sigh...
Quote:
Remove the double pole mcb that's the input for the inverter and go direct to the RCBO instead
|
You can't protect against overcurrent on an inverter output. They can't supply the power...it's not like the grid where a short circuit has the ESB Network to throw at the circuit breaker.
Earth leakage is all you need. RCBO, RCD..whichever.
Quote:
neutral out of the inverter to the earth of the van (chassis), most likely at the output point of the RCBO above
|
Earth to the neutral of the generator upstream of the RCD. In this case, the inverter. The earth is connected to the van chassis but that's further downstream and tangental.
You're making a fault path that will create an imbalance on the RCD and enable it to trip if there's an issue.
Shore power will already be neutralized so make sure your inverter neutralisation point is exclusive to inverter operation ie. upstream of the changeover contactor.
Quote:
Earth output & body of inverter to van chassis
Earth the consumer unit to the van chassis |
When you say van chassis it ought to be the earth bus. The chassis and all metalwork with a mains appliances are connected to that earth bus.
Gauranteed break before make. It stops you creating 400v from contact arcs in places you don't want.
Quote:
Check for continuity between live and van shell & neutral and van shell too with the system unpowered. Should be neither if you're floating earth.
Quote:
Are you referring to the final 240 supply feeding to the sockets to check?
|
You checked you have mains and inverter at the outputs.
You also need to check that you don't have inverter and mains at their counterparts inputs.
ie. no mains at the inverter output upstream of the changover and no inverter at the EHU pins upstream of the contactor.