Export Power Management

  • 22-03-2024 4:41pm
    #1
    Registered Users, Registered Users 2 Posts: 62 ✭✭


    Export Power Management

    My 15 panels with Solis Hybrid Inverter were generating no more than 2kWh per day

    The problem was that the Backflow Power which is how much power the system is allowed to export to the Grid was set to low at 200w. The solution was to change this to 5000w matching the output rating of the inverter.

    On the Inverter you go to Menu Advanced Settings Backflow Power On/Off

    This should help

    https://www.youtube.com/watch?v=1aFcX0OYyXc&t=33s

    I knew nothing of this until yesterday, and hope it is a help to others

    The change in generation is beyond expectations