Tuco88 wrote: » Its possible to experience a current greater than 30mA also with operation characteristic of the rcd so time being the factor.
2011 wrote: » I had a few little “tingles” myself back in the day, never tripped an RCD that way though.
Tuco88 wrote: » He could remove the load side of the rcd in the consumer unit and test, so taking all downstream faults out of the equation.
Risteard81 wrote: » No. Because with TN-C-S although combined at the origin they are separate throughout the installation. If you have interconnections beyond that point then you essentially have a PEN conductor at that point. It won't always have this effect though and very much depends on the loads etc. and how they are dividing, and ultimately what the RCD is seeing through its coil.
Bruthal wrote: » Risteard81 wrote: » When it is upstream it can desensitise the RCD so that it never trips as too much of the current is dividing to cause a sufficient imbalance. I've seen this with a neutral/earth fault on the tails for example. Anyone with a neutralised house has a desensitised RCD so?
Risteard81 wrote: » When it is upstream it can desensitise the RCD so that it never trips as too much of the current is dividing to cause a sufficient imbalance. I've seen this with a neutral/earth fault on the tails for example.
Bruthal wrote: » Risteard81 wrote: » Have you checked for an upstream neutral/earth fault desensitising the RCD? Doesn't have to be upstream of the test point for that to happen, just downstream of the RCD. It would be expected to trip if any load plugged in. More so in neutralised installations.
Risteard81 wrote: » Have you checked for an upstream neutral/earth fault desensitising the RCD?
Jay.D87 wrote: » Disconnected main neutral and did continuity test across all earth to neutral doesn’t seem to be any fault
Tuco88 wrote: » Test the rcd at the DB, with all the downstream breakers open to focus on that alone. Is there a shower RCBO if so hows that working? And polarity good? If the RCD is working with its test button thats a start. Cant be an S type if you got a brand new one so rule that out.
Bruthal wrote: » If you are testing via sockets, make sure they are wired properly, in case someone connected sockets with neutral linked to earth terminal in lieu of a proper earth or something mad like that.
Bruthal wrote: » Did you do a loop impedance test?
Jay.D87 wrote: » Cheers Bruthal so maybe hammering the earth rod in is best course of action?
Bruthal wrote: » Most assume a voltage reading of 230v L to E means there is a good earth path... But, a digital multimeter showing 230v L to E does not show/prove there is a good earth, or any real earth path. If you test from L to earth through a 1k resistor, the meter will still show 99.99% of the supply voltage because of the very high meter input impedance in voltage test setting, even though 1k ohm is practically an open circuit in terms of an earth fault path.
Tuco88 wrote: » Just a few questions. 1) Will the RCD operate on its own test button? 2) Is it a 30mA Rcd, Not 300mA? 3) Is it an AC or A type RCD and are you testing on the correct one? Does sound very odd.
Jay.D87 wrote: » I have an earth somewhere, as have 230V L-E at board. Although when I looked at ESB meter I can’t see the Neutralising done. I don’t even see any Earth on ESB side and I’m 90% sure there’s no earth rod either.