    Just checking what size cable you would recommend going from the inverter to the board for a 4.7kw solar setup covering a distance of about 30m


Comments

  • Registered Users Posts: 2,820 ✭✭✭ air


    spose wrote: »
    Just checking what size cable you would recommend going from the inverter to the board for a 4.7kw solar setup covering a distance of about 30m

    Go 10sq minimum to limit the voltage rise, worth it for the small increase in marginal cost.
    Your electrician will have the final say anyway.


  • Posts: 0 [Deleted User]


    Link

    Max operational current +20% overhead.
    Panels to inverter < 3% voltage drop.
    Inverter to CU < 3% voltage drop.
    Charger to battery ~1% voltage drop depending on nominal battery voltage.