Outdoor Socket - Breaker

  • 15-02-2021 1:01pm
    #1
    Registered Users, Registered Users 2 Posts: 2,594 ✭✭✭


    Hi all

    Appreciate your advice please.

    I have an outdoor socket. Last year I used a lot of power tools outside. Should I change the plain outdoor socket for something with a breaker - not sure exactly what I’m asking - but what’s the safest thing I should do. Don’t want to blow the place up accidentally - or on purpose for that matter.

    I think the outdoor socket is a feed off one of the light switches inside.

    Many thanks.


Comments

  • Registered Users, Registered Users 2 Posts: 1,583 ✭✭✭alan4cult


    An outdoor socket fed from a lighting circuit and driving power tools?
    Time for an electrician.


  • Registered Users, Registered Users 2 Posts: 2,594 ✭✭✭karlitob


    alan4cult wrote: »
    An outdoor socket fed from a lighting circuit and driving power tools?
    Time for an electrician.

    That was the electrician. Full rewire of the whole house when we renovated.

    I use an extension lead with what I think is a breaker (it has a reset button) but not sure if that’s doing anything.

    Any advice?


  • Registered Users, Registered Users 2 Posts: 5,374 ✭✭✭aido79


    karlitob wrote: »
    That was the electrician. Full rewire of the whole house when we renovated.

    I use an extension lead with what I think is a breaker (it has a reset button) but not sure if that’s doing anything.

    Any advice?

    I would have my doubts that an electrician rewired a house and put an outdoor socket on a lighting circuit but if that happened I'd be getting the whole thing checked by an electrician who knows what they're doing.

    If the circuit is rcd protected then there shouldn't be a need for anything else apart from the extension lead.


  • Registered Users, Registered Users 2 Posts: 3,609 ✭✭✭stoneill


    karlitob wrote: »
    Hi all

    Appreciate your advice please.

    I have an outdoor socket. Last year I used a lot of power tools outside. Should I change the plain outdoor socket for something with a breaker - not sure exactly what I’m asking - but what’s the safest thing I should do. Don’t want to blow the place up accidentally - or on purpose for that matter.

    I think the outdoor socket is a feed off one of the light switches inside.

    Many thanks.

    You can get a plug in RCD adaptor


  • Registered Users, Registered Users 2 Posts: 2,755 ✭✭✭niallb


    karlitob wrote: »
    That was the electrician...

    Is the switch actually one of a set of light switches, or just a switch that looks similar and perhaps has a slot marked Fuse on it? If it's a fused spur all should be good.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,988 ✭✭✭Andrea B.


    Hi. Post an image of your fuseboard and you will be guided on a simple check to ascertain what protective circuit and type it is on.

    "A test is worth a thousand opinions..." said someone once.


  • Registered Users, Registered Users 2 Posts: 2,594 ✭✭✭karlitob


    aido79 wrote: »
    I would have my doubts that an electrician rewired a house and put an outdoor socket on a lighting circuit but if that happened I'd be getting the whole thing checked by an electrician who knows what they're doing.
    .

    Why would you doubt it.

    He didn’t put in a doorbell after we all had a good laugh about the DelBoy skit.

    I have a cloakroom near the door where we wanted the cat5 that I have throughout the house to come to the router. It’s the same place we have the circuit board and where we wanted the first fix for the alarm system.
    However
    - he ‘forgot’ to put in any power source so impossible to actually plug in any router.
    - there are 4 cat5 points but only 3 cat5 wires in this area. I didn’t know that you shouldn’t/can’t split digital cable but apparently he didn’t know.
    - he asked me whether I had an RJ45 crimper and asked the local shop for a ‘loan’.
    - and we have no first fixed alarm system. Apparently we said we didn’t want one and would go with wireless. Handy thing to say after the house was finished.

    We wanted to put the 2 outside lights on the same switch at the back door. But now we have to go into two different rooms to put on the outside lights.

    He put a fire alarm into the sitting room rather than a carbon monoxide alarm - it has a gas fire.




    And finally he ‘forgot’ to put in an outside socket. So after hacking at the outside wall he took a feed from one of those outside switches that is in the wrong room.

    So many be you’re right. Report him to RECI and get another electrician to review. Of course, I won’t know if he does that correctly either.
    aido79 wrote: »
    If the circuit is rcd protected then there shouldn't be a need for anything else apart from the extension lead.

    Thanks for that. Does the extension lead actually provide some protection.


  • Registered Users, Registered Users 2 Posts: 2,594 ✭✭✭karlitob




  • Registered Users, Registered Users 2 Posts: 2,594 ✭✭✭karlitob


    Andrea B. wrote: »
    Hi. Post an image of your fuseboard and you will be guided on a simple check to ascertain what protective circuit and type it is on.

    "A test is worth a thousand opinions..." said someone once.

    Ah - turn off the switch at the fuse board and see if the outdoor socket works?


  • Registered Users, Registered Users 2 Posts: 2,594 ✭✭✭karlitob


    niallb wrote: »
    Is the switch actually one of a set of light switches, or just a switch that looks similar and perhaps has a slot marked Fuse on it? If it's a fused spur all should be good.

    Nope - just a normal switch. Single switch that links to the outside light.

    https://www.screwfix.ie/p/mk-logic-plus-10ax-1-gang-2-way-light-switch-white/11822?gclid=Cj0KCQiA1KiBBhCcARIsAPWqoSppJ8Q17QCTH4S3FHi08ef0aCrAFQv_GMhSzRQHj0vPWXiIAnPn0CgaAsviEALw_wcB&gclsrc=aw.ds


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,988 ✭✭✭Andrea B.


    karlitob wrote: »
    Ah - turn off the switch at the fuse board and see if the outdoor socket works?

    I aas hoping we could go deeper such as 10a / 20a / RCD / RCBO....
    Ye keep talking rcd etc, but there may also be circuit load concerns if it is a lighting circuit.


  • Registered Users, Registered Users 2 Posts: 2,594 ✭✭✭karlitob


    Andrea B. wrote: »
    I aas hoping we could go deeper such as 10a / 20a / RCD / RCBO....
    Ye keep talking rcd etc, but there may also be circuit load concerns if it is a lighting circuit.

    See below. Thanks. Appreciate any help.


  • Registered Users, Registered Users 2 Posts: 1,988 ✭✭✭Andrea B.


    karlitob wrote: »
    See below. Thanks. Appreciate any help.

    Radio plugged in to outside socket.Volume high.
    Trip no. 11 using blue button.
    Result=Radio off, you have shock protection and it is on socket circuit ( though we still have concerns on 5a lightswitch)
    Result=Radio stays on, come back here.

    As an aside, he may have routed cables via lightswitch box. I assume switching light does not effect the socket��?


  • Closed Accounts Posts: 61 ✭✭Gestureapo


    It'll be very unlikely it's connected to a lighting circuit realistically


  • Registered Users, Registered Users 2 Posts: 2,594 ✭✭✭karlitob


    Gestureapo wrote: »
    It'll be very unlikely it's connected to a lighting circuit realistically

    Why?


  • Closed Accounts Posts: 61 ✭✭Gestureapo


    karlitob wrote: »
    Why?

    Because the REC would have to be really stupid or negligent to do this

    There's like a 5% chance a REC did this without further evidence


  • Registered Users, Registered Users 2 Posts: 2,594 ✭✭✭karlitob


    Gestureapo wrote: »
    Because the REC would have to be really stupid or negligent to do this

    There's like a 5% chance a REC did this without further evidence

    Or both!


  • Closed Accounts Posts: 61 ✭✭Gestureapo


    karlitob wrote: »
    Or both!

    Would have to be both


  • Closed Accounts Posts: 61 ✭✭Gestureapo


    The worst RECs will still wire all sockets from radial socket circuits ime


  • Registered Users, Registered Users 2 Posts: 2,594 ✭✭✭karlitob


    Andrea B. wrote: »
    Radio plugged in to outside socket.Volume high.
    Trip no. 11 using blue button.
    Result=Radio off, you have shock protection and it is on socket circuit ( though we still have concerns on 5a lightswitch)
    Result=Radio stays on, come back here.

    As an aside, he may have routed cables via lightswitch box. I assume switching light does not effect the socket��?

    So radio plugged in and on loud. Number 11 blue button pushed. Radio off (as well as a whole range of things).

    What does that mean?

    Thanks for your help with this.


  • Advertisement
  • Closed Accounts Posts: 61 ✭✭Gestureapo


    karlitob wrote: »
    So radio plugged in and on loud. Number 11 blue button pushed. Radio off (as well as a whole range of things).

    What does that mean?

    Thanks for your help with this.

    It means the outdoor socket is RCD protected as expected

    The other scenario would be rare these days


  • Registered Users, Registered Users 2 Posts: 2,594 ✭✭✭karlitob


    Gestureapo wrote: »
    It means the outdoor socket is RCD protected as expected

    The other scenario would be rare these days

    So I can plug in power tools.

    Is there a wattage limit to the power tools I plug in.

    Is there an adapter I can plug in to the outdoor socket for it to fail there rather than throughout the whole house?

    The other poster said there may still be concerns regarding the 5A light switch. Not sure what this means?


  • Closed Accounts Posts: 61 ✭✭Gestureapo


    karlitob wrote: »
    So I can plug in power tools.

    Is there a wattage limit to the power tools I plug in.

    Is there an adapter I can plug in to the outdoor socket for it to fail there rather than throughout the whole house?

    The other poster said there may still be concerns regarding the 5A light switch. Not sure what this means?

    1. 13amp portable tools

    2. No ,there's no adapter you can fit in series with the board RCD

    You could get an RCBO fitted to reduce the potential nuisance

    3. No, there's no concerns now about light switches


  • Registered Users, Registered Users 2 Posts: 24,644 ✭✭✭✭punisher5112


    Get Philips hue lamps or even IKEA etc etc for the outside lights and control from phone, tablet, Alexa and also can fit a wireless sensor so lights will come on when motion detected.


  • Registered Users, Registered Users 2 Posts: 2,594 ✭✭✭karlitob


    Gestureapo wrote: »
    1. 13amp portable tools

    2. No ,there's no adapter you can fit in series with the board RCD

    You could get an RCBO fitted to reduce the potential nuisance

    3. No, there's no concerns now about light switches


    Thank you.

    1. Will keep an eye out for that spec. I was using a 9inch makita angle grinder last year. 2400w, 110V and used a transformer. I can’t seem to find the amp on the makita website. But that’s the sort of thing I was using. Oh and an electric cement mixer, belle 110v

    2. Understood. Had meant like some breaker on an extension cable that would break any overload.

    3. Thank you.


  • Registered Users, Registered Users 2 Posts: 1,988 ✭✭✭Andrea B.


    It appears, from the images that you have an installation of a conforming 13Amp double socket circuit with shock protection.
    In the eventuality that it trips all or some of the other sockets, then you and/or your circuit are being protected, so the inconvenience should be ignored.
    In other words, work away.


  • Registered Users, Registered Users 2 Posts: 1,988 ✭✭✭Andrea B.


    Gestureapo wrote: »
    Because the REC would have to be really stupid or negligent to do this

    There's like a 5% chance a REC did this without further evidence

    I would have assumed there is a 0% chance a REC would feed a socket circuit from a lighting circuit?


  • Closed Accounts Posts: 61 ✭✭Gestureapo


    Andrea B. wrote: »
    I would have assumed there is a 0% chance a REC would feed a socket circuit from a lighting circuit?

    The 5% chance is because the OP suspected this


  • Registered Users, Registered Users 2 Posts: 1,988 ✭✭✭Andrea B.


    Gestureapo wrote: »
    The 5% chance is because the OP suspected this

    True. I was using the wrong calculation. Percentages always catch me.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,594 ✭✭✭karlitob


    Andrea B. wrote: »
    It appears, from the images that you have an installation of a conforming 13Amp double socket circuit with shock protection.
    In the eventuality that it trips all or some of the other sockets, then you and/or your circuit are being protected, so the inconvenience should be ignored.
    In other words, work away.

    Thank you very much. As you can tell, little knowledge about electrics and so I’m very wary of it.

    Thanks again.


  • Registered Users, Registered Users 2 Posts: 1,988 ✭✭✭Andrea B.


    karlitob wrote: »
    Thank you very much. As you can tell, little knowledge about electrics and so I’m very wary of it.

    Thanks again.

    You are very welcome and wise to question the stuff. At least you know it is wired for shock protection.