Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Earth rod requirement

  • 02-03-2024 8:20am
    #1
    Registered Users, Registered Users 2 Posts: 1,506 ✭✭✭


    Have ordered solar panels and had them out at the house etc.

    Now shortly before the install they have told me I need an earth rod (Don't have one) and that it needs to be installed before they arrive for installation.

    I'm annoyed that this wasn't said to me before signing up. What would be the cost of getting one installed? Do any companies include that as part of install?

    Thanks



Comments

  • Moderators, Home & Garden Moderators Posts: 6,634 Mod ✭✭✭✭graememk


    All installs (houses) are meant to have an [inspectable] earth rod.

    You do likely have one but no idea where it is (and unmarked, )

    Did the solar company not offer to put one in(at a reasonable cost?)



  • Registered Users, Registered Users 2 Posts: 8,071 ✭✭✭10-10-20


    Agreeing with Graememk, it's supposed to be there in the first place. Not saying that it isn't - but if you can't find it then you can't evaluate it. Annoying I know, but they can't account for every nuance I suppose.



  • Registered Users, Registered Users 2 Posts: 5,181 ✭✭✭standardg60


    How old is the house OP?

    Anything built from the seventies should have one, could be buried or obscure somewhere. Have a look near the meter cabinet, be a green box or just a steel bar with earth wire attached.



  • Registered Users, Registered Users 2 Posts: 1,506 ✭✭✭maynooth_rules


    House was built in 2002. Spoke to last owners who built it, and they say it is somewhere under the meter box but a path has been put over it since.

    Solar company haven't offered the option of putting it in. I just got told it needs to be there for them



  • Registered Users, Registered Users 2 Posts: 1,506 ✭✭✭maynooth_rules


    Have these two boxes below our meter box, but don't think they are of use for earth rod




  • Advertisement
  • Registered Users, Registered Users 2 Posts: 8,071 ✭✭✭10-10-20


    That looks like they installed the power cable along soil pipes... odd to say the least! Can you see the green/yellow earth cable from the meter box at all?



  • Moderators, Home & Garden Moderators Posts: 6,634 Mod ✭✭✭✭graememk


    Could have just used the risers as inspection.

    Although that doesn't look like a meter box, more like the telecoms box (seems very low to be a meter box)



  • Registered Users, Registered Users 2 Posts: 2,875 ✭✭✭Buffman


    They're water so no good to you. If it's an estate can you ask any of the neighbors if they know where their ones are?

    A 2002 house should have one but if you don't see a little green or grey box like below or a rod sticking up somewhere then it's probably been buried and is inaccessible.

    FYI, if you move to a 'smart' meter electricity plan, you CAN'T move back to a non-smart plan.

    You don't have to take a 'smart' meter if you don't want one, opt-out is available.

    Buy drinks in 3L or bigger plastic bottles or glass bottles or cartons to avoid the DRS fee.



  • Registered Users, Registered Users 2 Posts: 1,506 ✭✭✭maynooth_rules




  • Registered Users, Registered Users 2 Posts: 1,506 ✭✭✭maynooth_rules


    Nope, unfortunately. All I've been told by my solar company is that it's a simple install. That's all I have to work.

    What's the ball park figure for getting one installed?



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 5,181 ✭✭✭standardg60


    I'm gonna guess it's there somewhere OP, the box is only 10cm square, so check under that debris on the left and any other.

    Edit. Zooming into the inspection chamber on the right that's not an earth rod with Denso tape on top at the bottom by any chance?



  • Moderators, Arts Moderators, Recreation & Hobbies Moderators Posts: 10,885 Mod ✭✭✭✭Hellrazer


    I take it your in Maynooth?

    Same problem here last year (Maynooth) I installed my own and it only cost me the cable, earth rod and a big 1.2m drill bit - around €100.00 euros - If you want to diy it I can loan you the big **** off drill bit and show you how I did it!!!!



  • Moderators, Home & Garden Moderators Posts: 6,634 Mod ✭✭✭✭graememk


    You drilled? we just sledged it in! (although it was a galv. Steel rod, not the copper ones you see the ones in the UK putting in.)



  • Moderators, Arts Moderators, Recreation & Hobbies Moderators Posts: 10,885 Mod ✭✭✭✭Hellrazer


    Because of the location of my fuse board (its in the garage which is converted to a sitting room) I had to drill through what I reckon was 1.5 to 2 feet of concrete out side the garage window on the drive way. Bought a 16mm drill bit that was 1.2m long just in case the concrete was thicker and drilled straight through the concrete and into the hard pack and then hammered it in the rest of the way. I did use a longer rod though - 1.8 meters I think to make up for the thickness of he concrete.

    Worked out well and only took about 15 minutes.

    Ran the earth cable from the spike back to the fuse box in conduit and bonded all the pipes myself running 2 new earth cables back as well. Reci said I saved about 500 euros - the pipe bonding took the longest as I had to bond all the copper pipes and then run everything up into the attic and back down to the fuse board.



  • Registered Users, Registered Users 2 Posts: 53 ✭✭captivo


    Hi - Sorry to hijack the thread. I have a similar issue as the OP. House built 2020ish. Planning on getting Solar panels and one of the sales guys who called out mentioned about the need for the earth rod. We had a look around couldn't find a green box.

    We're trying to track down the electrician who wired the house. Have a lead so hopefully I'll be able to contact him.

    Anyway in the meantime, I did a bit of looking around myself. 2 things. There is an earth wire in the meter box (picture attached), but I'm lead to believe that whilst this is an earth, an earth rod is still required.

    Second thing - I looked at the fuse box in the utility and saw that there are 4 wires coming out from the bottom. Can't take a pic as I can barely see in. 3 of the (thick black coated) wires are (I believe) going to the garage. One for water pump, one appears spare, (I believe for potential EV charger) and one to small fuse box in garage. The 4th wire is what appears to be an earth wire (green and yellow) and seems to be going under ground. But I've no idea where to. Would I be correct in assuming that this could be leading to an earth rod?

    If the earth rod is in place, would it be possible to find it using a metal detector? I'm assuming that the earth rod if it exists is in the general direction of the garage.




  • Registered Users, Registered Users 2 Posts: 239 ✭✭AmpMan


    You can look at the earth bar in the consumer unit and see how many 10sq cables are heading out.

    Count them and rule out the ones you can find (water,gas) and if you have any unaccounted for its probably the rod and you can investigate further.



  • Registered Users, Registered Users 2 Posts: 53 ✭✭captivo


    Is an earth rod a requirement for certification?



  • Registered Users, Registered Users 2 Posts: 62 ✭✭Seventy Plus


    Can they tie into the Earth in the ESB supply?



  • Moderators, Home & Garden Moderators Posts: 6,634 Mod ✭✭✭✭graememk


    It's not that they have to tie in to the earth rod, they need to verify that it exists and is in good condition.



  • Registered Users, Registered Users 2 Posts: 1,506 ✭✭✭maynooth_rules


    That's my meter box


    Thanks for the very kind offer @Hellrazer . Despite the name I'm not in maynooth any more. I'm over an hour away



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 62 ✭✭Seventy Plus


    If the Earth Rod reading is High? Does this mean that it is not in good condition?



  • Registered Users, Registered Users 2 Posts: 5,181 ✭✭✭standardg60


    Did you establish that your earth rod was in the inspection chamber on the right?



  • Registered Users, Registered Users 2 Posts: 1,506 ✭✭✭maynooth_rules


    Not there. That's the internet and phone line coming in, and the bit of green that can be seen was a leaf



  • Moderators, Home & Garden Moderators Posts: 6,634 Mod ✭✭✭✭graememk


    Any other inspection chambers possibly near where the consumer unit is (fusebox)



  • Registered Users, Registered Users 2 Posts: 5,181 ✭✭✭standardg60


    Ah ok so still no joy then? I've seen them half buried in the concrete and barely visible, any subsequent patios or decking laid? Could be under those too.

    Otherwise it's as Hellrazer did above, good job btw!



  • Registered Users, Registered Users 2 Posts: 2,738 ✭✭✭allinthehead


    Must be visible and available for inspection.

    No, not permissible. Earth rod cable must go back to the main earth terminal in the consumer unit.

    If the impedance is high it can mean a number of things. Poor termination, poor earth/soil resistivity, damaged cable, cable too small for length of run etc.

    ☀️



  • Registered Users, Registered Users 2 Posts: 2,738 ✭✭✭allinthehead


    Earth rod would usually be very close to the main consumer unit. Think, if you were to run a cable, what's the shortest easiest route from the main board.

    ☀️



  • Registered Users, Registered Users 2 Posts: 899 ✭✭✭ColemanY2K


    Quick question. The father has covered the earth rod when pouring the concrete for the footpath. I'm not 100% where it is but I do know it's somewhere behind the ASHP. Is this a problem? Will I need a new earth rod?

    🌞 7.79kWp PV System. Comprised of 4.92kWp Tilting Ground Mount + 2.87kWp @ 27°, azimuth 180°, West Waterford 🌞



  • Registered Users, Registered Users 2 Posts: 8,071 ✭✭✭10-10-20


    Only if somebody needs to see and test the earth rod does it become a problem. Is somebody asking?



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 899 ✭✭✭ColemanY2K


    No nobody is asking but the engineer has yet to sign the house off. The electrician has issued his completion cert though.

    🌞 7.79kWp PV System. Comprised of 4.92kWp Tilting Ground Mount + 2.87kWp @ 27°, azimuth 180°, West Waterford 🌞



  • Registered Users, Registered Users 2 Posts: 8,071 ✭✭✭10-10-20


    Open to correction here but electrically signed off is electrically completed. But it should have been left in a green inspection chamber anyway.



  • Registered Users, Registered Users 2 Posts: 899 ✭✭✭ColemanY2K


    That it wasn't I'm sure of or the father wouldn't have concreted it over.

    🌞 7.79kWp PV System. Comprised of 4.92kWp Tilting Ground Mount + 2.87kWp @ 27°, azimuth 180°, West Waterford 🌞



Advertisement