maxamillius wrote: » @Deezel, Picture of my oil boiler attached, not sure if you have a wiring diagram for it?!
ghostdancer wrote: » Would Nest work with an immersion that is run on a timeswitch, ie. to turn the heater for the hot water on/off? I have the heating (radiators, 1 zone) controlled from a segment-timer in the hallway, simple on/off one. I believe that Nest can replace this no problem? I also have the hot water immersion controlled from a timeswitch in a press upstairs. I say "controlled", but it's really just turning the hot water boiler on/off at specific times. This is the timeswitch: https://www.amazon.co.uk/gp/product/...?ie=UTF8&psc=1 Can one Nest be set to use both of these? I just want to be able to turn both on/off with the one device really. No need for adjusting temperatures (which I don't currently do anyway).
maxamillius wrote: » If I switch the boiler off, the pump will stop also, so the permanent live at the stat is actually a switched live from the boiler and then a switched live to the pump, does that sound correct?
deezell wrote: » Pretty much. In my description I assumed that the circulation pump will only operate if the stat is on and if the boiler is firing, but it is possible that the live to the stat is not taken from the boiler timed live. This would be a poor setup, if the pump continued to run when the boiler timed period is off, so just confirm that pump only runs when the boiler is fired and the stat is on. All the stats listed have a wireless relay, but it's optional with Tado as it has a switch in the stat for straight replacement of an existing wall stat which has been wired to control both boiler and pump. This would not be sufficient given your current wiring. The hive stat is currently good value in heat merchants, at €166 for 2 zone receiver. See earlier posts. This will connect to the boiler to fire it, and it has a spare HW relay switch for future use.
maxamillius wrote: » Thanks Deezel, agree that my system is very basic and I could do with more control. At the moment I don’t have the money to get done valves etc installed so just trying to start off small and work way up to more control. So can I do all of what you have just said using nest,tado etc to start off with my basic system?, then if I decide to add zone valves I can just expand the nest/tado or whatever I install.
deezell wrote: » You are using the boiler clock to fire the boiler in timed intervals, which in itself does nothing as both HW and CH require the circulation pump. Your current stat turns on and off the circulation pump. You can combine the timing and stat functions using the netatmo. You need to identify the electrical terminal in the boiler which fires it on or off. This sometimes labelled SL (switched live) or LR ( live return). This is likely connected to the live output of the built in timer, enabling the timer to turn on and off the boiler. Connecting a live cable to this terminal will fire the boiler. The netatmo is a wireless stat with a relay switch in the receiver. You must install this and connect the relay boiler adaptor cable brown and blue wires to the mains and connect the black and grey wires across the boiler Live and LR (or SL). The netatmo relay now controls the boiler firing. You now need to remove the old stat and either join together it's wires, or just turn it up full. The circulation pump will come on every time the boiler is fired, and this will be controlled by the time and temperature schedule of the Netatmo stat wirelessly linked to the receiver. Your system is far from perfect in that it does not allow HW independent of CH. If you want this you will need to make some plumbing alterations, such as the addition of zoned valves. The netatmo stat has no provision for controlling future independent HW only zones, so you might want to consider a Nest, Tado, Hive or Drayton Wiser stat which can have a HW relay as well as a CH relay to control zone valves. If you post the brand and model number of your oil boiler I shoul be able to find the terminal diagrams to which the netatmo relay is connected.
maxamillius wrote: » So I’m planning on installing one of these to replace the integral analogue time clock on my oil boiler, https://www.ie.screwfix.com/drayton-mitime-mt711r1a09sx-single-channel-timeswitch-with-li-ion-back-up.html. This in theory gives me a little more control over timings, currently difficult as the intervals on the analogue clock are not great. My current wall stat controls the circulating pump, looks to be a permanent and a switched live behind it. So when boiler comes on it does not do nothing until I turn the stat which starts the pump and thus the CH and HW. I tried switching boiler on and leaving stat turned down to see if HW would heat without pump being on, it didn’t. My question is, if I get netatmo, what do I need to do to install it? Do I need to alter wiring to boiler, alter wiring to pump, both? Cheers
loyatemu wrote: » in my case the boiler does stop running if all the stats are above their set temperature.
deezell wrote: » It should be done that way, otherwise the boiler cycles with no load and depends on its built in stat. Not efficient
2011 wrote: » If installed in the hot press how is the boiler switched on? Or are you assuming that the zone valves have been correctly connected to turn on the boiler? That has been my experience while working as an electrician. Unfortunately many zone valves installed do not have the auxiliary dry contacts wired back to the boiler. This means that a zone valve open status can not be used to switch on the boiler in the way you described in your earlier post (which is my preferred method too).
deezell wrote: » You'll most likely find that there are two switched lives (SLs) going from the single controller CH timed out to the individual stats. If there are, these will go to their separate CH outs on the Drayton. If not, the drayton can just be installed in the same location as all the zone valves, and the three SLs for each valve can be connected directly. Then you can just completely scrap the old stats and their wiring. This would be a better job too, as the zone valve wiring would not be ruuning off and back to a redundant stat location.
loyatemu wrote: » OK - our existing controller is a Siemens RWB29, which is a 2 channel controller (CH and HW) so I don't think the Drayton controller will be able to control the separate heating zones without some rewiring .
deezell wrote: » Here's the Hive Stat with or without HW control, Counter price in Heatmerchants only €166 (133 plus vat). You don't have to dress up as a plumber to buy. Extra zone 90 plus vat, €109, total €275, about the amazon price. Buy local in Ennis Heatmerchants. Enquire there about grant installers, pay him to install and sign the forms, get the full 700.http://www.heatmerchants.ie/v4/581ae...gDealDec18.pdf
loyatemu wrote: » Presumably I'll have to check that my existing controller is wired for the 2 heating zones separately. I thought the stats managed the zones and the controller just turned the whole system on and off, but I'm not an expert (as you've probably guessed). Currently our upstairs stat is on the landing, which is basically useless for controlling the temp in the bedrooms. With this at least I could put the wireless stat in our room then at a later date add TRVs to the other rooms.
deezell wrote: » Drayton wiser Kit 3, comes with controller and two wireless stats, about £208 on Amazon. App almost as good as Tado, install is a cinch. If you have an existing 3 zone controller, just swap over the wires to the Drayton one, mains, CH wires and HW wire, pair the stats, then connect the controller to d'internet, EDIT. Your existing stats will be wired with the timed signal from the existing controller going to each stat then on to their respective valves. the Drayton does all this in the controller, and your old stats will either be left on full or removed and the wires joined.
savemejebus wrote: » €795 is taking the michael alright. I have 3 zones, upstairs, downstairs and hot water so I'm figuring one 'hive heating and hot water' and one additional thermostat (to get separately would be £233 from amazon) would be what i need and also satisfy the grant requirements. Not confident to install it myself so checking to see if the grant (if possible) would be a more cost effective method to get it.
loyatemu wrote: » we have 2 zones + HW (gas boiler) I was looking at the Drayton system but I'm not clear as to how it controls the zones. We have a thermostat per zone (upstairs and downstairs); the timer/controller has separate programs for heating and hot water but AFAIK it has no individual control over the heating zones, the thermostats control those via powered valves. This has been the system in most places I've lived so I don't think this is unusual but if the Drayton only replaces the controller how can it individually control the zones?
savemejebus wrote: » Sorry, i guess I'm not following. The grant is 700. Based on the hive site's prices, installation for a multizone system would be probably 519.
2011 wrote: » I mean how much is the grant worth for the heating controls.
savemejebus wrote: » €700, so would cover just about everything.