Cable Size between CU & Inverter

  • 02-02-2023 05:39PM
    #1
    Registered Users, Registered Users 2 Posts: 62 ✭✭


    Hi All,

    The folks are looking at solar (6kw inverter) and have a 6mm2 cable running between the shed and house.

    What would be the max distance between the CU & Inverter before it becomes unsafe?

    They will be getting a sparky out to provide guidance etc but they are like hens teeth at the moment.

    Obviously they would like to avoid digging the garden up but while they wait for the sparky, they are happy to craic on with ground works if they are way outside the max distance on a 6mm2.

    Thanks.



Comments

  • Moderators, Sports Moderators Posts: 18,421 Mod ✭✭✭✭slave1


    I've a 16m 6sq run, no issues

    My stuff on Adverts, mostly Tesla Pre Highland Model 3

    Public Profile active ads for slave1



  • Registered Users, Registered Users 2 Posts: 178 ✭✭johndoe11


    I had a 40m run to the shed that was 6mm2 cable. The installer wouldn't commission without it being a 16mm2. I have a 6kw hybrid inverter. A messy and costly job, but it's done now forever.



  • Registered Users, Registered Users 2 Posts: 62 ✭✭Scoobydoobydoo101


    Thank you @slave1 that's certainly good info.


    @JohnDoe that is precisely why they would like to avoid the work. I have 10mm2 myself over a similar run with no issues


    Looking at some online calculators they seem to suggest that a 6mm2 is suitable based on 30amps over 40m with 10%voltage drop....



  • Registered Users, Registered Users 2 Posts: 178 ✭✭johndoe11


    Yeah I think 10mm2 would have been fine, but they said if going to that effort just put 16mm2 in. The said if it was a 6mm2 just dedicated to solar it might be ok, but I'm no expert on that. I just left the old 6mm2 in and ran the new cable to a new board beside the old one. Not much change from 1k when it's all done.