Solis - Error Over Grid Frequency

Options
  • 26-04-2021 11:42am
    #1
    Registered Users Posts: 241 ✭✭


    Hi Folks

    Keep getting the following error
    Current Status OV-G-V01 (Error Over Grid Frequency)
    and my Solis hybrid inverter shuts down for 5 mins or so then ramps back up

    Checking Google, it been mentioned that the Grid code/standard may not set properly

    Wondering if anyone knows what It should be set to
    My installer is coming back to finish it off but want to see if I can double check also

    Cheers


Comments

  • Moderators, Home & Garden Moderators Posts: 5,806 Mod ✭✭✭✭graememk


    olearydc wrote: »
    Hi Folks

    Keep getting the following error
    Current Status OV-G-V01 (Error Over Grid Frequency)
    and my Solis hybrid inverter shuts down for 5 mins or so then ramps back up

    Checking Google, it been mentioned that the Grid code/standard may not set properly

    Wondering if anyone knows what It should be set to
    My installer is coming back to finish it off but want to see if I can double check also

    Cheers

    More likely it's the grid frequency that is going too high, and not much that can be done about that.


  • Registered Users Posts: 3,954 ✭✭✭mp3guy


    Sounds like you're a victim of this problem too - https://www.boards.ie/vbulletin/showthread.php?t=2058171468

    Do you live in a rural area or urban? How close is the transformer that supplies your house? Any other houses on it?

    You can contact the ESB and see if they will come out and do anything about it for you, but it's unlikely.


  • Registered Users Posts: 241 ✭✭olearydc


    mp3guy wrote: »
    Sounds like you're a victim of this problem too - https://www.boards.ie/vbulletin/showthread.php?t=2058171468

    Do you live in a rural area or urban? How close is the transformer that supplies your house? Any other houses on it?

    You can contact the ESB and see if they will come out and do anything about it for you, but it's unlikely.

    Hi, thanks

    I am in Cork city - On the main road and not near any transformer that I know of. its a strange one and my installer is checking further


  • Registered Users Posts: 3,954 ✭✭✭mp3guy


    olearydc wrote: »
    Hi, thanks

    I am in Cork city - On the main road and not near any transformer that I know of. its a strange one and my installer is checking further

    Any neighbours with solar PV?


  • Registered Users Posts: 2,231 ✭✭✭Boscoirl


    I was getting an error like this. It was happening when we connected the RF link to the inverter. It wouldn’t happen when a WiFi link was connected.

    Haven’t managed to work out why it’s happening yet. For the moment don’t have any links connected.


  • Advertisement
  • Registered Users Posts: 3,954 ✭✭✭mp3guy


    olearydc wrote: »
    Hi, thanks

    I am in Cork city - On the main road and not near any transformer that I know of. its a strange one and my installer is checking further

    Oh I read wrong, grid frequency not voltage.


  • Registered Users Posts: 241 ✭✭olearydc


    mp3guy wrote: »
    Oh I read wrong, grid frequency not voltage.

    You were right - I was getting both alarms actually.

    Just in case anyone else has this down the line
    I was getting both alarms quite a lot - and the Solis system would drop for 15 mins or so then revert back up

    I installed Solis App (you need a dongle on the inverter) so I could see activity on my phone, alerts, alarms, etc. but you can still look at the inverter itself if no app, just easier for me as it was in the attic.

    Every time system shut down, I would check my power sockets with a voltmeter, to see voltage and it would show a high of approx 261 - -normally 250+. The inverter would show exactly the same in the alerts so pretty accurate

    I called up the ESB and mentioned that the voltage was high. the response was pretty fast as they take high voltage over 253 as a high priority.

    They came out within 3 hours, checked the voltage coming into the house, and were showing 257. So they went away and checked the transformer - -all good there and they let me know could be just a bad connection from house to the transformer as they have seen it before.

    That night, a few cheery pickers were seen and folks checking connections. since then, I have had no issues and system has been running 100%

    Just wanted to share in case other people have same issue


  • Registered Users Posts: 3,954 ✭✭✭mp3guy


    olearydc wrote: »
    You were right - I was getting both alarms actually.

    Just in case anyone else has this down the line
    I was getting both alarms quite a lot - and the Solis system would drop for 15 mins or so then revert back up

    I installed Solis App (you need a dongle on the inverter) so I could see activity on my phone, alerts, alarms, etc. but you can still look at the inverter itself if no app, just easier for me as it was in the attic.

    Every time system shut down, I would check my power sockets with a voltmeter, to see voltage and it would show a high of approx 261 - -normally 250+. The inverter would show exactly the same in the alerts so pretty accurate

    I called up the ESB and mentioned that the voltage was high. the response was pretty fast as they take high voltage over 253 as a high priority.

    They came out within 3 hours, checked the voltage coming into the house, and were showing 257. So they went away and checked the transformer - -all good there and they let me know could be just a bad connection from house to the transformer as they have seen it before.

    That night, a few cheery pickers were seen and folks checking connections. since then, I have had no issues and system has been running 100%

    Just wanted to share in case other people have same issue

    Wow! Glad you got it sorted so quickly, 257 is wildly high!


  • Moderators, Home & Garden Moderators Posts: 5,806 Mod ✭✭✭✭graememk


    260! Yeah that's a tad high, no wonder the inverter shut off.

    Glad you got it sorted,

    What's the normal voltage now, when your not generating solar?


  • Registered Users Posts: 2,230 ✭✭✭SD_DRACULA


    Was checking the voltage on my mains cable and it doesn't seem to spike past 240ish and all good with the inverter so far :)


  • Advertisement
  • Registered Users Posts: 1,151 ✭✭✭reni10


    What should the Solis Inverter Standard be set to?

    Mine is G99 but no idea if that is correct?


  • Registered Users Posts: 241 ✭✭olearydc


    graememk wrote: »
    260! Yeah that's a tad high, no wonder the inverter shut off.

    Glad you got it sorted,

    What's the normal voltage now, when your not generating solar?

    Its now showing approx 233
    Have seen it go to 240 but pretty stable now

    ESB said that anything over 253 is a no no - -which I was getting all the time before they fixed it


  • Registered Users Posts: 241 ✭✭olearydc


    reni10 wrote: »
    What should the Solis Inverter Standard be set to?

    Mine is G99 but no idea if that is correct?

    I think mine is set to EN50438IE or something like it - -will confirm tomorrow from the inverter (wife in bed, she will get a heart attack if I go in the attic now!!

    Also - -found this

    https://www.tvri.co.uk/downloads/ziehl/protection%20relays%20-%20ziehl/Howto-meet-EN50438-IE-with-noncertfied-solarPV-products-in-Ireland(1).pdf
    https://static.solartricity.ie/wp-content/uploads/2018/03/Solartricity-electrician-training.pdf
    page 55


  • Registered Users Posts: 2 mrtnmrgns


    An old thread but the same problem still persists. Worked fine Jan when installed then from 29th March alarms every day both over voltage and over frequency. Inverter set to UK standard. UK Power Networks have attended and fitting a monitor to the supply. They claim this is a common problem with Solis. I will update with the outcome and any solutions applied.



  • Registered Users Posts: 453 ✭✭phester28


    I have the same issue, it only shows over frequency at startup in the morning . While under warranty solis put on thee irish standard. But the settings were set to the irish values on the non irish en standard. So it made no difference. I don't believe the grid is going over freq. B



  • Registered Users Posts: 2 mrtnmrgns


    The grid have not yet given me their result but they seem absolutely convinced that it will not be them. My installer is ignoring it until I get the grids response meanwhile I am getting multiple error messages every day regarding both over voltage and over frequency. It’s not only a pain but it goes off line every time and so is not generating.



  • Moderators, Home & Garden Moderators Posts: 5,806 Mod ✭✭✭✭graememk


    I did have an inverter, that did read 20 odd volts too high, tested with a multimeter. Solis support made a change and a higher "compensation" to be set.