Pressure gone to 0 bar on MYNUTE HE gas boiler

  • 06-03-2018 5:21pm
    #1
    Registered Users, Registered Users 2 Posts: 495 ✭✭


    Hey guys

    anyone have any idea how to repressurise this ?

    Youtube videos seem to show a pressure valve that I can't seem to find / don't have :P

    444936.jpg


Comments

  • Registered Users, Registered Users 2 Posts: 8,565 ✭✭✭K.Flyer


    Rockin wrote: »
    Hey guys

    anyone have any idea how to repressurise this ?

    Youtube videos seem to show a pressure valve that I can't seem to find / don't have :P

    444936.jpg
    Rockin wrote: »
    Hey guys

    anyone have any idea how to repressurise this ?

    Youtube videos seem to show a pressure valve that I can't seem to find / don't have :P

    444936.jpg

    Well, first off filling valves are never inside the casing of a Gas Boiler.
    Secondly, unless you are a Gas Registered Installer, you should not be taking the casings of the gas boiler or adjusting anything inside them.

    Most filling valves are located in the hot press and look like the attached image.
    Open the valve and bring up the pressure to approx 1.25 bar.


    real-filling-loop-thumb.jpg


  • Registered Users, Registered Users 2 Posts: 409 ✭✭pmce4


    hi,
    If it has dropped to zero and it happened during the cold spell last week there is a chance you have a leak. I am in the same position. my boiler pressure hold pressure when heating is off but drops to zero from 1.5 bar in 15 mins when heating is turned on. I have a leak but need specialist equipment to locate it as it is under floorboards.