Hi. I’ve a warm flow oil boiler. Runs 3 zones but water taken off it atm. Lately it’s started kicking in and running for a few minutes throughout the day and night. I’ve checked the motorised valves and all working fine. I changed room thermostat downstairs also. It works fine when turned on from the control panel. When control panel off and it kicks in by itself it doesn’t heat any of the rads so at least that’s ok. What would be next to check
|
![]() |
Advertisement
|
|
19-01-2021, 13:41 | #3 |
Registered User
![]() |
Yeah it started a few weeks ago when temperatures were down but wasn’t too worried as I thought it was just the frost stat. But it never stopped
|
![]() |
19-01-2021, 14:15 | #4 |
Moderator
![]() |
|
![]() |
Thanks from: |
Advertisement
|
|
20-01-2021, 12:51 | #6 |
Registered User
![]() |
Yep. It looks like the micro switch is stuck. Thanks. I’ve got a new one different model. Only thing is that in the new one the grey wire says normally connected to boiler and pump and orange wire normally to the 230v opposite from the old one. Does it make any difference
|
![]() |
20-01-2021, 13:15 | #7 |
Registered User
![]() |
All microswitches are wired in parallel such that any zone valve indicating open will start the boiler. So you just need to identify the pair of wires feeding the old microswitch and disconnect from your wiring centre and duplicate the wiring setup with the new valve.
|
![]() |
20-01-2021, 13:27 | #8 | |
Registered User
![]() |
Quote:
|
|
![]() |
20-01-2021, 13:44 | #9 |
Registered User
![]() |
It shouldn't make any difference. If you have 3 zone valves then all 3 orange should be connected to one terminal and all 3 grey to another terminal. But you can 'mix and match', e.g. orange/orange/grey on one terminal and then grey/grey/orange on the other. All 3 switches are wired in parallel for either option.
|
![]() |