Do we need a second shower pump?

Options
  • 28-03-2024 10:29pm
    #1
    Registered Users Posts: 176 ✭✭


    Hi,

    We have an attic conversion with an ensuite and we've got a Stuart turner 2 bar negative head pump in the hot press to pump hot and cold to the attic. We are now thinking of putting a new shower into our main bathroom (which is currently electric) - would we need to put a second pump in (positive head?) or would we be able to replace the current pump with a more powerful one to handle both bathrooms?

    Thanks!



Comments

  • Registered Users Posts: 16,881 ✭✭✭✭Sleeper12


    The negative head will work fine for both bathrooms just not at the same time. Pressure wouldn't be great with 2 bar pump running 2 showers at the same time



  • Registered Users Posts: 176 ✭✭Ricey3509


    thanks - would a 3 bar be sufficient to run both concurrently?



  • Registered Users Posts: 3,466 ✭✭✭John.G


    3bar shoild bw OK IMO, the 2bar will give 7LPM from each end at a 1.5bar head & the 3bar will give 14LPM from each end at 1.5bar, you will get a reduced flow though with both on together depending on the distance from the pump but the 4.5bar pump but very much of a overkill IMO.



  • Registered Users Posts: 1,352 ✭✭✭Lenar3556


    An alternative might be to use a constant pressure pump such as the DAB EsyBox Mini.

    On these you can set the desired pressure on the digital display and the pump will ramp up and down as necessary depending on demand to maintain the set pressure.



  • Registered Users Posts: 3,466 ✭✭✭John.G


    This would then need the installation of a unvented cylider?.



  • Advertisement
  • Registered Users Posts: 1,352 ✭✭✭Lenar3556


    sorry yes, that pump wouldn’t be suitable for both hot and cold feed to a shower without an unvented cylinder. (It’s not a dual pump)

    The continually ramping constant pressure functionality was what I was promoting. I have had good experiences with them - works very well to deliver consistent pressure and flow rates even with multiple outlets being turned on and off at different times.