deezell wrote: » Can HW only be heated in conjunction with CH? Is it possible to have HW only, during the summer? If this is the case it sounds like a gravity HW system, with CH pumped. In this system HW is always heating once the boiler is fired, but CH only comes on when the CH timer operates a valve/pump. For this you will need the twin zone receiver set in gravity mode. If the entire system is HW and CH always together, then you could just get a single zone receiver. Its possible such a system is installed, with an internally pumped gas or oil boiler CH will always be on as well as HW, but its unlikely that a plumber would leave it like this. Still, some posters here and elsewhere have had just that, the HW being supplied during the summer by electric immersion, as boiler pump/circulation pump always ran when the boiler fired. Come to think of it, it's how our house was setup when we moved in, first thing I had to do was put in a gravity feed to the cylinder to let it heat sans circulation pump Now would be a good time to get a handle on which way your Ma's is wired and plumbed.
reignschaos wrote: » Looking for some wiring assistance. I've eventually gotten hold of my two Tado Thermostats and looking now to install and replace my existing ones. I popped off the front of my existing ones and was presented with 2 brown wires. My existing thermostats are called flash, see pictures below. Outside image available here Inside image available here Wiring image available here From what I can see the top brown wire is neutral and the bottom one is Live, however 1. I don't know why the top wire if it's neutral is brown. 2. I don't know what the whistle symbol after the N represents. My understanding of the tado termostats wiring is NO - Normal On NC - Normal Closed COM - Common Spare - For parking unused wires. and based on normal 3 coloured wiring my understanding would be NO - Normal On - Yellow (Calls Heat) NC - Normal Closed COM - Common - Brown (Permanent Live) Spare - Blue (Neutral) Based on the wiring of my existing Thermostat my thinking would be Top Brown = NO - Normal On Bottom Brown = COM - Permanent Live But I'm not sure. Any help would be greatly appreciated. N Thanks
squa wrote: » Sorry to hijack this thread, but seems like this is the best place to get some answers as my heating is system is pretty much as explained by deezell above. I have OFCH with x3 pumps attached - x2 for upstairs/downstairs CH and x1 for the HW. There's x2 old anologue thermos in the hall and landing, which I assume cut the x2 CH pumps in/out as required. I'm able to fire the HW on it's own without CH in order to heat the water in the cylinder upstairs as I've no immersion or electric showers in the house. For the most part it works well, but what I would like to do is replace the boiler control downstairs with something that has IP/WiFi capabilities so I can remotely control the system via an app. I've been doing some research online and a lot of these SMART solutions either have the thermo built into the controller for the boiler and/or want to completely take over to make heating more efficient. Having the thermo built into the controller won't really work for me as the controller is in our back kitchen with an indoor boiler located in the press underneath. So this location will warm up much quicker than the rest of the house. So really what I want to do is just replace the boiler controller, but I'm unsure how many zones the new controller would need to support, 2 or 3? Given that there's actually 3 pumps, it would be great to be able to turn on the upstairs or downstairs CH independently if required. Right now I can only turn on both via a switch on the boiler controller and allow the existing thermos to cut the pumps in and out as required. Then I assume another zone is needed just for the HW. I'm also happy to update the existing thermos if required, they are wired back to the boiler controller somehow and my basic understanding of CH systems has yet to figure that part out! Any suggestions re. a controller that might meet my needs? Many thanks, Squa
deezell wrote: » Picture of boiler controller if you can, make and model also. Is there a stat on the cylinder, or is it just timed from the controller. At the outset, you can just replace the two stats with two smart ones, they will take care of timing and temperature control of the house zones. If the controller you mention is a 3 zone timer device, yoi would normally set this to always on, however, I suspect your current stats only turn on and off the pumps, while the controller fires the boiler, so this arrangement msy be less than perfect. Send me a pic of controller, I'll tell you more then. If you can pop it open and get a pic of woring baseplate, all the better
OffalyMedic wrote: » We've a single zone heating system. Hot water works of CH. Slowly getting the house fully automated. Next thing on my to do list is a smart thermostat. Which would ye recommend Hive or Nest and why?
squa wrote: » Here's the various pictures you requested deezell.....thanks for your time looking at this. There doesn't appear to be any thermo on the HW cylinder as I can't see any electrical wires coming off the thank. Only copper pipes.
squa wrote: » Wow, a serious reply there deezell. Thanks for going into so much detail about what's required to achieve the correct firing if I want 3 independent zones using a new relay box. Not sure I'd have the confidence to wire that in myself, but my brother in law is a sparks so might call in a favour if I decide to go down that route. Attached is a picture of my pump arrangement. Maybe that helps to answer if HW is possible as an independent zone form CH or always has to be on as a function of the boiler. Using the existing stats I figured out that both pumps to the right are CH. One was obviously replaced at some stage prior to me buying the house as its much newer. If I was to back things up a little on this project. Do you know of any product that's available whereby I could just upgrade the existing control unit, keeping the current CH/HW arrangement, but the new product allows me do connect to it using an app so I can remotely turn on CH/HW as required? Or am I limited to using a Smart Stat with the need to upgrade to an NGR relay etc?
Bazza32 wrote: » I have been reading a number of the previous posts, and Tado seems to cause some confusion about what the do and don't support. Even down to the web site contradicting the telephone support. I was about to invest in a Tado last week, until I called their support, and was told that their system would not work for me. I currently have the following: Gas fired CH/HW, controlled by a three channel Horstmann Channelplus H37XL, the boiler is a Glo Worm Flexicom 30sx. Channel 1: Heats downstairs (8 rads) Channel 2: Heats upstairs (4 rads) Channel 3: Hot Water - but is permanently off, as we have Thermodynamic Solar Panels - https://www.lvprenewables.ie/thermodynamic-solar-panels/. This would only be used if we ever need to top up, and have not needed to do so, 1 year in. I have no thermostat currently upstairs or downstairs. To get started, I was going to get the Tado Smart Thermostat + Extension Kit, as the website seems to say it would be suitable. I was then going to add their smart radiator thermostats, and possibly another stat over time. All of the rads currently have Manual TRV's on them. Having spoken to their support, they say my system is not compatible with Tado, and I would have to start hard wiring the thermostats in, as I could not go with the wireless option. Also not sure the extension kit supports 3 channels either. So looking for options. The Tado support guy, seemed to suggest that this was a common setup for Irish homes, so I am assuming people on here have got some workarounds.
budhabob wrote: » Nest query: Just had nest installed last week by electric Ireland, getting our heads around it and like it, however, I'm not sure how it'll work in the spring / summer months. So we have a single zone / hot water. Can set the schedule based on temp, but how do we set it in the summer months when rads will be off and only want hot water for shower? Have looked at the site and says 3rd gen is capable of this, but it's not clear on the app how it's done. (Apologies if this is a stupid question)
deezell wrote: » Did you previously have a two channel timer/controller to independently set HW and CH, or just a single zone timer with maybe a HW -OFF- HW+CH switch. If the former the installer would have connected the separate terminal for a HW motorised valve and would have enabled HW on the stat, which would appear as a Tap icon on the App. If the latter, then its probably wired as single zone with HW and CH together. If you didn't have plumbed independent zones before, the Nest wont add them, but if you had a gravity HW system with separate switch to turn on the CH circulation pump, then I do have a solution to that. Have you still got any of the old controller or stat to send a picture.
budhabob wrote: » The latter, it was wired as a single zone with HW and CH together (Terrace house, upstairs heating rarely on so made sense at the time). So based on that, and what I read from above, it looks like there might not be a solution? We have a manual valve to use for turning the radiators off during the summer months, so just ran the boiler for shorter intervals. If i could just set the nest for time intervals it would be ideal.
deezell wrote: » Any Tado stat can be used just as that, a stat, plus it has programmable timing as well. So for any CH zone, you simply wire the stat in series with the Switched Live for that zone coming from the old programmer. You set that zone to always on, and let the Tado stat take over timing of the zone, plus thermostatic control. Repeat for the second zone. As you don't have existing pre wired stats upstairs or down, you will have to run cables back to the old controller. The HW timing on the old controller can be left aa is. Theres no point in buying an extension kit if you're not controlling HW timing, other than to use it as a wireless receiver for one of the stats. This would simplify wiring. You should also consider Nest and Netatmo smart stats. The nest is wireless by design, it comes with an extension box known as Heatlink. The Netatmo also can use it's supplied bridge relay to connect to the old controller zone outputs, locating the stat wirelessly in the zones. If you want to use Tado, you will need two stats, and if you want to avoid the wiring involved, you would need 2 wireless ext kits to provide wireless connection. However, a single Tado account can only have one extension kit, so one stat will be wired. Otherwise you would end up installing two individual tado accounts, which I'm unsure can be run from the one app. Wireless multi zone can be handled by Nest, Netatmo and also hive. With nest you just buy a complete Nest per zone, Nests gen 3 about €240 each. With hive its €200 for the first stat/ receiver/ hub, but it's just an additional stat/ receiver per additional zone, €120 each. Hive are throwing in a free Echo dot with the main stat kit.
Officer Giggles wrote: » The pictures would help I suppose
limnam wrote: » my GRASSLIN Towerchron won't fire HW unless i have the jumper on the back of the programmer set to gravity mode. Is yours set for gravity? Deezell would be the man to assist on this i'd say