Shefwedfan wrote: » Ok, I have a setup at the moment with two electric shower. Shower A and shower B. They are on a priority switch. So if Shower B was on and shower A was turned on then shower B would turn off till shower A finished All good. Got a car charger about 3 years ago. This was installed as well. No problem. It would turn off as well once Shower A or Shower B was turned on Last few months I have a problem. I can't seem to rectify. If I have car plugged in, doesn't even need to be charging. Shower B is not been used. If shower A is used then power is cut to shower B. Check the switch board and nothing tripped, I need to pull the switch down and put back up and then bang shower goes again. This is just happening randomly and I have tried all combinations myself and nothing then 20 mins later I go in and its gone. Asked electrician and he said could be charger cable so I swapped it and same problem. He mentioned it could be high moisture in the bathroom with the shower???? Any idea? and why would it not fully trip down the switch but cut the power off??? Thanks
meercat wrote: » That’s the rcd. My advice is to get a rec to investigate
Shefwedfan wrote: » Had electrician in..... He said they never break .....said it was condensation I am just wondering what it might be?
Shefwedfan wrote: » Had electrician in..... He said they never break
meercat wrote: » I’ve replaced numerous rcd’s If it’s condensation,where is it getting in and causing a trip. You need a competent rec to come in and test
Shefwedfan wrote: » He said condensation at the shower not at the trip switch Sounds dodgy to me
meercat wrote: » Did he do an insulation resistance test to confirm this or just a visual inspection. A notice of potential hazard should have been issued Get a competent rec in as this is a safety device and should be functioning correctly
Shefwedfan wrote: He said they never break .....said it was condensation
Shefwedfan wrote: Based on that I took it that it was failing. The electrician was onsite for another installation so I threw him a few quid to look at it, said nothing was wrong. Had to be condensation in the shower or something which was bridging the electricity and that was causing it to short out....I thought the answer was suspect but he didnt end up charging anything so left it.....windows wide open, no condensation in bathroom and still same random issue
Sleeper12 wrote: » As a shower repair company we have to replace dozens of RCBOs per year. Most seem very healthy but some can become over sensitive. You can put an electric shower in a steam room in a gym & it shouldn't suffer from the condensation. I have seen a shower needing the RCBO replaced three or even four times before everything settles down. I have seen a brand new RCBO trip on a shower & have to be replaced. The same RCBO could then work perfectly with another shower of the exact same make & model.
Xwebstar2 wrote: » Sounds more like black magic than electrical work I haven't seen massive numbers of faulty Rcbos over the years
Xwebstar2 wrote: » Sounds more like black magic than electrical workI haven't seen massive numbers of faulty Rcbos over the years
Xwebstar2 wrote: And there's thousands of homes out there with Rcbos and they'd be calling registered contractors to replace them, which they're not ime
Xwebstar2 wrote: It seems to me that you advocate Rcbo trial+error replacement as a quick fix to solve issues external to the shower
Xwebstar2 wrote: Pull-cord replacement is a major issue , no dispute there
Xwebstar2 wrote: » I've been called out to faulty showers and RCD/Rcbo trips for 20 years Faulty Rcbos has never been a major issue Sure, if you swop it out 3-4 times the problem may go away
Xwebstar2 wrote: » I'd also dispute that homeowners are calling shower repair companies for Rcbo trips and rarely electricians
meercat wrote: » It’s time to get a competent rec in and do some proper testing. Ask for the test results and a certificate I’d expect it to be a faulty rcbo as I’d agree with sleeper12 and I’ve replaced many over time. Let us know how you get on.
Sleeper12 wrote: » Well working on 1000 plus shower every year for 30 years I would expect to see faulty RCBS much more often then you do. The beauty with the RCBO is that isnt designed to be over sensitive rather than under sensitive Dispute all you want. Fact is shower breaks people call a shower repair company. How do you suppose we make a living doing nothing else but electric & power showers? How do we work on 1000 shower pr year & you get a handfull of shower calls? You understand this is my specialty right? I work at this & only this all day everyday? I'll leave you with whatever beliefs you want. I'm not going to keep replying to what is really tunnel vision. Best advice for OP is to get a good REC in to investigate. I assume OP has learned a lesson with the sparks he called & wont be using him again. Fingers crossed OP will report back with the answer to the mystery
Sleeper12 wrote: » I've an electrician that earns more than the average industrial wage just from the RCBO & pull cord switch work I hand him each week alone.
Xwebstar2 wrote: Are you actually testing when issues arise?
meercat wrote: Sleeper 12 uses a rec to do his electrical work for him .
Sleeper12 wrote: » What piece of equipment did he use to determine this? Pay a good REC to replace the RCBO that is tripping. This should resolve the issue.