    We have an A rated house of 240 square metres, it's a detachable bungalow built in 2014. We currently have oil heating with radiators, no underfloor heating and also have a solid fuel stove that can heat our water for the rads, we are looking into changing to an air to water system. Has anyone done similar looks for pros and cons and general thoughts on air to water system?



Comments

  • Registered Users, Registered Users 2 Posts: 2,342 ✭✭✭Lenar3556


    I’d be slow to go down that road.

    Radiators may not be large enough for lower flow rates on A2W.

    Electricity supply to house may be undersized. You really need 16KVA.

    It will probably be more expensive to run, when you consider current kerosene and electricity prices.




  • Registered Users, Registered Users 2 Posts: 21 marcobass


    Much appreciated....they forecasting a 13kw system and they think that radiator size are ok....thank you.



  • Registered Users, Registered Users 2, Paid Member Posts: 8,803 ✭✭✭ongarite


    What heat pump are they recommending to install? Is it a R290 refrigerant model which is better suited to radiators as it has higher flow temperatures?



  • Registered Users, Registered Users 2 Posts: 2,342 ✭✭✭Lenar3556


    Your high insulation levels will be favourable.
    What is the total cost?



  • Registered Users, Registered Users 2, Paid Member Posts: 21,965 ✭✭✭✭Cyrus




  • Advertisement
  • Subscribers, Paid Member Posts: 44,732 ✭✭✭✭sydthebeat


    Quote possible that would be required where you have a heat pump, electric shower and electric cooker.

    High load + instant demand = higher risk of tripping out



  • Registered Users, Registered Users 2 Posts: 2,342 ✭✭✭Lenar3556


    Because of the demand. A 13KW (output) air to water heat pump can be a 7KW electrical load at times. That’s 30A alone.

    A standard 12KVA supply is rated for a maximum of 52A continuous. So there wouldn’t be headroom for an electric shower, induction hob or effective EV charging for example.



  • Registered Users, Registered Users 2, Paid Member Posts: 21,965 ✭✭✭✭Cyrus


    That heatpump sounds over sized for a start, our house is 192 sqm and i think we have a 5KW samsung system that never goes over 2.5KW load. Id be amazed if you needed 7kw to heat a 240sqm a1 rated house. Also why would someone with a heatpump / modern house have an electric shower, thought they were gone since the 90s?



  • Moderators, Home & Garden Moderators Posts: 6,698 Mod ✭✭✭✭Wearb


    I dont think the op stated A1, just A. Also the house is 25% larger than yours.



  • Registered Users, Registered Users 2, Paid Member Posts: 21,965 ✭✭✭✭Cyrus


    Ok sorry thought i read A1, yes its 25% larger, would that require 200% more heat output? And electric showers? are they still a thing?



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 62 ✭✭greenbin2


    I love my electric shower, use it all summer

    I only use it on the lower power

    But I am a miserably cheap person



  • Registered Users, Registered Users 2 Posts: 21 marcobass


    Hi guys

    No electric shower need, also cooker is gas....only oven is electric.

    We do not use too much power through the day and we have solar system for 4.5kw... once out of the winter tunnel quiet self sufficient in the power side.

    We just worried about do a 20k( new grant coming inj)ob on air to water and the house will not be warm- insulation seem good enough,is a passive house and h-l-i is just below 1.9



  • Registered Users, Registered Users 2, Paid Member Posts: 21,965 ✭✭✭✭Cyrus


    whats prompting the move? 20k will buy a lot of oil, and heat pumps work best with UFH which you dont have.



  • Registered Users, Registered Users 2 Posts: 21,838 ✭✭✭✭Water John


    The only reason to make the switch would be for environmental reasons. With the good grants, it is the optimum time to consider it. A priority switch would solve any load issues. I'd be getting a second opinion on A2W size required. Any A rated house is easily heated.



  • Registered Users, Registered Users 2 Posts: 66 ✭✭ImTiredOfItAll


    You need an airtight home for a heatpump. Heatpumps heat the rads to a much lower tempeture. Little more that luke warm. Designed corectly this is fine. Without airtightness on days like today the heat will be sucked out of the home. Because heatpumps run the rads at such a low tempeture it takes a long time to get rooms back up to tempeture.



  • Registered Users, Registered Users 2, Paid Member Posts: 8,803 ✭✭✭ongarite


    Not if they are being recommended to install of r290 heat pump system. These run with water temperatures comparable to oil,gas boiler so can work with existing radiators.

    I asked earlier what system they were recommended but haven’t got answer so far.



  • Registered Users, Registered Users 2 Posts: 1,137 ✭✭✭Jonnyc135


    I think the SEAI are only piloting these heat pumps now in order to see if they will issue them with grants down the line.

    If I was th OP, I would hold off let the technologies develop. At the end of the day they are in an A rated house already with high insulation value which would mean low usage of solid fuel and oil to run the house as is. There are already doing their bit for the environment.

    Low temp air to water hp are better suited to Underfloor heating, I would let the high temperature HP develop and when they approve it for the grant then it may well be a good option



  • Registered Users, Registered Users 2 Posts: 2,342 ✭✭✭Lenar3556


    I couldn’t comment on the sizing without seeing it. But it’s a big house, and a 2014 build would have been in the earlier stages of the energy efficient construction methods that are common today.

    Again I don’t know the specific case, but a house of that size would typically have an annual domestic hot water requirement in the region of 6000 Kwh.

    But I was to hazard a guess, 13KW would seem comfortable. Many of these units have defrost and purification heaters which push up the instantaneous current consumption considerably when they are active.



  • Registered Users, Registered Users 2 Posts: 21 marcobass


    Viessmann 13 kw heat pump. They suggesting a buffer tank for the back boiler of the fireplace ( not to interfere with the system)

    The reason we looking at it is that we have heating on for 3h a day but for the 6 month a year is taking 1000 lt of oil.

    If I have to pay these money I like to have the house warm for most of the day and not only 3 h



  • Registered Users, Registered Users 2, Paid Member Posts: 21,965 ✭✭✭✭Cyrus


    6000kwh for DHW? that would be 16kwh per day for DHW, sorry that's way off.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,342 ✭✭✭Lenar3556


    R290 units can run at temps coming close to oil/gas boilers, but with significant COP degradation.



  • Registered Users, Registered Users 2 Posts: 21,838 ✭✭✭✭Water John


    A2W needs to be left on at a regular temp, in our case 19/20c, all the time through the winter. They are not meant to be used intermittently. They don't have the capacity to raise room temp quickly. These systems already do the DHW at a higher temp, and go higher again once a week to prevent Legionaires.



  • Registered Users, Registered Users 2 Posts: 2,342 ✭✭✭Lenar3556


    Why do you think it’s way off? It’s actually quite conservative if you consider a family of 5 which would be a reasonable assumption for a house of that size.

    To put it in perspective, 16Kw/h a day will give you a combined daily total of 20 - 25 minutes of power shower. So 5 No. 4 minute showers, without considering any handwashing, kitchen sink wash up etc.



  • Registered Users, Registered Users 2, Paid Member Posts: 21,965 ✭✭✭✭Cyrus


    if i pick a month where there was no heating say last June July or August, we used 55kwh on average in those months which was all DHW basically, family of 4.

    Now my kids are pre teen so they arent showering daily but even if they were its a big jump from less than 2kwh per day on average to 16 wouldnt you agree?



  • Registered Users, Registered Users 2 Posts: 2,342 ✭✭✭Lenar3556


    If it works for you, great.

    But I’m telling you that isn’t representative of a typical household’s hot water requirements. And it would be misleading to tell a family that putting 55Kw/h a month into a cylinder is going to give them a reasonable quantity of hot water - it isn’t.

    You are taking about one 3-4 minute shower a day at that rate.

    When you say you used 55Kw/h - where are you getting this figure from and what precisely is it this figure representing?



  • Registered Users, Registered Users 2, Paid Member Posts: 21,965 ✭✭✭✭Cyrus


    We aren't, there are two adults a day taking showers and using whatever hot water is needed from taps at the least with one or both of the kids being showered on some days too.

    I have a shelly energy monitor on the heat pump , that figure represents the total energy consumed by the heatpump in the months I stated , I am making the reasonable assumption that there is no heating required in those months , if there is then the dhw usage would be lower.

    Given I am the one providing actual figures and you are maintaining I am wrong do you care to offer any data yourself ?

    Few others reporting their monthly usage as well in this thread no one reporting dhw usage like that

    https://www.boards.ie/discussion/2058281726/heat-pump-running-costs/p22



  • Registered Users, Registered Users 2 Posts: 2,342 ✭✭✭Lenar3556


    So that’s a different scenario entirely.
    The shelly energy monitor will tell you the electrical energy your heat pump is consuming, not what heat it is producing. In the middle of summer the heat pump should easily have a COP of 4. So the 55Kw/h input energy will be about 220Kw/h output, and that is your monthly domestic hot water heating requirement, not 55Kw/h.

    Multiply that out across the year, and make an allowance for colder supply water temperatures in winter and you are looking at about 3,000Kw/h+ of annual DHW heat requirement, which is on the lower end of the normal range.



  • Registered Users, Registered Users 2, Paid Member Posts: 21,965 ✭✭✭✭Cyrus


    Fair enough that wasn't clear to me from your post, my system is a bit older and doesnt report COP so my only focus is on a) maintaining a comfortable temp in the house and b) minimising the amount of energy used to achieve that / or at least minimising the cost of that energy by using it when electricity is cheap.



  • Registered Users, Registered Users 2 Posts: 2,342 ✭✭✭Lenar3556


    And you’re doing very well by all accounts. You have something that’s working for you and you’re keeping an eye on it.