Are Single Module RCBO faster reacting than Double Module?

I'm having issue with nuisance tripping.
2U RCBO works fine 20A 30mA, trip time 28ms
1U RCBO is nuisance tripping 32A, 30mA trip, time 25ms and 8ms with a 180° offset.


I'd rather use the 1U for reasons but it's too sensitive. If I get another will it be the same?


Hager AD920J (2U)
Hager ADA332G (1U)
Sir Liamalot is offline  
Advertisement
26-11-2020, 12:19   #2
2011
Moderator
 
Join Date: Apr 2009
Posts: 10,524
Are these feeding nonlinear loads?
I do not see why the width of the device and nuisance tripping would be related.
In terms of reliability I would consider Schnieder Electric RCBO’s to have the edge on Hager. Schnieder make 1 mod RCBO’s.
2011 is offline  
Thanks from:
26-11-2020, 12:31   #3
Sir Liamalot
Combobulator
 
Sir Liamalot's Avatar
 
Join Date: Mar 2010
Posts: 5,009
Synchronising inverters tripping with load transfer feeding the house (test load). So yeah fridge motors and leds.
It does it with purely resistive loads too though. It's something to do with the phase shift.
Sir Liamalot is offline  
26-11-2020, 12:43   #4
Sir Liamalot
Combobulator
 
Sir Liamalot's Avatar
 
Join Date: Mar 2010
Posts: 5,009
Quote:
Originally Posted by 2011 View Post
Schnieder make 1 mod RCBO’s.

Acti-9 won't fit unless I put them upside-down...
Sir Liamalot is offline  
26-11-2020, 13:07   #5
Sir Liamalot
Combobulator
 
Sir Liamalot's Avatar
 
Join Date: Mar 2010
Posts: 5,009
I just ordered a Schneider EZ9D16832
Rebranded GET so I'm not 100% on yer brand confidence.

I'll let you know if it fairs any better. Cheers.
Sir Liamalot is offline  
Advertisement
26-11-2020, 13:57   #6
 
Join Date: Nov 2020
Posts: 248
They should be fairly random the trip times shouldn't they?

Anything over 1/2 I∆N

Are.any of single mod units actual double pole switching?
Pasteur. is offline  
26-11-2020, 15:07   #7
2011
Moderator
 
Join Date: Apr 2009
Posts: 10,524
Quote:
Originally Posted by Sir Liamalot View Post
Synchronising inverters tripping with load transfer feeding the house (test load).
The high frequency PWM switching of inverters can cause nuisance tripping.
This can still be an issue even if the inverters are supplying a resistive load.
2011 is offline  
26-11-2020, 16:45   #8
Sir Liamalot
Combobulator
 
Sir Liamalot's Avatar
 
Join Date: Mar 2010
Posts: 5,009
I swapped the RCBO. Had no problem with the last one. I only use low frequency inverters because they're waaaay better and the HF requirement of B-type RCDs are a waste of money I could just spend on transformer surge capability instead.

Pretty consistent trip times on a digital RCD tester.
Occasionally didn't nuisance trip when the master and slave gensets were harmonising or swapping roles but did most of the time.

There's no fault on the load side.
Sir Liamalot is offline  
26-11-2020, 16:56   #9
Sir Liamalot
Combobulator
 
Sir Liamalot's Avatar
 
Join Date: Mar 2010
Posts: 5,009
1U RCBOs only interrupt the Live. Single phase TN-S application.

And yes both sets are TN-S but not at the same time.
A double pole would be better in hindsight but I sacrificed the space to metering and a 16A sub.
Sir Liamalot is offline  
Advertisement
26-11-2020, 17:03   #10
 
Join Date: Nov 2020
Posts: 248
Quote:
Originally Posted by Sir Liamalot View Post
1U RCBOs only interrupt the Live. Single phase TN-S application.

And yes both sets are TN-S but not at the same time.
A double pole would be better in hindsight but I sacrificed the space to metering and a 16A sub.
Don't think double pole is strictly required for TN
Pasteur. is offline  
26-11-2020, 18:50   #11
Sir Liamalot
Combobulator
 
Sir Liamalot's Avatar
 
Join Date: Mar 2010
Posts: 5,009
It's not. Would be for floating applications which is a possibility (like right now ironically). I can always put a module inline on a fly lead for this. It's not something I'd elect to do without good reason though. TN-S is my prefered method.
Sir Liamalot is offline  
26-11-2020, 18:58   #12
2011
Moderator
 
Join Date: Apr 2009
Posts: 10,524
Quote:
Originally Posted by Pasteur. View Post
Don't think double pole is strictly required for TN
As far as I recall it is a requirement in ROI. I will look later if I get a chance.

Anyway 1 mod wide RCBO's are available with 2 pole switching.
2011 is offline  
(2) thanks from:
26-11-2020, 19:03   #13
Sir Liamalot
Combobulator
 
Sir Liamalot's Avatar
 
Join Date: Mar 2010
Posts: 5,009
Do building regs apply when there's no building or/nor utility involved?

If you do find a reference I'd appreciate the feedback. I like the space-saving so would bias 1Us for this.

I'll have a look for double pole breaking too. Obviously better.
Sir Liamalot is offline  
26-11-2020, 19:44   #14
 
Join Date: Nov 2020
Posts: 248
Quote:
Originally Posted by 2011 View Post
As far as I recall it is a requirement in ROI. I will look later if I get a chance.

Anyway 1 mod wide RCBO's are available with 2 pole switching.
I haven't checked either but I think they use the phrase

"Neutral reliably at earth potential" for everything TN

Which means only have to switch the phase/ line
Pasteur. is offline  
26-11-2020, 19:46   #15
 
Join Date: Nov 2020
Posts: 248
Quote:
Originally Posted by 2011 View Post

Anyway 1 mod wide RCBO's are available with 2 pole switching.
That's good to know thanks
Pasteur. is offline  
Post Reply

Quick Reply
Message:
Remove Text Formatting
Bold
Italic
Underline

Insert Image
Wrap [QUOTE] tags around selected text
 
Decrease Size
Increase Size
Please sign up or log in to join the discussion

Thread Tools Search this Thread
Search this Thread:

Advanced Search



Share Tweet