Airlock upstairs on fitting new boiler

  • 05-11-2022 3:43pm
    #1
    Registered Users, Registered Users 2 Posts: 12,881 ✭✭✭✭


    All rads downstairs working.

    Upstairs rads and DHW cylinder heating coil not working.

    flow and return go under the floor from outside boiler room and I don't know where the upstairs circuit starts, may be under the DHW cylinder

    2 bar pressure in the system

    The bathroom rad is full of water when I bleed it

    There is an air vent on a tee off the DHW heating coil in hot press


    All suggestions welcome.

    Thanks as always

    “I can’t pay my staff or mortgage with instagram likes”.



Comments

  • Registered Users, Registered Users 2 Posts: 1,004 ✭✭✭Pinoy adventure


    There is a vent on the pump above the gas boiler.



  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    What type of boiler?

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    turn off the downstairs rads



  • Registered Users, Registered Users 2 Posts: 12,881 ✭✭✭✭Calahonda52


    Grant Vortex outdoor oil 21-36 kW

    Sealed system

    “I can’t pay my staff or mortgage with instagram likes”.



  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    They can be a hoor to bleed. Let off a few litres from the safety valve, run it for a while (a day or until it stops on high temperature) and repeat.

    Because of the way the circulation pump is fitted, the air seems to gather in the top of the boiler.

    Once you get rid of that, it'll be easier to get rid of the air in the rads.

    BTW you could be dealing with scalding water from safety valve.

    Perhaps some of the other experienced lads on here will have some tips....

    Be sure to keep the water pressure up while doing above.

    Please follow site and charter rules. "Resistance is futile"



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 12,881 ✭✭✭✭Calahonda52


    Pump is external, didn't come with system,

    Primary heat exchanger is empty of air.

    all downstairs rads are fully bled

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 12,881 ✭✭✭✭Calahonda52


    This solved the problem, lots of air in a few upstairs, but will bleed them in the morning

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 12,881 ✭✭✭✭Calahonda52


    So, after working done for 3 weeks, upstairs rads didn't come on this morning, OH not happy

    Pressure is 2 bar

    Any thoughts?

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    do you have motorised valves fitted



  • Registered Users, Registered Users 2 Posts: 12,881 ✭✭✭✭Calahonda52


    “I can’t pay my staff or mortgage with instagram likes”.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 8,069 ✭✭✭10-10-20


    Are you still thinking it's air-locked? I presume not?

    Did it come on when triggered manually? Did the burner have a high temp alarm or can you tell?



  • Registered Users, Registered Users 2 Posts: 12,881 ✭✭✭✭Calahonda52


    Turned off the downstairs rads and it came on upstairs and is now working as before, all over the house so there may have been some air in it, need to change an air vent in hot press which may be sticking

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 8,069 ✭✭✭10-10-20


    Maybe you also have an air-leak and pump pressure issue (such as a balancing problem) and it's not moving the air into the rads where it can be vented. Just a thought.