Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Live self-Builds - mod warning in post no. 1

1333436383953

Comments

  • Moderators, Home & Garden Moderators Posts: 10,141 Mod ✭✭✭✭BryanF


    Me. Im at 1rst fix.

    Good for you Roisin. Any photos? Care to share your experiences?


  • Registered Users, Registered Users 2 Posts: 5,422 ✭✭✭just do it


    Photobucket picture removed as it gave my email address!


  • Registered Users, Registered Users 2 Posts: 1,088 ✭✭✭AntrimGlens


    JDI,
    No wonder you've been missing. ;). Great stuff. good luck with it.


  • Registered Users, Registered Users 2 Posts: 1,504 ✭✭✭BarneyMc


    It's been a very long time since I posted here but hopefully the photo sums it up - external work finished now and starting firts fixes soon. It's good to be on so far and yet so much still to do! :)


  • Registered Users, Registered Users 2 Posts: 1,740 ✭✭✭hexosan


    Love the garage Barney


  • Registered Users, Registered Users 2 Posts: 5,422 ✭✭✭just do it


    vFNvujT.jpg Raft foundation with retaining wall in place

    GFfvyzp.jpg

    RnxgO5p.jpg
    Just as well the pop-up was taped :D


  • Registered Users, Registered Users 2 Posts: 5,422 ✭✭✭just do it


    TjuSuZR.jpg

    Pipes for meter box. Note it will be outside the wide cavity.


  • Registered Users Posts: 458 ✭✭kboc


    just do it wrote: »

    Pipes for meter box. Note it will be outside the wide cavity.

    Just Do It,
    Is the raft insulated and are you doin that later?

    What is the make of your walls?

    Thanks
    K


  • Registered Users, Registered Users 2 Posts: 5,422 ✭✭✭just do it


    kboc wrote: »
    Just Do It,
    Is the raft insulated and are you doin that later?

    What is the make of your walls?

    Thanks
    K

    The raft is structural and not insulated. The walls are reinforced concrete retaining walls. There will be over a metre of backfill around the high corner.

    The inner leaf will have one coarse of quinlite and it's a 250mm cavity which will be pumped.


  • Registered Users Posts: 23 calum22


    Looking good Just Do It!!


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 649 ✭✭✭Cork selfbuild


    Haven't posted in a while, we are now pretty much finished the block work, bar a small few bits here and there... Roof should be started in a week or so, windows are ordered, so far so good! :D

    9b64387edb8ebfa5dc8fb56e1c19e6b7.jpg

    0e083a39e33f78e6a7af5eb524337113.jpg


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    Why the returned block at the reveals - how will you limit the cold bridged at this point


  • Registered Users, Registered Users 2 Posts: 5,422 ✭✭✭just do it


    It's funny what you get stuck on. We paused the building of the workshed for a fortnight as it has a prominent position on the site and it is the first thing you see when you drive in. So we've gone through a few different sketches involving the roof and ultimately the QS priced the architects preferred option and we're back to the original, cheaper design :D. Still it was worth doing it. I don't want to look back on any element of this and think if only I'd researched that a bit more.

    I'm glad with the team of people I've selected as I feel we are all working well together and that is a huge consideration.


  • Registered Users, Registered Users 2 Posts: 5,422 ✭✭✭just do it


    Lower floor block work done and now waiting on precast floor and stairs.

    5FQcdG.jpg


  • Registered Users, Registered Users 2 Posts: 12,861 ✭✭✭✭mfceiling


    just do it wrote: »
    Lower floor block work done and now waiting on precast floor and stairs.

    5FQcdG.jpg

    That's a lovely view to wake up to every morning!!


  • Registered Users, Registered Users 2 Posts: 5,422 ✭✭✭just do it


    mfceiling wrote: »
    That's a lovely view to wake up to every morning!!

    Yes looking forward to it although as it is an upside down house we'll have to get up to admire it :)


  • Moderators, Home & Garden Moderators Posts: 10,141 Mod ✭✭✭✭BryanF


    Haven't posted in a while, we are now pretty much finished the block work, bar a small few bits here and there... Roof should be started in a week or so, windows are ordered, so far so good! :D

    9b64387edb8ebfa5dc8fb56e1c19e6b7.jpg

    0e083a39e33f78e6a7af5eb524337113.jpg
    where you have steels, what thermal breaks have you provided?


  • Registered Users Posts: 141 ✭✭thumper10


    hey everyone, so we've our plans in with Galway coco, and i've just started researching the insulation for the foundations/walls, and i'm already feeling over whelmed...
    We're building a split level house and from years of rental cold-very poor insulated accom, we're hoping like everyone i suppose, to build a near-passive house.
    any recommendations at this stage would be fantastic......where to start! :)


  • Registered Users, Registered Users 2 Posts: 5,422 ✭✭✭just do it


    thumper10 wrote: »
    hey everyone, so we've our plans in with Galway coco, and i've just started researching the insulation for the foundations/walls, and i'm already feeling over whelmed...
    We're building a split level house and from years of rental cold-very poor insulated accom, we're hoping like everyone i suppose, to build a near-passive house.
    any recommendations at this stage would be fantastic......where to start! :)
    A good place to start would be to read the first post on this thread ;)


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 649 ✭✭✭Cork selfbuild


    BryanF wrote: »
    where you have steels, what thermal breaks have you provided?

    All the horizontal steels are separated, there is 2 beams, one for each leaf, insulated in between.

    The structural uprights are sitting on a type of pad to try provide a break, like a rubber style pad. These will then be wrapped in insulation before being blocked around.

    The one in the ceiling is wrapped in insulation between slab, the airtight layer and ceiling insulation will then wrap under this again.


  • Registered Users Posts: 4 kc123


    Hi im just wondering if anyone has any recommendations for an engineer/assigned certifier in the Galway area? we are hoping to go direct Labour as we have friends who are brick layers, plasterers etc and are all registered, but most engineers/assigned certifiers we have talked to only want to work with building contractors, but it's working out so much more expensive this way. any recommendations welcome!


  • Registered Users, Registered Users 2 Posts: 1,583 ✭✭✭kkelliher


    kc123 wrote: »
    Hi im just wondering if anyone has any recommendations for an engineer/assigned certifier in the Galway area? we are hoping to go direct Labour as we have friends who are brick layers, plasterers etc and are all registered, but most engineers/assigned certifiers we have talked to only want to work with building contractors, but it's working out so much more expensive this way. any recommendations welcome!

    by pm only thank you


  • Registered Users Posts: 166 ✭✭about2build


    The new regulations if not require make it an imperative to have a main contractor builder over any new builds.....it sucks but way for government to attack the black economy


  • Registered Users Posts: 178 ✭✭Old Jim


    Got the results of my air-tightness test on my new build today. 0.6ACH. Happy with that.
    Block wall with 250mm pumped bead cavity. Sealing behind the electrical sockets made the big difference - 2.2 down to 0.6 after this was done.


  • Registered Users, Registered Users 2 Posts: 1,504 ✭✭✭BarneyMc


    Old Jim wrote: »
    Got the results of my air-tightness test on my new build today. 0.6ACH. Happy with that.
    Block wall with 250mm pumped bead cavity. Sealing behind the electrical sockets made the big difference - 2.2 down to 0.6 after this was done.

    Would you like to share how you sealed behind the sockets?


  • Advertisement
  • Closed Accounts Posts: 1,011 ✭✭✭ht9zni1gs28crp


    Id like to see that answer too, im not far off that stage!


  • Registered Users, Registered Users 2 Posts: 1,740 ✭✭✭hexosan


    BarneyMc wrote: »
    Would you like to share how you sealed behind the sockets?



    +1


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    What we did is chased the walls, use the pink bonding to parge the chase and back of the socket boxes and then pushed the box into the soft pink bonding mix.

    Might have a photo or two at home later

    0.54 ACH :)


  • Registered Users, Registered Users 2 Posts: 12,861 ✭✭✭✭mfceiling


    Becoming very regular to do the chases now.

    Saw one lad run airtight tape down the channel and then a throw of compound in the space where the socket box goes.

    By the sounds of things, the proof is most definitely in the pudding!!


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    I hope this helps

    An REMEMBER - inside walls should be treated the same (blocks are porous)

    We scud coated all walls - door reveals and the tops of the walls so that the block work was FULLY ENCASED in cement

    This picture also shows the row of Quinn at floor level to reduce thermal bridge downwards

    Also note the conduit went up to BELOW the membrane and then all cables etc run below the membrane (suspended ceiling). The only perforation through the membrane for cables (TV, Satalite, outside lights etc) was a single piece of ply in the center of the house with a hole for each cable which each of which was sealed with guke. Bunches of cables are hard to seal around,.

    In cupboard through door way you can see service ducts coming up - we had to go back and tape more proficiently than first done the DPC to the ducts. Put lots of ducts in you can always cap them - gates, lights, CCTV, alarm, garage, well, garden sockets, floor lights, Xmas lights ........

    Lastly I know sleep in passive comfort where this picture was taken (its the bedroom)

    340380.JPG


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 167 ✭✭lownhard


    fclauson wrote: »

    An REMEMBER - inside walls should be treated the same (blocks are porous)

    Why do the internal walls? Air coming up from the ground?


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    lownhard wrote: »
    Why do the internal walls? Air coming up from the ground?

    No - where you have it "T" with an external wall it will leak through the block work

    340388.jpg


  • Registered Users, Registered Users 2 Posts: 5,422 ✭✭✭just do it


    FC

    What's it costing you annually to heat your house? I know you have the figures ;):D


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    just do it wrote: »
    FC

    What's it costing you annually to heat your house? I know you have the figures ;):D

    Heating & Hotwater is of the order of 4000Kwh primary energy (electricity) for 350sqM - Hot water used around 65% of that number

    The PV on the roof (I have no solar thermal panels) produces around 4000Kwh and I use the grid as a "battery" - so the system has zero "running" costs.

    In reality the PV will pay for itself in around 7 years - (assuming the ESB Networks keeps paying me 9c per excess unit - they have stopped paying this for new connection) In any event we should never suffer #FulePoverty

    Reason for PV vs Solar Thermal is that in the summer we export around 1800Kwh and Solar Thermal would be "dumping" that excess while still trying to give meaningful input to the shoulder of the year (March April / Sept-Oct)

    Given there is no export payment would I do things differently today - may be - depending if building control would allow me to not explicitly meet the DEAP requirement of 10Kwh/sqM


  • Registered Users Posts: 178 ✭✭Old Jim


    BarneyMc wrote: »
    Would you like to share how you sealed behind the sockets?
    I was out of the country when it was done so don't have the full details but I believe it involved using a blue silicone-like sealant(Fortax 6400 by Gerband) and worked this into all the holes and edges of the metal backing box for all the electrical sockets. That adhesive is typically used for adhering airtight membranes to surfaces.
    Obviously the easier method is to parge the chases with this or other suitable airtight 'goo' or the pink bonding mentioned earlier before the electrical first fix is done.


  • Registered Users, Registered Users 2 Posts: 5,422 ✭✭✭just do it


    Old Jim wrote: »
    I was out of the country when it was done so don't have the full details but I believe it involved using a blue silicone-like sealant(Fortax 6400 by Gerband) and worked this into all the holes and edges of the metal backing box for all the electrical sockets. That adhesive is typically used for adhering airtight membranes to surfaces.
    Obviously the easier method is to parge the chases with this or other suitable airtight 'goo' or the pink bonding mentioned earlier before the electrical first fix is done.
    Well done on a great airtightness result - but more questions! What type of build? Single or two storey? Other elements of the airtightness strategy?

    Building a 2 storey at the moment and finding I'm educating people regarding airtightness, including the supplier of the airtightness membrane!


  • Registered Users Posts: 178 ✭✭Old Jim


    just do it wrote: »
    Well done on a great airtightness result - but more questions! What type of build? Single or two storey? Other elements of the airtightness strategy?

    Building a 2 storey at the moment and finding I'm educating people regarding airtightness, including the supplier of the airtightness membrane!

    Thanks. It's a 2-storey, fairly standard design. The design gave it the best chance of good airtightness - no chimneys, no recessed lights in the airtight layer. We wrapped the hollowcore on all sides, taped all penetrations, windows and doors, filled any ducts/conduits going into the attic. Lots of things we didn't do including taping the wall to floor junction, separating wires going through airtight layer - all the wires went though in the one place bunched tightly together and taped around.
    I wasn't expecting such a good result as we didn't focus massively on detailing.


  • Registered Users, Registered Users 2 Posts: 5,422 ✭✭✭just do it


    Old Jim wrote: »
    Thanks. It's a 2-storey, fairly standard design. The design gave it the best chance of good airtightness - no chimneys, no recessed lights in the airtight layer. We wrapped the hollowcore on all sides, taped all penetrations, windows and doors, filled any ducts/conduits going into the attic. Lots of things we didn't do including taping the wall to floor junction, separating wires going through airtight layer - all the wires went though in the one place bunched tightly together and taped around.
    I wasn't expecting such a good result as we didn't focus massively on detailing.

    Very interesting and good to hear. You'll have to stick up a few photos at some stage ;)


  • Registered Users, Registered Users 2 Posts: 5,422 ✭✭✭just do it


    Rather than hollowcore I've a solid reinforced concrete first floor. It's wrapped in membrane with mortar above and below it. I was very impressed with the dropping in of the slabs. The build is paused at this stage for a year. We've secured the edges of the membrane and sealed the top of the cavities as the dpcs were getting blown around by the wind. My concern is the integrity of the membrane will be damaged. Without going to extraordinary effort it's impossible to keep it dry. Time will tell.


  • Registered Users, Registered Users 2 Posts: 2,642 ✭✭✭Cavanjack


    Old Jim wrote: »
    I was out of the country when it was done so don't have the full details but I believe it involved using a blue silicone-like sealant(Fortax 6400 by Gerband) and worked this into all the holes and edges of the metal backing box for all the electrical sockets. That adhesive is typically used for adhering airtight membranes to surfaces.
    Obviously the easier method is to parge the chases with this or other suitable airtight 'goo' or the pink bonding mentioned earlier before the electrical first fix is done.

    Would silicone or mastic do the same job as the product you used?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    Cavanjack wrote: »
    Would silicone or mastic do the same job as the product you used?

    yes until it dries out and shrinks - there is a reason these products are more expensive !!


  • Registered Users, Registered Users 2 Posts: 2,642 ✭✭✭Cavanjack


    fclauson wrote: »
    yes until it dries out and shrinks - there is a reason these products are more expensive !!

    Wouldn't have known that. Thanks. What is the pink bonding that you parged the back of the chases with? Is it just standard gypsum hard wall?


  • Registered Users, Registered Users 2 Posts: 1,691 ✭✭✭fclauson


    Cavanjack wrote: »
    Wouldn't have known that. Thanks. What is the pink bonding that you parged the back of the chases with? Is it just standard gypsum hard wall?

    Yes !


  • Registered Users, Registered Users 2 Posts: 9,149 ✭✭✭893bet


    Slow work!!


  • Registered Users, Registered Users 2 Posts: 15,951 ✭✭✭✭Villain


    893bet wrote: »
    Slow work!!

    It is, I remember it well but well worth it, try make sure tape isn't tight on the corners so when window boards are "beaten" into they place they won't puncture the tape.


  • Registered Users, Registered Users 2 Posts: 9,149 ✭✭✭893bet


    Villain wrote: »
    It is, I remember it well but well worth it, try make sure tape isn't tight on the corners so when window boards are "beaten" into they place they won't puncture the tape.

    I have learnt that already. There is a good chance the first window will get redone as I learn!


  • Banned (with Prison Access) Posts: 144 ✭✭THE DON FANUCCI


    893bet wrote: »
    Slow work!!


    what did you fill your cavity with? and how did you close the cavity at the windows? that tape looks great job! painstaking i'd say. did you fit it? or can you hire somebody to do this?


  • Registered Users, Registered Users 2 Posts: 9,149 ✭✭✭893bet


    what did you fill your cavity with? and how did you close the cavity at the windows? that tape looks great job! painstaking i'd say. did you fit it? or can you hire somebody to do this?

    Cavity to be fully filled. Cavity closed with PIR tightly wedged. Did the tape myself. You can hire someone but I would recommend the DIY route. It's not that tough.


  • Registered Users, Registered Users 2 Posts: 9,149 ✭✭✭893bet


    Electritions are flying! Really happy with how neat they are!


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 178 ✭✭Sligoronan


    893bet wrote: »
    Electritions are flying! Really happy with how neat they are!
    How do you intend to achieve air tightness behind sockets and chases?
    U only get one chance at it.