WIndow Jamb closers - requriemnet for firestop or propritary cavity closers

  • 05-06-2024 9:21am
    #1
    Registered Users, Registered Users 2 Posts: 4


    Hi,

    Is it acceptable to close the cavity around a window with packed PIR insulation or is there a requirement for propriatry cavity closers/firestop products to be used?

    It is a 200mm pumped cavity with blockwork internal and external leafs.

    Thanks



Comments

  • Registered Users, Registered Users 2 Posts: 46,550 ✭✭✭✭muffler


    Proprietary closers are best practice but other methods may be acceptable providing your assigned certifier can sign off on same.



  • Registered Users, Registered Users 2 Posts: 400 ✭✭Biker1


    Proprietary closers are an expensive option and make airtightness sealing more difficult. Best practice is to return the inner leaf of the blockwork to 100mm from the outer leaf and fill the remaining gap with PIR insulation.