm weather, like today, stats don't fall below target except maybe in the waking hour, so very little boiler activity. Tip, most mobiles take a screenshot by pressing the On and Home buttons together.
legend99 wrote: » Important question so - and a bit late lol! - but do you think it's saving you money?
Penny Huge Clock wrote: » Is ember good? Can it be used with alexa? Any better options?
deezell wrote: » In a word, No. Just a remote version of standard EPG controller. Read up on Drayton. Tado, Nest, Hive, Netatmo.
Penny Huge Clock wrote: » Any summary available of the extra features in those ones?